Results 1 to 24 of 24
    Jan 2008
    Australia
    9
    Free software for heat load calcs & sizing A/C units?
    Does anyone know where i can download some free software for calculating heat loads & sizing up A/C units?
    I need to size up a A/C unit for a bodybuilders gym with about 150 people in it at any 1 time pumping iron.
    May 2006
    India
    82
    1,013
    Re: Free software for heat load calcs & sizing A/C units?
    You may refer CoolPack. The link may already be in this forum. You will have to locate the same.
    Split Croatia
    57
    6,151
    36
    Coolpack software has module named "Cooling demand for air conditioned room"
    http://tinyurl.com/2x83d9
    May 2006
    India
    82
    1,013
    The Cool Pack download link is as follows :
    http://www.et.web.mek.dtu.dk/Coolpac...-download.html
    Jan 2008
    Australia
    9
    Thanks guys very good program
    BTW does anyone know where i can find the chart that tells you how many watts per sq meter you need for certain applications?
    Or even a good quick and easy heat load calc sheet??
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by eskimoair View Post
    Why do you need chart when you have software like that? Is this software very complicated for you?
    Jan 2008
    Australia
    9
    The software is great whilst im in the office but a quick reference chart would be great whilst out in the field when i need to quickly size up a unit for a customer.
    Of course the chart would have to be suitable for use is Sydney Australia.
    Aug 2007
    Sydney
    1,083
    23
    I find the AIRAH hand book the best for quick checks in the field, it's got all sorts of goodies in it. Made for Ausi + NZ. www.airah.org.au Ph 03 9328 4116. Good luck and welcome to the forum, I also work in Syd. 28 degs today, time for a beer.
    May 2006
    India
    82
    1,013
    Visit the undermentioned link, it may be of help.
    http://www.tombling.com/cooling/heat...calculator.asp
    Jan 2008
    Australia
    9
    thanks guys ive been looking for a copy of that hand book...........sweeeet.
    now it's time for a bundy & coke.
    Jan 2008
    Australia
    9
    Ok i have come up with 90kw can some one verify this is correct or calculate it using your software?
    Specs
    Type of Business
    Gym
    Brisbane Australia
    Area
    220sq/m
    Ceiling
    8m high from slab to the tin roof with insulation
    People
    120 people working out at peak times
    Peak Time
    3pm
    Walls
    4 external Besa Block walls
    Floor
    Concrete Slab
    Jan 2008
    Australia
    9
    anyone got experience sizing air con for gyms?
    Split Croatia
    57
    6,151
    36
    That is job for HVAC engneer to go on site and consider all in his calculations. He also need to calculate needed ventilation and heat gain and loss by ventilaton, maybe consider heat recovery and etc. That is not something what you could properly done on forum or by phone. Without considering all said, you could be pretty much off from really needed capacity.
    May 2006
    India
    82
    1,013
    Calculating the heat load, there are a large number of factors to be considered. Even while using the software, one has to have the basic knowledge and consider many factors. In the software you should put the proper inputs and then you can get the correct load. Otherwise follow your thumbrule .
    Jun 2006
    British West Indies
    543
    you would typically keep a gym cooler than say a house
    gym needs fresh air, you need to check your ventialtion load for your 120 people.
    the people will have a big gain also, probably 32 kW or there about, a lot of it will be latent.
    If ventilation air is more humid than normal room air, I think you will need either reheat or a dedicated dehumidifier
    Take the V out of HVAC and you are left with a HAC job
    Jun 2006
    British West Indies
    543
    have you accounted from the heat gain of the lighting?
    Jan 2008
    Australia
    9
    I have allowed for the metal halide lighting, yes.
    Just need to work out how much fresh air i need per person...........
    In coolpak it asks for the air change factor (ACF= the amount of times the air is completely changed over in a 24hour time peroid) is this where i enter how much fresh air i require?
    Split Croatia
    57
    6,151
    36
    In coolpak it asks for the air change factor (ACF= the amount of times the air is completely changed over in a 24hour time period) is this where i enter how much fresh air i require?
    You enter number 240 (10 complete air changes in 1 hour is standard here in Croatia for gym) for ACF.
    Also you need to consider windows, shading etc... , but Coolpack doesn't have that option
  19. #19
    May 2006
    India
    82
    1,013
    CoolPack has the Window details. There are a lots of option in it.
  20. #20
    Jan 2008
    Australia
    9
    Thanks nike123
    Can anyone from Australia chip in here? is 10 air changes an hour sufficient.
    The gym has no windows.......just a roller door which is permanantly shut.
  21. #21
    Split Croatia
    57
    6,151
    36
    I totally oversee that. I did not use Coolpack for that purpose for few years! You are right Samarjit Sen.
  22. #22
    Jan 2008
    Australia
    9
    so is 10 air changes correct?
    When i enter that coolpak sizes the unit up as being in excess of 400Kw
  23. #23
    Split Croatia
    57
    6,151
    36
    No, ACF means Air Change Factor and it is expressed in number of air changes per 24 hours. So, if you have 100 m3 of room volume and 10 air changes in hour that mean that you have 1000m3/h or 240ACF. You have possibility to enter both of these values selecting proper input on form field.
    Watch your units, they must be metric!
  24. #24
    Split Croatia
    57
    6,151
    36
    From my quick calculation you need 90 kW for fresh air and 35 kW for heat generated by peoples for 120 peoples and outdoor highest 35°C. I did not added here building transmission heat gain.
  1. Compressor loading, cooling, and range of operation.
  2. Cellar Cooling sizing software
    By Andy W in forum Tools and Calculators
    Last Post: 01-12-2006, 07:35 PM
  3. Free Software, Bèta vers.: Designbuilder
    By Peter_1 in forum Tools and Calculators
    Last Post: 05-01-2006, 12:01 AM
  4. Energy Plus Software - Free
    Last Post: 18-10-2004, 06:29 AM
  5. Energy PLus software FREE
    Last Post: 19-04-2004, 07:14 AM