    Hi, was hoping someone could help with an outdoor pool heat pump that is not reaching or maintaining temperature.
    For the last 3 weeks the pool has had no cover. At first I thought this was the problem as ambient temperature is between 16-22C day and 8-12 night. But the customer says that pool has never maintained temp even when covered in warmer months.
    They have had two of these 60kw heat pumps on two matching pools. The first one lasted only one month before compressor failure. It was replaced with a 50kw unit that seems to be easily reaching temp (with a cover).
    Pool is 16m x 8m and holds 160,000lts. Set temp is 27C but is only reaching 21C to 25C depending on ambient temp, sunlight hours and wind.
    Do I just have too much heat loss due to evaporation, or another faulty unit? The owner is convinced that the heat pump is at fault and pool is due to close in one week (before cover is repaired).
    Heat pump uses 410A refrigerant,
    Air on 16.5C
    Air off 10.4C
    Discharge press 295psi, temp 51C
    Suction press 95psi, temp 10.5C
    Liquid line temp 26C
    Water in 24.5C
    Water out 28C
    Any help or ideas appreciated.



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Pool Heat Pump

    Quote Originally Posted by elvis View Post
    Hi, was hoping someone could help with an outdoor pool heat pump that is not reaching or maintaining temperature.
    For the last 3 weeks the pool has had no cover. At first I thought this was the problem as ambient temperature is between 16-22C day and 8-12 night. But the customer says that pool has never maintained temp even when covered in warmer months.
    They have had two of these 60kw heat pumps on two matching pools. The first one lasted only one month before compressor failure. It was replaced with a 50kw unit that seems to be easily reaching temp (with a cover).
    Pool is 16m x 8m and holds 160,000lts. Set temp is 27C but is only reaching 21C to 25C depending on ambient temp, sunlight hours and wind.
    Do I just have too much heat loss due to evaporation, or another faulty unit? The owner is convinced that the heat pump is at fault and pool is due to close in one week (before cover is repaired).
    Heat pump uses 410A refrigerant,
    Air on 16.5C
    Air off 10.4C
    Discharge press 295psi, temp 51C
    Suction press 95psi, temp 10.5C
    Liquid line temp 26C
    Water in 24.5C
    Water out 28C
    Any help or ideas appreciated.
    Your water flow through the condensor is to low.
    Check this first, water split and discharge should reduce, if corrected

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Pool Heat Pump

    Could the condenser perhaps be under-sized?

    What would typical pumping rates be for this kind of pool?

    My calcs show that currently, if the system were indeed delivering 60kW, that the balancing water mass flowrate would be around 246kg/min.

    What diameter water pipes connect to the system?
    Last edited by desA; 23-03-2010 at 11:05 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    elvis's Avatar
    elvis Guest

    Re: Pool Heat Pump

    Thanks. I will try adjusting water flow today and see if that makes a difference.
    The water connections are 50mm. The Heat pump is a Temperzone outdoor unit retrofitted with 3 x shell and tube heat exchangers in series.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Pool Heat Pump

    Quote Originally Posted by elvis View Post
    Thanks. I will try adjusting water flow today and see if that makes a difference.
    The water connections are 50mm. The Heat pump is a Temperzone outdoor unit retrofitted with 3 x shell and tube heat exchangers in series.
    So it is not a HOT WATER HEAT PUMP LIMITED model, just one that has been Knocked up.

  6. #6
    elvis's Avatar
    elvis Guest

    Re: Pool Heat Pump

    Sorry, yes it is HOT WATER HEAT PUMPS unit. Model 7GP60-3T.
    The name plate on electrical panel says it's a Temperzone OSA405RKTV.
    You were right about the low water flow. Pool cleaner has noted that water level keeps dropping below skim drains reducing water flow.
    Will check later today for an improvement.

Similar Threads

  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Replies: 10
    Last Post: 23-09-2010, 10:50 AM
  2. Addition of a heat pump to solar heating system
    By rt29781 in forum Heat Pumps
    Replies: 24
    Last Post: 23-01-2010, 09:46 AM
  3. Pool heat pump water side diagram
    By nike123 in forum Heat Pumps
    Replies: 23
    Last Post: 22-03-2009, 08:42 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. swimming pool heat pump
    By Andy AC in forum The Trail of Tears
    Replies: 8
    Last Post: 26-08-2007, 04:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •