    Does anyone know if there is a limit in pipe size or radius when bending pipes which carry R410A. I like to bend pipes up to 1 1/3" but i'm not sure if it is permissable with the higher pressures.

    Is there anything wrote in any regulations?

    If a system carrying R22 has a HP set at 400 - 450 psi then this is not far off the operating pressure of R410A, to me this makes it okay.

    Regards



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Bending R410A pipes

    Freezy
    When you form a bend with pipe benders the outside of the bent tube is pulled & stretched out so it gets thinner in wall thickness.
    Tube manufacturers know that & build in a safety factor to allow for tube forming.
    You need to get data from the copper tube manufactorers.
    HP switch setting for most 410a systems will be well over 40 bar / 600 psi. Lots of splits & VRF pressure switch specification is 41.5 bar cut off pressure.
    You might also find that with this type of pressure you can use standard gauge wall thickness copper tube up to 3/4 inch diameter but any larger size tube & you may need to start looking for heavy duty wall thickness tube.
    Some UK distributors stock upgraded wall thikness tube on the larger sizes for the higher preesure 410a applications.

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Bending R410A pipes

    freezy

    What psi pressure strength test will you carry out to test integrity of the installed pipework installation ?

  4. #4
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: Bending R410A pipes

    Hi Thermatech

    We pressure test to manufacturers spec, normally 38 bar. British standards want 1.1 x operating pressure and 1.3 x operating pressure for a strength test.

    With the wall thickness thing, all pipe sold in the UK has to conform to British Standards and should have the correct SWG for this.

Similar Threads

  1. Pressure Testing for R410a
    By Pooh in forum Tools and Calculators
    Replies: 33
    Last Post: 13-08-2008, 11:41 PM
  2. R410A pressure in air conditioning
    By irwinchong80 in forum Technical Discussions
    Replies: 4
    Last Post: 06-10-2007, 07:33 PM
  3. R410A - state of art
    By MrReds in forum Refrigerants
    Replies: 2
    Last Post: 04-03-2007, 10:56 PM
  4. R410A split min and max line temps
    By smileypete in forum Domestic
    Replies: 1
    Last Post: 17-11-2005, 10:38 PM
  5. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 09:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •