Thread: Stulz CSD542A PEC Aircon
-
18-09-2007, 02:07 AM #1
Stulz CSD542A PEC Aircon
Anybody has any problems with this type of PEC aircon. Thanks
-
28-08-2008, 10:09 AM #2
Re: Stulz CSD542A PEC Aircon
what are the problem if i can share
-
14-02-2009, 12:14 PM #3
Re: Stulz CSD542A PEC Aircon
Hi chimb and hasli,want any detail of stulz product,i am stulz employe.
-
14-02-2009, 05:16 PM #4
Re: Stulz CSD542A PEC Aircon
we have three of these
in our biggest customers comm's room and having never worked on stulz products before i must say that they have been great,bar the odd room RH/return air sensor going, touch wood we have never had a problem with them and the UK technical backup has been very impressivePaul
"KEEP IT COOL"
-
14-02-2009, 10:53 PM #5
Re: Stulz CSD542A PEC Aircon
I work for a company who are service agents for stulz in he North of UK. Any problems I would be happy to help where I can
-
15-02-2009, 04:35 PM #6
Re: Stulz CSD542A PEC Aircon
I got called to a problem with 2 Stulz units, C6000's. One was bringing fault code up for Compressor Low Pressure. Fixed this as it had a refrigerant leak.
The 2nd was coming up with Compressor High Pressure. Checked all the obvious things like outdoor condensor fans, filters etc but after spending half a day onsite, I could not find why it would suddenly trip out on this fault. Pressures maintained a constant 55psi/220psi.
Any ideas?
-
15-02-2009, 04:56 PM #7
Re: Stulz CSD542A PEC Aircon
what it one of these
http://ats.stulz.com/uploads/pics/202_038_2_copy.jpg
these floor mounted type are forever getting blocked condenser coil,did you disconnected the condenser fans and see if the HP switch if working correctlyPaul
"KEEP IT COOL"
-
15-02-2009, 06:08 PM #8
Re: Stulz CSD542A PEC Aircon
Look on wiring diagram to see what terminal the hp switch wires back to before going out to control circuit.Check all the connections for good contact and if ok then: From A1 on the terminal block which is your 24V supply wire in a bit of cable to link out pressure switch. With Gauges connected run the unit up and monitor the running pressures. If the prssures are good I would say you have a faulty hp switch, i have had a few go on me. Be warned that there is no shrader behind the hp switch when you come to changing one.
-
10-04-2009, 04:10 AM #9
-
10-04-2009, 04:16 AM #10
-
28-01-2010, 07:48 AM #11
-
20-08-2010, 09:02 AM #12
Re: Stulz CSD542A PEC Aircon
Hi nileshbraut , did you solve the problem on stulz aircon ?
Alessio
-
21-08-2010, 03:05 PM #13
Re: Stulz CSD542A PEC Aircon
Had similar alarm coming up on downdraught unit on startup so thought HP switch faulty, also had no wiring diagram. With help from Stulz UK decided problem was thermistor module on compressor, ordered replacement and unit worked ok. Comp was cold and control voltages were ok but dropped out on start up. If your compresser runs then stops could be compressor internal temperature getting to high
Similar Threads
-
crazy 3rd-world idea: aircon from small fridge
By lsemprini in forum FundamentalsReplies: 71Last Post: 29-05-2008, 01:10 AM -
Static pressure calculation for aircon duct
By sparo in forum Air ConditioningReplies: 3Last Post: 29-03-2007, 11:28 PM -
Ducted AirCon Leaking into Ceiling
By plucka99 in forum Air ConditioningReplies: 10Last Post: 15-03-2007, 03:22 PM -
Mercedes c 250d aircon
By ddocwra in forum TransportReplies: 0Last Post: 23-09-2006, 04:34 PM -
dunham-bush split aircon unit
By philly in forum Air ConditioningReplies: 4Last Post: 06-07-2006, 10:24 PM