    Re: Hitachi Summit 2.5kW Failed!

    No, the defrost is OK - I mean the outdoor ambient was about freezing. The system was working fine when I left it, but come the morning it would not run, the indoor unit indicating outside unit failure.

    It then would not work again, regardless of power cycles etc., for a couple of days. I then left it for the rest of a week, after which it again runs fine!

  2. #2
    Join Date
    Jan 2008
    Location
    Kent
    Age
    47
    Posts
    46
    Rep Power
    0

    Re: Hitachi Summit 2.5kW Failed!

    Hi, in case anyone is interested.

    Supplier duly provided crankcase heater which I installed under their direction:
    http://sittingbourne.homeserver.com/...ssorHeater.jpg

    As it happens it's been really cold past few days, well below freezing on occasion, but system is running perfectly and no lock-outs .

    Apparently the lock-out occurs only with thermoplastic tubing, not on copper. Not too sure why.

    So final step I'm going to mount a frost-stat in a weatherproof box to control the heater, so it's only on when actually needed.

    Thanks again!

Similar Threads

  1. Hitachi CCU420-2
    By amber in forum Air Conditioning
    Replies: 1
    Last Post: 19-11-2007, 02:24 PM
  2. Hitachi Inverter Systems
    By Vishnukurup in forum Air Conditioning
    Replies: 13
    Last Post: 15-11-2007, 01:15 PM
  3. Hitachi Details
    By Slim R410a in forum Air Conditioning
    Replies: 4
    Last Post: 29-06-2006, 10:20 AM
  4. Hitachi timeclock
    By rbartlett in forum Air Conditioning
    Replies: 2
    Last Post: 21-06-2006, 09:49 PM
  5. F**K Hitachi
    By rbartlett in forum Air Conditioning
    Replies: 38
    Last Post: 24-10-2005, 05:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •