    Daikin U4 error code



    I've been asked to look at a Daikin ducted unit model RYEP71L7V1 in an apartment block.

    The initial problem was the indoor unit freezing up quite badly and causing considerable leaks in the ceiling void. Plus the remote displaying a U4 error code (comms problem?).

    My client uses the apartment as a holiday home and therefore doesn't use the air conditioning much but did say the unit leaked water all the time.

    After a process of elimination (there are about 20 outdoor units on the roof) I've discovered the outdoor unit doesn't switch off at all and so I think that may explain the ice build up.

    I don't have any wiring diagrams but the power goes to the outdoor unit which then feeds the indoor unit.

    The indoor unit will operate when the remote is switched on.

    Any suggestions would be appreciated.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin U4 error code

    sounds like compressor relay welded closed if it's a conventional type (non inverter).
    edit:
    Daikin error codes here http://www.refrigeration-engineer.co...ghlight=daikin
    Last edited by paul_h; 19-01-2008 at 12:34 PM.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin U4 error code

    You can download Daikin's full fault-code matrix HERE.

    But...Outdoor unit is running constantly and there is a communication error, my suspicion is that the outdoor unit's PCB is gone..

  4. #4
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Daikin U4 error code

    check that the condenser relates to the evaporator your looking at - comms problems as well as freezing up / cooling all the time - could be mixed up interconnecting wiring, never swithching off due to another unit demanding the cooling process, from the wrong condenser. Is this a recent install?

  5. #5
    Join Date
    Mar 2006
    Location
    Australia
    Posts
    28
    Rep Power
    0

    Re: Daikin U4 error code

    is it possible the interconnects were mixed up?

    U4 is an error in communication between indoor and outdoor units.

    daikins have the "1,2,3" wiring, with off memory 1 is a premanent active, 2 being neutral, and 3 being a signal wire. if 1 and 3 were mixed up, would that possibly give a permanent active to the signal wire and possibly cause the condensor to continually run?

    i dont know much about the internal workings of these units, just throwing something up in the air, some of the other guys on the forum will have a better idea.

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin U4 error code

    No, because the outdoor gets mains voltage straight from the circuit breaker. If you swap '1' with '3' it's the indoor that would be only be getting signal, so it wouldn't be getting voltage to run.
    Like I said, the outdoor unit is probably a pretty much melted mess, the relay contacts for the comp would be welded and the board itself pretty much fried.

  7. #7
    Stevo1978's Avatar
    Stevo1978 Guest

    Re: Daikin U4 error code

    if you switch the indoor unit off does the condensing unit stay running

  8. #8
    Join Date
    Jan 2008
    Location
    Spain
    Age
    63
    Posts
    7
    Rep Power
    0

    Re: Daikin U4 error code

    Thanks for your suggestions.What I didn't mention was the unit is in Spain and fitted about three years ago by 'builders'. The wiring is literally open to the elements and my initial suspicion was that the indoor and outdoor units were incorrectly wired, especially when a brown wire ended up at a earth wire, but following it through, it does seem ok.

    I cant confirm thats its ever worked, but judging by the ice, its been a long time.

    Although my client left me the keys to his apartment, the 'President' of the urbanisation has changed keys to the front entrance and so I can't get back into the building until June....

    Again, thankyou for your suggestions and I'm sorry it may take a while before I confirm what the problem was .

  9. #9
    Join Date
    Dec 2007
    Location
    Gloucestershire
    Posts
    8
    Rep Power
    0

    Re: Daikin U4 error code

    Hi, this might be too late but I think you will find the problem is that the outdoo runit has been switched into 'Emergancy' operation. This does two things; 1 The outdoor unit runs 24 hours 7 days, and 2 communication between the indoor and outdoor is stopped which is the U4 fault. The solution is to isolate the mains to the outdoor unit and switch DS1-1 to the off/down position and then turn the mains back on. Hope that helps.

  10. #10
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Daikin U4 error code

    what a noddy.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. DAIKIN - Weybridge: How to get a Quote.
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 25-04-2007, 08:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •