    Air cooled condensor sizing



    I have a sitiuation , I recevied one Air cooled Condensing unit of 1.5tr capacity at -1degC evaporating and 54 degc condensing . We feel that the condesor supplied is small . As the unit is tripping frequently in HP . we checked all the other parameter which are correct as per practise.
    Can some one help us in giving following details

    1. What should be the face surface area of condensor ? the condensor supplied has 3.7 sqft of face surface area.

    2. How to decide on correct size of condensor



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    That is too little data.

    What is evaporator cooling capacity at -1°C or what is evaporator mod no.?
    What is condenser model no.
    What is compressor capacity at that conditions or what compressor model do you have.
    What is refrigerant.

  3. #3
    Join Date
    Nov 2006
    Location
    India
    Age
    50
    Posts
    19
    Rep Power
    0

    Re: Air cooled condensor sizing

    Thanks Nike

    The compressor model is CR 30 Of kirloskar copeland make (India) Hermatic type , the compressor delivers 16000 btu/hr at -1 degC evaporating and 54 degc condensing.

    Refrigerant used - R 22

    Evaporator is of matching capacity

    regards

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Air cooled condensor sizing

    What are the physical dimensions, no. of tubes, feeds, fin spacing, rows deep, wether it has subcooling circuit or not, if so the no. of tubes, no. of feeds, tube dia. air flow etc. are required to get the capacity of the condenser. The make of condenser. If possible please provide the above, then may be I could help you.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    Quote Originally Posted by nambiandy View Post
    Thanks Nike

    The compressor model is CR 30 Of kirloskar copeland make (India) Hermatic type , the compressor delivers 16000 btu/hr at -1 degC evaporating and 54 degc condensing.

    Refrigerant used - R 22

    Evaporator is of matching capacity

    regards
    This is result from Coolpack software!
    Check data to see if they correspond with your case!








  6. #6
    Join Date
    Nov 2006
    Location
    India
    Age
    50
    Posts
    19
    Rep Power
    0

    Re: Air cooled condensor sizing

    Dear nike.

    thanks it is a useful information.


    Dear Mr Sen

    I do not have those details now.I will Try to get it

    Can you suggest some good book on Condesor & evaporator design

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Air cooled condensor sizing

    If you can get me the details as I had asked for, then I can work out the capacity of your existing condenser. Condenser and Evaporator design is not easy and involves a lot of deep study. The people who can, help are the members of this forum.

    If you go through the threads you will find a number of interesting discussions on this.

  8. #8
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Air cooled condensor sizing

    Quote Originally Posted by nambiandy View Post
    I have a sitiuation , I recevied one Air cooled Condensing unit of 1.5tr capacity at -1degC evaporating and 54 degc condensing . We feel that the condesor supplied is small . As the unit is tripping frequently in HP . we checked all the other parameter which are correct as per practise.
    Can some one help us in giving following details

    1. What should be the face surface area of condensor ? the condensor supplied has 3.7 sqft of face surface area.

    2. How to decide on correct size of condensor
    Hi,

    It is roughly expected that the face area (length * Height) of the condenser ranges from 0.275 m2 to 0.33 m2. This depends on the air temperture difference and air face velocity. If u can tell me about those parameters May be I could give u the exact sizing. However, to jude on the condenser fits this case or no the Judment should be done on the total surface area not the face "frontal" area.

    Cheers

    Mohamed

  9. #9
    Join Date
    Jan 2008
    Location
    India
    Age
    46
    Posts
    14
    Rep Power
    0

    Re: Air cooled condensor sizing

    Face velocity should be in-between 4.5 - 5.5 m/sec. Condenser design is depend upon size of tube, thickness of tube. ambient temperature. No. of fins. If you can give me the details i can calculate the area for yyou.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Air cooled condensor sizing

    What are the condenser entering and leaving air temperatures?

    What is the liquid line temperature at receiver outlet?

    What is the saturated condensing temperature (from pressure/temperature chart)?

  11. #11
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: Air cooled condensor sizing

    It might seem I’m going to over simplify this but, let’s cut to the chase. The Copeland CR30 is a nominal 2.5 HP compressor, R-22 High Temp (0 to 45 F (-18C to +7C). It pumps 16,600 btuh @ +30 F (-1C) SST @ 129F (+54C) CT @ 230-1-50.

    Copelands' 2 through 3-1/4 nominal HP, rated 0 to +45 F SST, condensing units use a condenser sized at 32” x 18”, 10FPI, 3 row, and use 2 fans……… roughly 3.75 SF surface area. They rate their units up to an 110F (+43C) ambient.

    If your condenser is near this size and specifications and the ambient temperature is not extreme, them you have other problems causing the high head pressure.

    Typical causes of high head pressure:
    • Unbalanced system, load in excess of the design conditions
    • Air in the system. If so, then check the low side for a leak.
    • Dirty condenser.
    • Re-circulating of condenser air. This is a common occurrence when an oversized outdoor weather hood has been installed.
    • Air flow is restricted thru the condenser.
    • The ambient temperature surrounding the condenser is too warm. This is common on walk in coolers and freezers when the condensing unit is mounted on the box and closed off by a drop ceiling.
    • Refrigerant overcharge.
    • Liquid refrigerant backed up in the receiver.
    • Restriction in the discharge line due to physical damage or an internal restriction.
    • Incorrect air flow thru the condenser. Has someone previously installed a new fan motor or blade? Check the rotation, horsepower and blade size, compared to the specifications of the unit.
    • Fan cycle control out of calibration.
    • Flooded head pressure control: Receiver too small for summer application.
    • Flooded head pressure control: Bypass port wedged open due to a foreign material lodged in it, or the port is worn.
    • Flooded head pressure control: Field adjustable controls are set incorrectly.
    Regards……………..Powell
    Last edited by powell; 19-02-2008 at 06:47 AM.

