Re: 3 phase resistance calculation
If compressor have thermal protection in windings, it should protect motor, because with 2 phase, he will overheat.
If compressor have thermal over current relay together with contactor, it should react and protect compressor, because other two phases now draws higher current.
If compressor have electronic (hall type) over current relay together with contactor, it should react immediately at phase drop and protect compressor.
It is often case that one phase fail (acting of fuse etc...), but it is rare case that compressor burns because that phase loss, unless someone has fiddling with protective devices.
Most likely, if for some reasons (work on power transformer or distribution boxes), someone change phase order (rotation direction) scroll compressors is going to rotate in reverse direction than you could get damaged (blocked) compressor. That is is why most (reputable) manufacturers have phase rotation and presence relay when they have scrolls.Last edited by nike123; 26-01-2008 at 05:10 PM.
Similar Threads
-
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
NH3 thermosiphon evaporator calculation
By cygbob in forum NH3Replies: 3Last Post: 27-11-2007, 10:00 AM -
Single phase contactor
By Andy T in forum CommercialReplies: 9Last Post: 23-10-2006, 01:45 PM -
Phase Failure Protection
By Abe in forum ElectricalReplies: 11Last Post: 08-11-2005, 09:23 PM -
3 phase connections
By davidler in forum IndustrialReplies: 2Last Post: 22-03-2004, 02:11 PM