    Calculating Performance



    In order to check whether a high wall split type air conditioner of 24000 BTU/hr is producing its rated capacity in cooling mode I took the following readings from the place :
    Indoor Unit
    1-Dry bulb temp. of entering air = 80 F.
    2-wet bulb temp of entering air = 67 F.
    3-Leaving dry bulb temp of air = 60.8 F.
    4-Leaving wet bulb temp of air = 57.2 F.
    5-Air entering indoor unit cfm = 700 cubic ft/min.

    I checked the outdoor dry bulb temp of air = 95 F.

    Here I dont know if I have to take a ventilation effect in the calculations or not ,( but if it is exsists, where does it come from ?) so I didnt take it in regard.

    When I put these informations on the psychrometric chart the result was far away from the nominal rated mentioned on the nameplate ,where is the mistake please help?

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating Performance

    That is about 14000 Btu of sensible heat.
    You need to give us more details in order to give you any meaningful answer.
    Pressures and temperatures of refrigerant in various part of air-con. are needed to tell you what is wrong with your unit.

  3. #3
    Join Date
    Dec 2007
    Location
    Saui Arabia
    Posts
    12
    Rep Power
    0

    Re: Calculating Performance

    Quote Originally Posted by Mohammed Qasim View Post
    In order to check whether a high wall split type air conditioner of 24000 BTU/hr is producing its rated capacity in cooling mode I took the following readings from the place :
    Indoor Unit
    1-Dry bulb temp. of entering air = 80 F.
    2-wet bulb temp of entering air = 67 F.
    3-Leaving dry bulb temp of air = 60.8 F.
    4-Leaving wet bulb temp of air = 57.2 F.
    5-Air entering indoor unit cfm = 700 cubic ft/min.

    I checked the outdoor dry bulb temp of air = 95 F.

    Here I dont know if I have to take a ventilation effect in the calculations or not ,( but if it is exsists, where does it come from ?) so I didnt take it in regard.

    When I put these informations on the psychrometric chart the result was far away from the nominal rated mentioned on the nameplate ,where is the mistake please help?

    Thanks
    you have to add latent load to sensible load

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating Performance

    Quote Originally Posted by Gaafar View Post
    you have to add latent load to sensible load
    In this particular case there is no latent heat because there is no condensation of water. Put his readings on Mollier chart and you will see that condensation didn't occurred.

  5. #5
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Calculating Performance

    Here's what I got from your readongs:
    Total Cooling Btu/hr 20,430
    Sensible Cooling Btu/hr 14,856
    Latent Cooling Btu/hr 5,574
    Tons of Cooling 1.7
    CFM per Ton Leaving Coil 411.2
    Sensible Heat Ratio 0.73
    Dry Bulb TD 19.2°
    Enthalpy Difference 6.52 Btu/lb
    Mass Air Flow Rate 3152.87 lb/hr
    CFM Entering Coil 727.7 ft³/min
    Apparatus Dew Point 54.2°
    Bypass Factor 0.26
    Last edited by wambat; 24-12-2007 at 04:56 AM.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating Performance

    I made some mistakes during conversion from imperial to SI units.
    Wambat, what software is this?
    Last edited by nike123; 27-12-2007 at 09:03 PM.

  7. #7
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Calculating Performance

    Entering Air 80/67, v=13.845 ft^3/lb da, h=31.51 Btu/lb da, Dewpoint about 60.3F, grains of mositure 78.6/lb da, 700 CFM

    Leaving air, 60.8/57.2, h=24.58 Btu/ lb da, grains of moisture 64.3/lb da, dewpoint about 54.9F

    total cooling is about 700/13.845x60x(31.51-24.58)= 21,023 Btu/hr



    s

Similar Threads

  1. Calculating heat load
    By Abe in forum Technical Discussions
    Replies: 13
    Last Post: 13-08-2010, 05:40 PM
  2. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  3. Screw compressor performance
    By faryuki in forum Industrial Compressors
    Replies: 12
    Last Post: 17-12-2007, 03:50 AM
  4. Low System Performance (Hunting ?)
    By rhlg in forum Technical Discussions
    Replies: 31
    Last Post: 25-10-2006, 01:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •