19-01-2008, 09:16 AM #1
Trane Chiller low temperature operation
I have installed a second hand Trane Air Cooled chiller that used to run on Chilled water but now needs to run on Glycol at -5*C, I have reset controlled to -5 but unit keeps tripping on LP, Superheat is good, suction is between 320 and 350 kPa when leaving gltycol is +4*C. I have been told there is a switch or jumper to change to brine operation but this is not mentioed in the manual I have. The chiller Model is CGAB050, with two x semihermetic comps on R22 with the RCMtype controller, Anyone have a manual to descibe where and what to change for low temp glycol operation
-
20-01-2008, 01:14 AM #2
Re: Trane Chiller low temperature operation
Depending on the options on the unit, there can be a lp pressostat on the suction line which you'll have to set to a pressure for a suitable one for your conditions.
On the RCM, there's also a frost setting.
If you send me a pm with your mail adres, I'll send you the list with settings!
-
20-01-2008, 07:18 AM #3
Re: Trane Chiller low temperature operation
Thanks Lowrider, The LP is a transducer, I can access the settings in the RCM, I would approeciate if you would send me the settings for RCM. my email address ******************** removed by admin
ThanksLast edited by WebRam; 20-01-2008 at 10:03 AM. Reason: dont post your email address, use the PM system
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
re ref. circuit
By shsalameh in forum FundamentalsReplies: 5Last Post: 06-08-2007, 12:59 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM