29-12-2007, 02:39 PM #1
vac pumps
what types do you use
seem to be having a lot of burn't out vac pumps that are dual voltage, but only ever used on 110v. the wiring has been correctly changed
reccomend me a 110 and a 240 one please
anyone else have probs??
-
29-12-2007, 04:47 PM #2
Re: vac pumps
Hi Refaircon
We tend to use the Robiaire Vaccum Pumps mainly.
I allways save an older one for when using on Ammonia systems.
They are allways 110V Surely the 240v option is illegal for site use?
In fairness there are plenty of other makes as well and I have not heard of a bad one!
Maybe you are not sizing the pump to the job and causing the pump motor to overheat. Only you can answer that one.
I did have one burn out on me once and that was were a site Electrician converted it from 240v to 110v (back in the old days before it was mandatory)to allow me to use it onsite. Maybe thats the common thread?
GrizzlyLast edited by Grizzly; 29-12-2007 at 05:21 PM. Reason: did not read the original post fully
-
29-12-2007, 05:03 PM #3
Re: vac pumps
hi their,
i have a javac shark (240v) and duel voltage robinaire both are as good as one another
-
29-12-2007, 05:20 PM #4
Re: vac pumps
Hi
I've been using YellowJacket vac pumps for eight years with no trouble (on 240 v) To switch to 110 v you need to change the wiring connections around. When i was at the RAC show the YellowJacket rep said that for the pump to meet regulations (which regulation i don't know) you need a postive action to switch voltage use e.g. swapping wires, switching a switch as on other makes was not 'allowed' as its not a deliberate enough action (Switch could get knocked, maybe this could be a cause of the burnouts)
Also as i'm sure you know, in the cold weather we are having at the moment many pumps will struggle to start. A friend of mine keeps his pump in the cab to ensure its oil is warm enough to start ok. Why don't they fit a heater?
Jon
-
29-12-2007, 05:51 PM #5
Re: vac pumps
???
As someone who did my apprenticeship and the first 10 years of my working life in Sweden (which is ever so slightly colder than the UK), I never experienced vacc pumps not starting because they are cold (even thou sometimes it was colder outside than in the freezers).
The only reason I can see for a vacc pump to be affected by the cold is if there is moisture in the oil (and then it would be down to you not looking after it)...
-
29-12-2007, 06:58 PM #6
Re: vac pumps
Hi Viking,
check out
http://www.yellowjacket.com/questions.asp
and click on the vac pump cold weather starting link
Cheers Jon
-
29-12-2007, 07:54 PM #7
Re: vac pumps
So, I was right!
(Somehow, I can not see the extreme cold bit being relevant here in UK before the next ice age)
Thank you MS for a nice link.
-
29-12-2007, 08:53 PM #8
Re: vac pumps
The moral of the story is don't use Yelow Jacket when it's cold then?
MS you say you have been using YJ for 8yrs without trouble. Then why throw in the curve ball about the cold starting?
More importantly can 1 of our trainers tell me what is the score with using 240v and site work please.
As far as I know it is not allowed to trail 240v leads???
Help please!
Grizzly
-
30-12-2007, 12:38 AM #9
Re: vac pumps
Good evening everyone
What is the easiest way to size up a vacuum pump to the system?
Thanks
-
30-12-2007, 12:40 AM #10
-
30-12-2007, 12:52 AM #11
Re: vac pumps
Taken from the website given above...
Frequently Asked Questions
1. How can I select the right pump cfm?
The following guidelines are for domestic through commercial applications.
System size (tons) Pump cfm
1-10 1.5
10-15 2.0
15-30 4.0
30-45 6.0
45-60 8.0
60 and above 11.0Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-12-2007, 12:54 AM #12
Re: vac pumps
I have used the same dual voltage YJ for 8 years as well, no probs at all. It is usually set to 110v.
There are two ways you can use 230v on site. One is to plug into an RCD only when no 110v alternative is available and keep you leads as short as possible. The other is not strictly correct but ALL service engineers use it up and down the country when time is short........
Come one chaps who else has made up a lead to take 230v of a condensing unit?
We always fit a fused 5a socket inside our VRV/VRF's now
Saves no end of time
eggs
-
30-12-2007, 12:59 AM #13
Re: vac pumps
No big thing Rob other than I am confused as to wether it is acceptable practice that's all.
As I asked earlier I was hoping someone can advise.
I appreciate as you said your problem is with the 110v version. But it made me wonder are we allowed to use 240v and if so when?
Also as I said earlier the only time I can remember a motor failure was after I had, had 240v motor changed to 110v.
Your question is still relevant.
Grizzly
-
30-12-2007, 01:53 AM #14
-
31-12-2007, 03:26 PM #15
-
31-12-2007, 04:05 PM #16
-
31-12-2007, 04:41 PM #17
Re: vac pumps
Same here and it's a pain when told "Just pop down the road" (30 to 40 ml) to get a replacement from the nearest Wholesaler.
When you get there you find your on stop. Because any one of the numerous depots we have are in "dispute". Therefore the whole company is Temporarilly Black listed. Sound Familiar?
Has the burn out problem resolved itself or is it still ongoing?
Grizzly
Similar Threads
-
Precaution in Liquid ammonia Pumps operations
By smpsmp45 in forum NH3Replies: 13Last Post: 29-03-2008, 05:12 PM -
High Altitude Heat Pumps
By Grog in forum Air ConditioningReplies: 2Last Post: 23-03-2007, 09:30 AM -
Vacuum pumps
By Andy AC in forum Tools and CalculatorsReplies: 9Last Post: 04-03-2007, 10:24 PM -
NH3 Recirculation pumps
By lraja in forum NH3Replies: 7Last Post: 16-11-2006, 08:17 PM -
Heat Pumps
By US Iceman in forum IndustrialReplies: 11Last Post: 14-04-2006, 07:29 PM