    Walk in Cooler (short cycling)



    I've got a quick question on a system I've been working on. The problem I am having is after the tstat is satisfied and the solinoid valve closes, the system pumps down and shuts off on low pressure. That is great but seconds after this process occurs my suction pressure rises quickly and short cycling occurs. Why the rapid pressure gain? I know that there should be some pressure rise but not that quick. Anybody have any thoughts on this condition? Thanks for the input




    P.S. I've got a full sight glass at the compressor after the filter drier. The system has a short line set and the refrigerant is R-22. Superheat at the compressor is 38F. Also it seems every morning the evap is iced up. After removing the ice the system operates as described above.



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi Brandon,
    possible
    causes are a passing liquid line solioide valve (dirt mechanical damage) or worn compressor valve plates.
    1/ strip and check, or just renew liquid line solinoide valve.
    2/ pump test compressor by lowering/shorting out L.P. cutout to see what level of vacumn the compressor will pull.
    Another possibility is the L.P. switch is set up incorrectly. Herefishy will tell you more about this, but basically you do not need to set the switch much lower than say 30psig, coming back in at say 50 to 55 psig.
    What is the settings on the L.P cutout?
    Regards. Andy

  3. #3
    Brandon's Avatar
    Brandon Guest
    I think the compressor is to blame. The valves in the compressor are probably damaged. When I started working on this system, I found it low on refrigerant. I would have to say in the past it had probably been "topped off" with liquid in the low side which we all know does wonders to the compressor. Thanks for the input

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34
    Grab the suction line and shut off the compressor. If there is a rush of hot gas coming from the direction of the compressor, the discharge valves are leaking. Not a positive test, but may indicate badly leaking valves. If the system is holding temperature during operation, the problem is more likely to be the solenoid valve. But again, not a positive test.

    Under stable operation, measure the following:

    Low side:

    Evap air in temp
    Evap air out temp
    SST (saturated suction temp) or pressure
    Suction line temp at coil outlet
    Suction line temp at comp inlet

    High side:

    Cond air in temp
    Cond air out temp
    SCT (saturated condensing temp) or pressure
    Liquid line temp at cond outlet
    Liquid line temp at TXV inlet

  5. #5
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    718
    Rep Power
    23
    I wonder if this may be a scroll compressor?

    Perhaps with a short lineset to the evaporator?

  6. #6
    Brandon's Avatar
    Brandon Guest
    No....its not a scroll. Its a 1/2 hp recip. 230 1ph. I have not seen any walk in coolers with a scroll compressor, but then again I have only been in the trade 6 years.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34
    Without a full set of temperature measurements, all we can do is guess. Guessing games are fun, but not very professional.

  8. #8
    Join Date
    Oct 2001
    Location
    New Jersey
    Age
    71
    Posts
    83
    Rep Power
    0
    Andy,

    Correct me if I'm wrong here. I was told never ever jump out the L.P. switch on a compressor and let it draw a vacuum. I always thought the reason was if there is a very minute leak somewhere it could draw air into the system. ???

  9. #9
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    718
    Rep Power
    23
    Actually, I was told by Copeland Engineering that the reason for wanting not to run a compressor in a vacuum in such a manner, is due to the possibility of the fusetite arcing to the compressor shell (ground).

    Admittedly this is a rare occurence, nonetheless a possibility and as such the reasoning.

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    That is great but seconds after this process occurs my suction pressure rises quickly and short cycling occurs.
    Depending upon the length of the line-set and low pressure control settings and the location of the liquid line solenoid, this could be okay. I didn't say that all that well, so it is time for a new paragraph.

    If the liquid line solenoid is at the compressor unit, there is a lot of liquid in the liquid line that can still feed through the expansion valve, causing suction pressure to rise when the compressor is stopped. It is not uncommon to to see periodic cycling of the compressor as it continues to pump down under these circumstances.



    I've got a full sight glass at the compressor after the filter drier. The system has a short line set and the refrigerant is R-22. Superheat at the compressor is 38F. Also it seems every morning the evap is iced up. After removing the ice the system operates as described above.
    Whoa there! Icing up every morning? You are not defrosting? The following advice from Andy comes to mind:

    causes are a passing liquid line solioide valve (dirt mechanical damage) or worn compressor valve plates.
    Forget the valve plate. Your liquid line solenoid is not closing.

    Okay. Now it is okay to think about the valve plate.

    But first things first.

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi Robearbam,
    shorting out an L.P can be done, but it is a good idea to establish if you have any lowside leaks first. If you were working on a NH3 blast freezer it would be running in a vaccum anyway.
    I have worked on quite a few poorly designed R22 low temp plant over the years that had to run in a vaccumn to acheive temperature. Most leaks are not on the low side, why would the lowside leak, after all it is under no great pressure.
    Shut the suction severice valve and run the compressor in a vac, a few second won't pull in that much air.
    I would be more worried about marginal lubrication during the test, rather than air getting in.
    Regards. Andy

  12. #12
    Join Date
    Oct 2001
    Location
    New Jersey
    Age
    71
    Posts
    83
    Rep Power
    0
    Hey Guys,
    I guess I should have specified that which I work on is older open drive stuff dependent on drive shaft seals and the ever so infamous refrigerant know as 12. When I was a kid this stuff was old. I do remember some of the older mechs then, telling me to pump it down at the end of the season but never let it go below zero PSI. Never let anyone pull a vacuum with a compressor. (Gas back then for this was around .79 cents a pound.) Guess I should have questioned it more at the time but, I didn't, so....now....I'm in the process of learning why....right here.

Similar Threads

  1. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 12:56 PM
  2. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  3. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 02:25 PM
  4. hermetic cycling times
    By bill1983 in forum Trouble Shooting
    Replies: 14
    Last Post: 23-12-2004, 05:47 AM
  5. freezer is now a cooler
    By superheat in forum Commercial
    Replies: 20
    Last Post: 18-03-2003, 01:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •