Results 1 to 13 of 13
Thread: To charge or not to charge?
14-01-2008, 05:25 AM #1
Recently while working on a roof top unit for a walk in cooler, I came across the question of wether to charge or not to charge. R-22 *****. Ambient air outside @ 23 degrees. Hi side @ 155#. Lo side @ 12#. Sight glass is full. Cooler room temp is @ 39 degrees. Unit seems to recover rather quickly. I suspect a slight low charge. What would you do?
thanks-Fire and Ice
14-01-2008, 08:56 AM #2
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
Re: To charge or not to charge?
I would measure superheat, subcooling and temperature difference of evaporator and condenser, also compressor current and discharge temperature.
17-01-2008, 02:07 PM #3
I'm with Nike, I'd audit the system then determin where to go from there with certainty.
Is it cappilery tube or txv, this will tell you the most usefull messure.
Evap clean and all that sort of thing?
17-01-2008, 11:56 PM #4
Why do you think it needs more refrigerant?
18-01-2008, 12:10 AM #5
Only at the two extremes (grossly undercharged and grossly overcharged) does the amount of refrigerant in the system have anything to do with the head pressure.
Between these two extremes, the head pressure is almost entirely determined by the temperature and volume of air flowing through the condenser.
On a cool day, the head pressure is down. On a hot day, the head pressure is up.
Increase the airflow and the head pressure is down. Decrease the airflow and the head pressure is up.
Head pressure (aside from the extremes) is not about charge.
18-01-2008, 12:31 AM #6
19-01-2008, 04:29 PM #7
19-01-2008, 07:14 PM #8
19-01-2008, 07:56 PM #9
19-01-2008, 09:09 PM #10
what is the name of your book gary? It was once on Xtreme systems but the name has drifted off forever into cyber space!
I'd be interested in it.
20-01-2008, 12:03 PM #11
See the man's signature
20-01-2008, 04:00 PM #12
Or click on this link:
https://www.merchantamerica.com/tmethod/Last edited by Gary; 20-01-2008 at 04:02 PM.
20-01-2008, 08:11 PM #13
Ya I noticed that a bit after posting the question, thank you gary.
low charge or cap tube blockage?
By NC joe in forum CommercialReplies: 8Last Post: 02-09-2009, 02:53 PM -
Help please. How to charge a unit
By God55 in forum Air ConditioningReplies: 18Last Post: 23-03-2007, 10:07 AM -
Subcooling vs charge graph?
By Larry2 in forum FundamentalsReplies: 4Last Post: 01-12-2006, 07:40 PM -
Who's in charge?
By chillin out in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-10-2006, 10:51 PM -
How do you charge a car A/C
By dude in forum Air ConditioningReplies: 21Last Post: 02-04-2004, 09:36 AM