  12. #12
    Join Date
    Dec 2001
    Location
    South Africa
    Age
    53
    Posts
    29
    Rep Power
    0

    Re: Air cooled condensor sizing

    I have to agree with Powell. I think that you have a problem with the fundamentals of the system.

    But i am impressed with all the system design software the was applied here. I would like to get my hands on that!!

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    Quote Originally Posted by allanbaker View Post
    I have to agree with Powell. I think that you have a problem with the fundamentals of the system.

    But i am impressed with all the system design software the was applied here. I would like to get my hands on that!!
    It is free!
    http://tinyurl.com/2hd4av

  14. #14
    Join Date
    Dec 2001
    Location
    South Africa
    Age
    53
    Posts
    29
    Rep Power
    0

    Re: Air cooled condensor sizing

    Hey Nike that is twice today you have given me work......im gonna start to call you boss

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    Quote Originally Posted by allanbaker View Post
    Hey Nike that is twice today you have given me work......im gonna start to call you boss
    Don't!
    Finally, after 10 years as project manager, nobody calls me "boss" any more (I am self employed, one-man-company now).

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Air cooled condensor sizing

    Quote Originally Posted by Gary View Post
    What are the condenser entering and leaving air temperatures?

    What is the liquid line temperature at receiver outlet?

    What is the saturated condensing temperature (from pressure/temperature chart)?
    To expand on this a little:

    The difference between entering and leaving air temperature is the condenser delta-T. Excessive dT indicates insufficient airflow.

    The difference between SCT and liquid line temperature is the subcooling. This tells you if liquid is backing up into the condenser (overcharge).

    The difference between liquid line temperature and leaving air temperature is the condenser approach. This tells you if there is efficient heat transfer between the refrigerant and the air (condenser coating).

    The difference between entering air temperature and SCT is the condenser TD. If all else is within normal parameters and given normal heat load, this tells you about the relative condenser sizing.
    Last edited by Gary; 20-02-2008 at 09:46 PM.

  17. #17
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: Air cooled condensor sizing

    nambiandy,

    Do you have any follow up details? There's a lot of good input in this thread.

    I'm sure the other posting members, myself included, are interested in the results.

    Powell

  18. #18
    Join Date
    Sep 2008
    Location
    india
    Age
    39
    Posts
    15
    Rep Power
    0

    Re: Air cooled condensor sizing

    please send me condenser design book in PDF format on sagar_babar45@indiatimes.com

  19. #19
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: Air cooled condensor sizing

    Quote Originally Posted by sagar45 View Post
    please send me condenser design book in PDF format on sagar_babar45@indiatimes.com

    please send me $100 first... doyourownhardwork@freeloader.com
    ...and she said "give it to me you big fridgie"

  20. #20
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Air cooled condensor sizing

    Yo Sagar, you sound like ABBA, give me give me give me.

    what do we get ???

    Ice

  21. #21
    Join Date
    Sep 2008
    Location
    india
    Age
    39
    Posts
    15
    Rep Power
    0

    Re: Air cooled condensor sizing

    i am desinging a condenser for Danfoss MT100 Compressor At Evaporating temperature 7.2 And 55 Condensing temp.Refriegrant R22 . The toatal heat rejection Is het Load + Compressor Work 23.5 KW+ 8 KW = 31.5 KW
    the FPI for Condenser iS 10
    The Tube Diameter IS 3/8"
    pitch Distance Horizontal Is 25.4 mm
    Please anyone suggest how can i caqlculate the heat transfer are and Air flow

    also how can i select the circuits

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    Quote Originally Posted by sagar45 View Post
    i am desinging a condenser for Danfoss MT100 Compressor At Evaporating temperature 7.2 And 55 Condensing temp.Refriegrant R22 . The toatal heat rejection Is het Load + Compressor Work 23.5 KW+ 8 KW = 31.5 KW
    the FPI for Condenser iS 10
    The Tube Diameter IS 3/8"
    pitch Distance Horizontal Is 25.4 mm
    Please anyone suggest how can i caqlculate the heat transfer are and Air flow

    also how can i select the circuits

    What is maximum ambient temperature, relative humidity and altitude?

  23. #23
    Join Date
    Sep 2008
    Location
    india
    Age
    39
    Posts
    15
    Rep Power
    0

    Re: Air cooled condensor sizing

    Ambient temperature is About 43 Degc

  24. #24
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Air cooled condensor sizing

    Air cooled condenser surface area as well as air quantity is important. Normally around 750 to 1000 cfm per TR is required and again depends on the suction and discharge. If the ratio is more Heat rejection factor will be more.

  25. #25
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Air cooled condensor sizing

    Hi sagar,

    Get the HGM100 condensing unit from danfoss, then start your studies!!!!

    Ravi

  26. #26
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air cooled condensor sizing

    Quote Originally Posted by sagar45 View Post
    Ambient temperature is About 43 Degc
    What is maximum ambient temperature, relative humidity and altitude?
    ...............................

Similar Threads

  1. Remote air cooled application
    By David T in forum Tools and Calculators
    Replies: 1
    Last Post: 04-06-2010, 02:02 PM
  2. Replies: 9
    Last Post: 30-01-2009, 08:50 AM
  3. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  4. water cooled
    By tait71 in forum Trouble Shooting
    Replies: 27
    Last Post: 02-03-2007, 07:22 PM
  5. water cooled condenser shell type
    By abbasi in forum New Technologies
    Replies: 0
    Last Post: 27-04-2005, 08:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •