    Denco unit L.P trip



    Hi guys, working on a denco under floor aircon, unit is tripping on L.P, which would suggest low refrigerant, put guages on without comp running, both low and high side balanced out at 100psi, activated contactor manualy and suc went below Opsi diss also down to zero, removed any refrigerant left in system and charged with 7bar O.F.N, leak checked every joint and nut on system no leaks found while unit is in this poorly condition am going to change drier and clean out filter on t.e.v, any other suggestions would be welcome. thanks.

    P.S system has had nitro in for about hour and a half and guages show no loss at all...



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Denco unit L.P trip

    A few things, it's hard to get data when the post is written like a story, you need paragraphs and line breaks when you are stating observed pressures and temperatures.
    Sorry if I'm wrong but from what I could understand you said HP went from a static 100 PSI, down to zero when you ran the system?
    Systems only short of refrigerant don't have the HP going down when you start the system, let alone going all the way down to 0psi

    Also 700kpa isn't much to leak test with, I always leak test with the same presuure that the HP could be in normal running conditions. I've found heaps of leaks that others couldn't using that method and a bit of soapy water.

  3. #3
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Denco unit L.P trip

    I'll keep my story telling for my daughter next time then, would have thought 7bar was adequate press, will boost it up some more and re-chack..Cheers.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Denco unit L.P trip

    Quote Originally Posted by N.Lewis View Post
    Hi guys, working on a denco under floor aircon, unit is tripping on L.P, which would suggest low refrigerant, put guages on without comp running, both low and high side balanced out at 100psi
    That just shows you that you have refrigerant in system.



    activated contactor manualy and suc went below Opsi diss also down to zero,
    There is no chance that both suction and discharge reads 0psi after you read 100psi initially. This reading you could get only if you connected both gauges at low side of circuit.


    removed any refrigerant left in system
    How much did you recovered and what is required refrigerant charge for that unit?


    and charged with 7bar O.F.N, leak checked every joint and nut on system no leaks found while unit is in this poorly condition am going to change drier and clean out filter on t.e.v, any other suggestions would be welcome. thanks.

    P.S system has had nitro in for about hour and a half and guages show no loss at all...
    You should pressure test it with higher pressure (maximum allowable working pressure) and also introduce some small amount of refrigerant in it and then test it with electronic leak detector.
    Then you should record temperature of surrounding and after 6h check pressure in system.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Denco unit L.P trip

    I assume that the system is operating on R22.

    Increase your OFN pressure to 375psig (25bar) and leave it on test for 24 hours, then check your gauges for any pressure drop.

    Sometimes when you can't find a leak under OFN pressure test , it could have been the schraeder cap that was leaking but now doesn't show up as your gauge line is making a good seal.

  6. #6
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Denco unit L.P trip

    Thanks for all replies, paulh and frank, increased ofn to 25b found pin prick leak on cappilary line going into pressure control valve which was behind L.P/H.P switch, Happy Day's

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Denco unit L.P trip

    Might also suggest that your HP reading was perhaps downstream of a solenoid valve which didn't open when you manually pushed the contactor in.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Denco unit L.P trip

    As Brian says most Denco downflow units I`ve seen have a liquid solenoid and remote condenser. I am still concerned how you managed to pull a vac at suction and discharge . Did you measure at the service valves on the rotalocks. You may have more than a leak to worry about

  9. #9
    Join Date
    Mar 2005
    Location
    Newcastle upon Tyne
    Age
    52
    Posts
    16
    Rep Power
    0

    Re: Denco unit L.P trip

    Simply put, if you just pushed the contactor in, then the solanoid wouldn't have been energized, if your HP guage was connected down stream of the solanoid then your basically reading the same pressure as your LP side.
    Pressure test.
    Repair leak.
    re pressure test.
    Vac.
    Recharge and run under on demand of controls.

    Chris.

  10. #10
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: Denco unit L.P trip

    I can concur if you just "push" the contactor in the liquid line sol valve will not be energized.

    Very confused re the high side?? did you have the gauges on the same side of the system?

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. MV600 head pressure trip (ghost)
    By andre_fridge in forum Technical Discussions
    Replies: 9
    Last Post: 28-01-2006, 02:16 PM
  5. MV600 ghost trip
    By andre_fridge in forum Chit Chat & Service Stories
    Replies: 0
    Last Post: 23-01-2006, 09:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •