i spoke to a guy from RS today and he confirmed what many of you have said, that there is o formula to calculate the resistance. he did tell me that the resistance is a result of the motor design and that the motor is designed to rotate at a certain speed which is determined by the work the motor has to do. i don't understand it fully yet, but i will report back on this forum, hopefully before the end of the week, with a better explanation.
thanks again for your interest
-
23-06-2009, 06:58 PM #2
Re: 3 phase resistance calculation
i am going to try and answer the origanal question.
you are wanting to do a quick calc to check a motor winding. on the side of any motor there is a data plate ( as i am sure you know). the info you need is motor KW, V, A and cos.
formula W (kw/1000) = 1.732 * VL * IL * cos
The motor KW rating is the culmative total of all three balanced windings. so motor kw/3 is approx the power rating of 1 winding. ANS/Vp = Ip. then do Vp/Ip = winding Z ohms.
in reality its a bit more complicated than that, but in the middle of the night on a wet and windy roof, it should give you a good idea.
hope that helps
sparky matt
-
25-09-2010, 03:52 PM #3
Re: 3 phase resistance calculation
Originally Posted by bill1983;91170...It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
NH3 thermosiphon evaporator calculation
By cygbob in forum NH3Replies: 3Last Post: 27-11-2007, 10:00 AM -
Single phase contactor
By Andy T in forum CommercialReplies: 9Last Post: 23-10-2006, 01:45 PM -
Phase Failure Protection
By Abe in forum ElectricalReplies: 11Last Post: 08-11-2005, 09:23 PM -
3 phase connections
By davidler in forum IndustrialReplies: 2Last Post: 22-03-2004, 02:11 PM