    humidity inside refrigerant circuit



    hi
    in a R404A refrigerant circuit , the high rate of humidity 900ppm could induce the formation of ice beans located inside the elbow of evaporator operating at -30°c. ( the phenomenon is called ice bean effect). The situation could lead to create a big force on the elbow and then leakage on the welding.
    Do you think this situation is so probable?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: humidity inside refrigerant circuit

    It is more likely that, before that occurs, you end up with capillary tube or TEV blocked by ice.
    Correct me if I am getting something wrong here.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: humidity inside refrigerant circuit

    And with modern refrigerants/oils, an acidic oil mixture that eaten the windings resulting in a burnout.

  4. #4
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: humidity inside refrigerant circuit

    yeah .. mos cases, high moisture content in refrigeration piping will cause immediate chockages at high flow low pressure areas ... expansion valves & solenoid valves.

    that will be good signs & symptoms for immediate remedies. cheers

  5. #5
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: humidity inside refrigerant circuit

    hi,

    yes, the biggest problem you will finally have in the mid term is a more than probable burn out, due to the acidity in the circuit.

    I recomend you to clean it properly, recycling the 404A, and flushing correctly the circuit with the correct system.

  6. #6
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: humidity inside refrigerant circuit

    Quote Originally Posted by sakly View Post
    hi
    in a R404A refrigerant circuit , the high rate of humidity 900ppm could induce the formation of ice beans located inside the elbow of evaporator operating at -30°c. ( the phenomenon is called ice bean effect). The situation could lead to create a big force on the elbow and then leakage on the welding.
    Do you think this situation is so probable?

    Are you sure its moisture, as per the previous posters you would have serious blockages first.

    Is the system new? reason i ask is a few years ago i read a piece about a coil manufacture using a cleaning/flushing agent when making the coil, if this agent was not totally removed and the coil was flushed with refrigerant (I.E used with-in the month) the cleaning agent used to eat its way through the copper (i think they called it copper worm) it was noted that it only happened when the coil had been stood for a few months with residues of the cleaning agent still in it.

  7. #7
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: humidity inside refrigerant circuit

    inserting cleaning agents, solvents, base substances is inserting more dirt and residues difficult to extract afterwards in the circuits.
    It is better to clean porplerly the system with the same refrigerant from the equipment.

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. How critical are circut lengths when using a distributor?
    By kengineering in forum Technical Discussions
    Replies: 17
    Last Post: 27-02-2006, 07:35 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Twin Circuit RTU Humidity Control Modification
    By bernie in forum Trouble Shooting
    Replies: 40
    Last Post: 18-03-2002, 12:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •