    Re: 3 phase resistance calculation

    Frank

    You are completely right lots of modern 3 ph splits do include some phase rotation protection but often it is to ensure scroll compressors rotate in the correct direction.

    My little story pre dates 407c equipment by quite a few years though & lots of engineers looking on this site still working on basic R22 kit.

    The point I tried to make was that nobody tends to think about this issue until its to late & some one has to pay.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: 3 phase resistance calculation

    Quote Originally Posted by Thermatech View Post
    The point I tried to make was that nobody tends to think about this issue until its to late & some one has to pay.
    Thermatech
    It's not just the reverse phase protection though. If the phase imbalance goes over 10% the electronics shuts down the equipment under fault conditions to prevent damage.
    I agree that not all manufacturers include this but most of the 'better' ones do.
    I've worked on lots of old 22 units where this is so. Chillers especially (OK I know that's not splits)

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 3 phase resistance calculation

    Quote Originally Posted by Thermatech View Post
    Frank


    The point I tried to make was that nobody tends to think about this issue until its to late & some one has to pay.
    I do, always a overcurrent relay on a 3 phase motor.
    Besides this, many hermetic compressors have a clixon in the starpoint of the windings.
    Most semi hermetics have an additional Kriwan protection and together with the overcurrent, you almost have a perfect motor protection.
    If you have a phase loss on a 2 phase motor, then it simply will stop to run.

    The electronic devices in splits and VRV/VRF's not only control phase rotation but also phase loss, it's incoporated in teh same enclosure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  2. Replies: 3
    Last Post: 27-11-2007, 10:00 AM
  3. Single phase contactor
    By Andy T in forum Commercial
    Replies: 9
    Last Post: 23-10-2006, 01:45 PM
  4. Phase Failure Protection
    By Abe in forum Electrical
    Replies: 11
    Last Post: 08-11-2005, 09:23 PM
  5. 3 phase connections
    By davidler in forum Industrial
    Replies: 2
    Last Post: 22-03-2004, 02:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •