12-01-2008, 11:44 PM #1
Re: Hitachi Summit 2.5kW Failed!
No, the defrost is OK - I mean the outdoor ambient was about freezing. The system was working fine when I left it, but come the morning it would not run, the indoor unit indicating outside unit failure.
It then would not work again, regardless of power cycles etc., for a couple of days. I then left it for the rest of a week, after which it again runs fine!
-
12-02-2008, 01:01 PM #2
Re: Hitachi Summit 2.5kW Failed!
Hi, in case anyone is interested.
Supplier duly provided crankcase heater which I installed under their direction:
http://sittingbourne.homeserver.com/...ssorHeater.jpg
As it happens it's been really cold past few days, well below freezing on occasion, but system is running perfectly and no lock-outs .
Apparently the lock-out occurs only with thermoplastic tubing, not on copper. Not too sure why.
So final step I'm going to mount a frost-stat in a weatherproof box to control the heater, so it's only on when actually needed.
Thanks again!