    Cool Reversing valve problem?



    Being new to heat pumps reversing valves are also new. An air con unit works fine on "forced" cooling but when I try on heat mode the compressor starts for a while and then cuts out. The solenoid is o.k.This fault happened after topping up the unit. Is the valve at fault?Has it stuck in cooling mode?Has it frozen in position? Any ideas



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem?

    Quote Originally Posted by coffeebreak View Post
    Being new to heat pumps reversing valves are also new. An air con unit works fine on "forced" cooling but when I try on heat mode the compressor starts for a while and then cuts out. The solenoid is o.k.This fault happened after topping up the unit. Is the valve at fault?Has it stuck in cooling mode?Has it frozen in position? Any ideas
    Did you recover refrigerant and then charged by weight?
    It looks like overcharging.

  3. #3
    Join Date
    Jan 2008
    Location
    Spain
    Posts
    14
    Rep Power
    0

    Re: Reversing valve problem?

    the unit was operating poorly in heat mode so after checking pressures i topped up refrigerant. the problem occured after this. Is it just a case of removing some refrigerant or is there another option?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem?

    Quote Originally Posted by coffeebreak View Post
    the unit was operating poorly in heat mode so after checking pressures i topped up refrigerant. the problem occured after this. Is it just a case of removing some refrigerant or is there another option?
    When you checking pressures you also need to check temperatures, air quantities and humidity in order to know what is happening in air conditioner. Simply checking discharge pressure cannot tell you that system is undercharged or overcharged.
    In order to simply, surely and quickly establish what is going with split-type air conditioner, easiest thing to do is (by my experience) to recover and weigh refrigerant and then act accordingly.
    It takes about half hour to find about lot of things.
    In the meantime you could chit-chat with customer and even drink 1 beer.

  5. #5
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: Reversing valve problem?

    Nice one, Nike123,
    You sound like my good Czech colleagues in Prague & Kolin - they invariably take me for " good Czech food " whenever I visit - dumplings & beer, more dumplings and beer !

    regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem? OT

    Quote Originally Posted by thermo prince View Post
    Nice one, Nike123,
    You sound like my good Czech colleagues in Prague & Kolin - they invariably take me for " good Czech food " whenever I visit - dumplings & beer, more dumplings and beer !

    regards
    T-P

    I understand them, this is my favorite supplier of parts :

    http://www.mediafire.com/imageview.p...zdntgm&thumb=4
    http://www.mediafire.com/imageview.p...2gnyj0&thumb=4

    Guess, what is my favorite part!

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reversing valve problem?

    Coffebreak, do not 'top-up' when in heating mode. Your superheat readings will go haywire.

    Do not 'top-up' at all. If it was short then find the leak and recharge by weight.

    Reversing valves need a pressure differential across them to operate, if the system has pressure problems then the valve may not work correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jan 2008
    Location
    New Zealand
    Age
    50
    Posts
    27
    Rep Power
    0

    Re: Reversing valve problem?

    Coffee , is the unit going out on high or low pressure??
    What sort of expansion valves does the unit have?
    There could be a problem with one of the Txv if these are in the unit, I had a similar problem lately , thought it was reversing valve not fully moving, but turns out it was the power head on the indoor unit. The unit would work on heating but on cooling low pressure would drop into vacumm.
    hope that is some help

  9. #9
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Reversing valve problem?

    Are all the fans working? What is it cutting out on? overload, HP cut out, thermistor protection (eg compressor discharge over heat)

  10. #10
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: Reversing valve problem?

    Hey there..yep,best to recover and recharge by weight...does the compressor automatically restart or is it manually done?Best to check the wiring to the comp to see where it stops...hope it helps...

  11. #11
    Join Date
    Sep 2007
    Location
    Norfolk uk
    Age
    61
    Posts
    38
    Rep Power
    0

    Re: Reversing valve problem?

    hi, just a thought is the air handler too small for the condensing unit, i had a similar problem with the air handler too big and if charged for heating it flooded the condenser in cooling and tripped on hp.

  12. #12
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: Reversing valve problem?

    one of our young engineers is having a problem with sinilar fault at the moment, i have been trying to find some idagnostic info on these valves ( had some somewhere but cant find it now!!! )
    anybody got any links to info ?

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem?


  14. #14
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: Reversing valve problem?

    thanks Nike 123 i have printed that for him,

    why do the posts come up a different way round when i log in to the way they are when i am just browsing???

  15. #15
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: Reversing valve problem?

    how can you say to recharge the system! unless im missing something he did nt even tell us what the pressures where!
    there could be problem with the defrost control, it could be anything!
    Last edited by jason09; 17-02-2008 at 08:17 AM.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem?

    Quote Originally Posted by davej View Post
    thanks Nike 123 i have printed that for him,

    why do the posts come up a different way round when i log in to the way they are when i am just browsing???
    I really don't know.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Reversing valve problem?

    Quote Originally Posted by jason09 View Post
    how can you say to recharge the system! unless im missing something he did nt even tell us what the pressures where!
    there could be problem with the defrost control, it could be anything!
    Yes, you are missing!
    This fault happened after topping up the unit.

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Reversing valve problem?

    Unfortunately, a great many service techs believe that pressures are a direct indicator of refrigerant charge. Sorry, it doesn't work that way.

    At the extremes (grossly undercharged or grossly overcharged), yes the pressures are about the charge.

    In between those extremes, the pressures are almost entirely about the temperature and volume of the air flowing through the coils.
    Last edited by Gary; 28-02-2008 at 05:53 PM.

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reversing valve problem?

    Quote Originally Posted by davej View Post
    why do the posts come up a different way round when i log in to the way they are when i am just browsing???
    It depends on how you have set up your account to view the forum.

    When 'just browsing' you are at the forum defaults.

    When you log in then you are at 'your' defaults.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  2. quiet 4 way reversing valve
    By steveg in forum Air Conditioning
    Replies: 7
    Last Post: 06-10-2006, 11:27 AM
  3. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •