    Stulz CSD542A PEC Aircon



    Anybody has any problems with this type of PEC aircon. Thanks



  2. #2
    Join Date
    Aug 2008
    Location
    MALAYSIA
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    what are the problem if i can share

  3. #3
    macbool's Avatar
    macbool Guest

    Re: Stulz CSD542A PEC Aircon

    Hi chimb and hasli,want any detail of stulz product,i am stulz employe.

  4. #4
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Stulz CSD542A PEC Aircon

    we have three of these

    in our biggest customers comm's room and having never worked on stulz products before i must say that they have been great,bar the odd room RH/return air sensor going, touch wood we have never had a problem with them and the UK technical backup has been very impressive
    Paul


    "KEEP IT COOL"

  5. #5
    Join Date
    Dec 2008
    Location
    England
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    I work for a company who are service agents for stulz in he North of UK. Any problems I would be happy to help where I can

  6. #6
    Join Date
    Oct 2007
    Location
    Cheshire, UK
    Age
    39
    Posts
    43
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    I got called to a problem with 2 Stulz units, C6000's. One was bringing fault code up for Compressor Low Pressure. Fixed this as it had a refrigerant leak.

    The 2nd was coming up with Compressor High Pressure. Checked all the obvious things like outdoor condensor fans, filters etc but after spending half a day onsite, I could not find why it would suddenly trip out on this fault. Pressures maintained a constant 55psi/220psi.

    Any ideas?

  7. #7
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Stulz CSD542A PEC Aircon

    Quote Originally Posted by Radlam View Post
    I got called to a problem with 2 Stulz units, C6000's. One was bringing fault code up for Compressor Low Pressure. Fixed this as it had a refrigerant leak.

    The 2nd was coming up with Compressor High Pressure. Checked all the obvious things like outdoor condensor fans, filters etc but after spending half a day onsite, I could not find why it would suddenly trip out on this fault. Pressures maintained a constant 55psi/220psi.

    Any ideas?

    what it one of these



    http://ats.stulz.com/uploads/pics/202_038_2_copy.jpg

    these floor mounted type are forever getting blocked condenser coil,did you disconnected the condenser fans and see if the HP switch if working correctly
    Paul


    "KEEP IT COOL"

  8. #8
    Join Date
    Dec 2008
    Location
    England
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    Look on wiring diagram to see what terminal the hp switch wires back to before going out to control circuit.Check all the connections for good contact and if ok then: From A1 on the terminal block which is your 24V supply wire in a bit of cable to link out pressure switch. With Gauges connected run the unit up and monitor the running pressures. If the prssures are good I would say you have a faulty hp switch, i have had a few go on me. Be warned that there is no shrader behind the hp switch when you come to changing one.

  9. #9
    zulkarnain's Avatar
    zulkarnain Guest

    Re: Stulz CSD542A PEC Aircon

    Quote Originally Posted by haslie View Post
    what are the problem if i can share
    In this case, please refer to Stulz it may help you.

  10. #10
    zulkarnain's Avatar
    zulkarnain Guest

    Re: Stulz CSD542A PEC Aircon

    Quote Originally Posted by Radlam View Post
    I got called to a problem with 2 Stulz units, C6000's. One was bringing fault code up for Compressor Low Pressure. Fixed this as it had a refrigerant leak.

    The 2nd was coming up with Compressor High Pressure. Checked all the obvious things like outdoor condensor fans, filters etc but after spending half a day onsite, I could not find why it would suddenly trip out on this fault. Pressures maintained a constant 55psi/220psi.

    Any ideas?
    Check your filter drier and change it.

  11. #11
    nileshbraut's Avatar
    nileshbraut Guest

    Re: Stulz CSD542A PEC Aircon

    Quote Originally Posted by chimbo View Post
    Anybody has any problems with this type of PEC aircon. Thanks
    I am in India, newly working on stulz units pls send me wiring diagram of PACs

  12. #12
    Join Date
    Apr 2007
    Location
    Italy
    Posts
    6
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    Hi nileshbraut , did you solve the problem on stulz aircon ?

    Alessio

  13. #13
    Join Date
    Jan 2008
    Location
    UK
    Posts
    20
    Rep Power
    0

    Re: Stulz CSD542A PEC Aircon

    Had similar alarm coming up on downdraught unit on startup so thought HP switch faulty, also had no wiring diagram. With help from Stulz UK decided problem was thermistor module on compressor, ordered replacement and unit worked ok. Comp was cold and control voltages were ok but dropped out on start up. If your compresser runs then stops could be compressor internal temperature getting to high

Similar Threads

  1. crazy 3rd-world idea: aircon from small fridge
    By lsemprini in forum Fundamentals
    Replies: 71
    Last Post: 29-05-2008, 01:10 AM
  2. Static pressure calculation for aircon duct
    By sparo in forum Air Conditioning
    Replies: 3
    Last Post: 29-03-2007, 11:28 PM
  3. Ducted AirCon Leaking into Ceiling
    By plucka99 in forum Air Conditioning
    Replies: 10
    Last Post: 15-03-2007, 03:22 PM
  4. Mercedes c 250d aircon
    By ddocwra in forum Transport
    Replies: 0
    Last Post: 23-09-2006, 04:34 PM
  5. dunham-bush split aircon unit
    By philly in forum Air Conditioning
    Replies: 4
    Last Post: 06-07-2006, 10:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •