    Unhappy ICS Danfoss valve



    Hallo,

    I've mount an ICS 40 ( EVM pilot and pilot external connection on hot gas pipe) on suction line of ammonia pumped system. I want to use it for defrost cycle.

    Maybe it is not the happiest solution ( I think PMLX would be better) but I've done it.

    I've start up the plant and, after defrost the ICS can't open.

    I think the reason are:

    - dirty into the pipe
    - the hot gas is not enaugh for opening the ICS

    What are your opinion about it?



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: ICS Danfoss valve

    Quote Originally Posted by jax1 View Post
    Hallo,

    I've mount an ICS 40 ( EVM pilot and pilot external connection on hot gas pipe) on suction line of ammonia pumped system. I want to use it for defrost cycle.

    Maybe it is not the happiest solution ( I think PMLX would be better) but I've done it.

    I've start up the plant and, after defrost the ICS can't open.

    I think the reason are:

    - dirty into the pipe
    - the hot gas is not enaugh for opening the ICS

    What are your opinion about it?

    If the pressure inside the evaporator is to high you will have no pressure difference between the hotgas line and the inside of the evaporator, that's why the valve wont open.

    there is a small hole in the piston of the valve piston that bleeds the pilot pressure when the EVM closes, so the valve returns to closed position.

    so if the hotgas pressure is to low you will not be able to open the valve after a defrost cycle. I had the exact same problem a few weeks ago on a new installation, I had to open the OFV valve a little bit to lower the pressure inside the evaporator, and just to be on the safe I also raised the hotgas pressure a little bit.


    The main problem was when the operators left it to long between defrost and freezing, making the compressor reduce capacity.

    If you mounted the damping nozzle on the EVM I would suggest you drill it up by atleast 1 mm as the normal size is the same as the bleed hole in the PM's piston, making it harder for the valve to open if the pressure difference is on the small side
    -Cheers-

    Tycho

  3. #3
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: ICS Danfoss valve

    How'd it go?
    -Cheers-

    Tycho

  4. #4
    Join Date
    Oct 2006
    Location
    Romania
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: ICS Danfoss valve

    very good, indeed

Similar Threads

  1. FRICK TDSH 233 Slide Valve and guide damaged
    By 404cab in forum Industrial Compressors
    Replies: 9
    Last Post: 30-07-2008, 11:24 PM
  2. Danfoss PHTQ Valve
    By dallan in forum Industrial
    Replies: 5
    Last Post: 29-07-2006, 11:25 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •