    Daikin Inverter R22



    Hello Guys,

    I need to fix a 4 year old Daikin Inverter (Indoor) Model# FTKD50BVMA I'm getting U4 Error Code. What could this be. Thanks!!!
    Last edited by air4life; 03-01-2008 at 04:17 AM. Reason: Got more info



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: Daikin Inverter R22

    Welcome to the forum air4life.
    Not equipment I normally work on. So maybe some of the other guys can elaborate further.
    The info I have says that U4 is a communication fault between the indoor and outdoor units.
    Grizzly

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin Inverter R22

    The "normal" fault when it flashes U4 is that someone turned the power off to either the outdoor unit or another indoor unit on the same system.

    Otherwise you are looking at communication wires or PCBs.

Similar Threads

  1. Hello and help please with daikin inverter
    By classic in forum Air Conditioning
    Replies: 8
    Last Post: 09-09-2010, 10:48 PM
  2. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 11-03-2010, 11:25 PM
  3. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  4. Problem with an inverter compressor in V.R.V system DAIKIN R 407
    By Harris Greece in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 12:53 AM
  5. new daikin inverter kit
    By allyjg30 in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2007, 12:04 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •