10-02-2008, 01:23 PM #1
Troubleshooting.
Dear RE members,
While conducting performance test of watercooled DX screw chiller in factory I have following observations.
Charged less than spec.( R& D)
Capacity is less by 3%
Discharge/suction pr. as per design
subcooling 5 deg C
Suction superheat is @ 3 deg C.
Discharge superheat 27 deg C.
I need to know do I have to charge additional gas or not?
Since suction superheat is low if I open TXV my capacity will be dropped.
Pl. suggest solution.
Thanks in advance.
-
23-04-2008, 06:01 PM #2
Re: Troubleshooting.
Hi refystem, if you check the discharge pressure you can determinate if your system have the correct referigerant chargecould you send me the suction pressure and the discharge pressure
-
23-04-2008, 06:33 PM #3
Re: Troubleshooting.
hello,
if not enough gas yes u need to charge, but make sure that you must have enough load ( for heat transfer ) what kind of refrigerant you used, is the system have level gauge or refrigerant sight glass
for screw compressor mostly the design base is 10~20degc suct superheat at full load
-
29-10-2009, 10:18 PM #4
Re: Troubleshooting.
How to make and model of machine is?
Similar Threads
-
troubleshooting books
By marc5180 in forum Refrigeration BooksReplies: 42Last Post: 04-04-2009, 06:08 PM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Copeland scroll troubleshooting
By nike123 in forum Trouble ShootingReplies: 8Last Post: 26-02-2008, 05:37 PM -
Looking For A Good Troubleshooting Guide
By nightranger121 in forum Trouble ShootingReplies: 10Last Post: 23-11-2007, 06:16 PM -
Troubleshooting my Fridge
By IslandGirl in forum DomesticReplies: 1Last Post: 23-08-2006, 10:33 AM