    Question Same run/dia different temp



    I have checked temps comming from the registers in two locations (two different bedrooms). The difference is 8 degrees!
    Checked for leaks either end - no luck there.
    Changed both ducts with new 6.0 r value runs. same diameter same lengths, no bends or separate attic areas.
    I do not know what is causing one to be 8 degrees lower than the other!
    Any help would help.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Tell us about the main duct these branch ducts are connected to. How far apart are the connections? How far from the end of the main duct? Did you use the same thermometer to measure each?

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, GOOSE2,
    what way is the flow balanced in this system? Have the flow dampers in the grills been set up for the design air volume?
    Regards. Andy

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Let's assume the air is at one temperature before it branches off the main duct.

    If this is a cooling question, the colder air must be the air delivered most swiftly and the warmer air must be moving much slower permitting greater heat transfer within the branch duct.

    If this is a heating question, the colder air must be the slower air for the same reasoning.

    Gary's and Andy's questions are addressing this consideration.

    Try this: restrict the air flow from the grill that has the desired temperature and see if the grill that is 8 degrees from the desired temperature achieves the desired temperature.

    If it does, you have an extremely imbalanced air flow. If it doesn't, then we need to think further.

  5. #5
    Join Date
    Apr 2003
    Location
    dfw, texas
    Posts
    5
    Rep Power
    0

    Same run/dia

    Hey Guys,
    First off thanks for the replies. I guess I did not provide enough info.
    Both runs come dirrectly out of the plenum at opposite ends. There are no obstructions in the plenum (ie dampers of any shape or form).
    I have no real technical way of determining the airflow through these, except that of the sheet of paper being deflected. I did try that (again not very scientific) yet both registers seem to deflect the paper the same amount.
    If I have missed any other info please let me know.
    I could understand a couple of degrees difference, but not 8!
    Oh, and I did use the same thermometer on both registers.
    Thanks again for all your help.
    Goose2

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    it could be that the air entering the plenum is at different temperatures as it comes off the coil/heat element (due to bypass factors) and then it is distributed down opposing ducts without having the chance to combine/eqalise.

    If this is so then an equalising grid on the inlet to the plenum would help. What is the distance from the coil/heat element to the plenum inlet?

    Frank

  7. #7
    Join Date
    Apr 2003
    Location
    dfw, texas
    Posts
    5
    Rep Power
    0

    Cool Same run/diameter

    Frank,
    The coils are located just prior to the plenum. The distance from the edge of the fins to the plenum mouth is 2.5 inches. the plenum mouth measures 22 x 22 x 48 and has a wedge shape with runs comming off 3 sides. Unit sits horizontally in attic.
    Thanks,
    Goose2

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Try taking temp measurements across the face of the fins and see if you get the 8F temp diff at this point

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I'm thinking a picture would be worth a thousand words.

    The plenum should be capped at the opposite end from the mouth. All branch connections should be off the sides at least a foot from the end. There should never be a connection in that end cap, as the air is being tossed directly into it, robbing the others.
    Last edited by Gary; 27-04-2003 at 09:30 PM.

  10. #10
    Join Date
    Apr 2003
    Location
    dfw, texas
    Posts
    5
    Rep Power
    0

    Smile Same run/diameter

    Success!
    I tapped the plenum in a different area (same face) where I had checked temp and the difference is now only 1 degree!
    Thanks for the tips to all who responded!
    GOOSE2

  11. #11
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I am no A/C-duct man, but could we have some other problem that we are bypassing by moving the location of the tap?

    I am thinking a long the line of an unevenly fed "A" coil, perhaps a restricted distributor tube or two. Or could we just have a poorly designed plenum?

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Good point - but if the coil is fed from the side with a restricted distributor etc then the coil would surely be even temp from left to right but not from south to north. The air temp leaving the coil would also be even from left to right etc.

    I think this problem is really down to a lack of space for the air temp to eqaulise as is bourne out by the statement that the plenum is only 2.5 inches from the coil and the take off ducts are at opposing ends.

    Frank

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  3. Condensing temp in refrigeration
    By anup in forum Fundamentals
    Replies: 1
    Last Post: 02-10-2005, 11:18 AM
  4. Multiplex For Low Temp and Medium Temp
    By allanbaker in forum Technical Discussions
    Replies: 0
    Last Post: 28-11-2002, 10:15 AM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •