Thread: inverters pulling vacuum
24-01-2008, 08:21 AM #1
We always asked to pull a vauum from both high and low sides valves ever wondered why.
Why do we preheat aircon(sump heaters ) before commissioning a system ?Is it worth where ambient Temp is high +30c?
24-01-2008, 08:45 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: inverters pulling vacuum
This is from one article I have on my comp:
Factors Affecting The Speed At Which A Pump Can Dehydrate A Refrigerant System
Several factors influence the "pumping speed" of a high vacuum pump, and thus the time required to remove all moisture from a refrigerant system. Some of the most important are: the cubic feet of the system; the amount of moisture contained within the system; the ambient temperature present; internal restrictions within the system; external restrictions between the system and the vacuum source; and the size of the pump.
The only factors under the control of the service technician are the external restrictions between the system and the vacuum pump.
Let us assume that all other variable factors affecting pump down time are equal within a system. Variable pressures within a system attempt to equalize one another. The higher pressure "flows" toward the lower pressure. The above illustration shows the variable pressure creating a vacuum of 100 microns and the system at higher atmospheric pressure. The higher pressure in the system will flow toward the vacuum pump until it is reduced or equal to the 100 microns of pressure. The speed at which it will flow is controlled by the I.D. and length of the connecting line. Laboratory tests show that pump down time can be significantly reduced by use of larger diameter hoses. For optimum pumping speed, keep access lines as short in length and as large in diameter as possible.
All of us have released an inflated balloon, allowing the escaping air pressure to propel it on a wild course. At other times you have inflated a balloon and stretched its stem, allowing the air to escape with a squealing sound. In effect, you were controlling the connecting I.D. as in the above illustration and, in turn, controlling the time it took to release all of its pressure. The principal is identical — the higher pressure is trying to move toward the lower pressure. These illustrations stress the importance of eliminating all external restrictions whenever possible.
In answer to our first question, it is perfectly acceptable to use a 4 CFM or larger vacuum pump on a small system. Using too small of a pump on a large system, e.g. a 1.2 CFM vacuum pump on a 40 ton unit, could cause the pump to operate in a "free air" condition for an extended period of time, thus risking premature pump wear.
To answer our second question, the best way to know for sure that the system has been thoroughly dehydrated is by using a thermistor vacuum gauge. This prevents wasting time by pulling down after evacuation is complete or risking inadequate dehydration.
When reading vacuum, remember that the location of the gauge tube will affect the reading. The closer the gauge is to the vacuum pump, the lower the reading will be. To get the most reliable reading, isolate the vacuum pump using a vacuum valve assembly. Let the pressure to equalize throughout the system, then take a final reading.
Liquid refrigerant could not be compressed and that lead to great damage of compressor. Also, liquid refrigerant dilutes the oil. If compressor is coldest spot in system and enough time is passed, most or all of liquid refrigerant could end up in compressor crankcase
05-02-2008, 09:12 PM #3
As a general rule the oil should be at least 10 degrees (C) above ambient temperature to ensure it is refrigerant free
Aquarium filling by vacuum.
By romaurie in forum HobbiesReplies: 19Last Post: 25-08-2010, 04:16 PM -
vacuum timeline
By phicks1065 in forum CommercialReplies: 11Last Post: 12-01-2008, 10:10 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM -
Recovery and vacuum equipment
By Larry2 in forum FundamentalsReplies: 2Last Post: 19-07-2006, 12:16 AM -
Can I leave a system in a vacuum overnite?
By kengineering in forum Technical DiscussionsReplies: 15Last Post: 17-05-2006, 03:03 PM