09-01-2008, 05:36 AM #1
Suction and Discharge Temperatures for Ammonia Compressor Comparison
All,
Now I have received two quotations from two different suppliers for 100 HP Ammonia compressor. With in the quotation of the first supplier mentioning “that the his screw compressor is designed to provide 90.8 TR of refrigeration at 30 °F suction, and 90 °F discharge”. The second supplier mentioned his compressor is “100 HP screw compressor 74 Tons @ + 12 °F suction and 90 °F condensing”
My questions:
1-Are they comparing apple with apple?
2-How can we compare and know with different suction temperatures?
3-What does the change in suction temperatures effect?
And is there some thing else I have to know? and is there any trick with that?
Thanks in advance.
09-01-2008, 07:25 AM #2
Re: Suction and Discharge Temperatures for Ammonia Compressor Comparison
Hi power(N,6)!
i feel they have not give you some in common ground to compare.
if you wish to have better ideas, ask for their capacity chart. mostly it will be in +35degC condensing temp.
high suction temp >> high input power.
computation of motor power is also important because both may have very different factor uses.
09-01-2008, 04:52 PM #3
Compressor performance quotes are tricky to read. You were wise to question this.
Ask for the compressor performance to be quoted with the following:
Evaporating pressure
Suction line pressure loss
Suction pressure & temperature
Plus
Discharge pressure
Discharge line pressure loss
Condensing temperature
Amount of subcooling used
Then
Ask for the compressor displacement (CFM - the swept volume of the compressor at it's rated speed of rotation)
And,
Ask the vendors to provide the compressor capacity delivered and the power required at the operating conditions you specify.
If the compressor CFM of the two compressors is fairly close and the quoted performance is similar (based on the same operating conditions specified above) then and only then can you try to understand what you are buying.
NEVER, NEVER, just ask for a 100 HP compressor! That does not mean anything.
Let me guess...both quotes are from screw compressor salesmen, right?If all else fails, ask for help.
12-01-2008, 12:39 AM #4
Hi Iceman,
We are operating at the time being at 26 psi suction pressure.
Below is what I have got a reply from one of the suppliers (Dis not get any thing from the other):
1- Capacity Chart? ............................ 90.8 TR
2- Evaporating Pressure?....................... 30 degF
3- Suction line pressure loss?................. 2.0 psi
4- Suction pressure & temperature?............. 44.9 psig & 30degF
5- Discharge pressure?......................... 165.5 psig
6- Discharge pressure loss?.................... 5.0 psi
7- Condensing temperature?...................... 90 psig
8- Amount of subcooling used?................... 2.0 degF
9- Compressor displacement (CFM - the swept volume of the compressor at it's rated speed of rotation)
....186.9 CFM @ 3550 RPM
10-Compressor capacity delivered and the power required at the operation conditions? 90.8 TR using 93BHP
= 1.02 HP/TR producing 82DBA
11-Operating conditions? 30 degF & 90 degF
Is that what I have to get or some thing else?
Thanks.
12-01-2008, 01:49 AM #5
Well, the first problem is the compressor is rated for a suction pressure higher than you are currently running. (26 psig is about a 12°F saturation temperature while the quote says the compressor is rated at about 45 psig, which is a saturation temperature of about 30°F).
If the system runs at 26 psig, then the compressor should be rated at that condition.
I will say the rating data you provided looks like a reasonably well stated set of rated operating conditions because they include pressure losses (suction & discharge). However, I question the subcooling. You do not typically get subcooling on a condenser in a properly operating condenser. By adding the subcooling this tends to artificially increase the rated compressor capacity. In all likelihood, you won't get that capacity if you were running at 45 psig suction.
Without getting into a math exercise, the CFM you provided looks more like the gas volume flow at the rated condition. From a quick check I did, that's what it looks like instead of the compressor displacement. For now, I'm not going to worry about it.
I did quickly check the performance for a recip. compressor at the 45 psig & 90° condensing temperature... the BHP/Ton for a recip at these conditions is: 0.92, which is about 10% better than the screw compressor.
We are getting closer....If all else fails, ask for help.
16-01-2008, 07:06 PM #6
Hi Iceman,
Below is the reply for the second supplier:
1- Capacity Chart? - to follow
2- Evaporating Pressure? - Which evaporator are you asking about?
3- Suction line pressure loss? – This is function of the system piping not the compressor however past tests have shown that there is less than .5 psig between the LPR and the compressor suction. – The balance of the evaporator coils require higher suction pressures. The line losses were designed for approx 2 psig pressure drop.
4- Suction pressure & temperature? - Where are you asking about? The LPR should be around 25 to 26 Psig which would be 11 – 12 °F
5- Discharge pressure? - This is controlled by the size and setting of the condenser. Normally if everything is working properly your peak condensing temperature would be 90F or 165 Psig. I will be higher on start-up and on extreme high humidity days.
6- Discharge pressure loss? – The system was originally designed for 2°F pressure drop in the system discharge piping to the condenser.
7- Condensing temperature? - Original design 90F
8- Amount of subcooling used? – Subcooling is not used in the calculations of a system like this because typically there is none. Anything that appears from time to time under specific operating conditions is a bonus but cannot be counted on for system design.
9- Compressor displacement (CFM - the swept volume of the compressor at it's rated speed of rotation)? - to follow
10-Compressor capacity delivered and the power required at the operation conditions? - 74 Tons @12F SST, 90F SCT, and 98 BHP
11-Operating conditions? - 74 Tons @12F SST, 90F SCT, and 98 BHP
What exactly that means?
And Kindly I would ask you what does each mean?
Thanks.
17-01-2008, 02:21 AM #7
Interesting comments from all. To obtain a quotation for two similar compressors is not difficult, but the information from the suppliers needs to be interpreted correctly. Most Screw Compressor manufacturers have similar sized compressors. You will normally find that they all have a relativley similar COP, Swept Volume, Absorbed Power etc. However most manufacturers performance data is based on what is occurring at the compressor ports. They do not normally allow for system line loss unless specifically asked to do so. Just ensure your conditions for each option are the same to ensure an accurate comparison of performance data.
discharge superheat
By philjd26 in forum Trouble ShootingReplies: 8Last Post: 09-01-2008, 07:48 AM -
suction and discharge head for parallel compounding compressors
By herman in forum CommercialReplies: 1Last Post: 11-10-2006, 08:32 PM -
Interesting Problem
By NH3LVR in forum Industrial CompressorsReplies: 13Last Post: 12-08-2006, 10:27 PM -
Bearing trouble - rotary compressor
By rosetennis in forum Industrial CompressorsReplies: 6Last Post: 18-05-2006, 01:26 AM -
temperatures of the suction and discharge lines
By VIXS in forum Air ConditioningReplies: 4Last Post: 17-05-2006, 07:18 AM