Thread: Calculating Performance
21-12-2007, 11:07 PM #1
In order to check whether a high wall split type air conditioner of 24000 BTU/hr is producing its rated capacity in cooling mode I took the following readings from the place :
Indoor Unit
1-Dry bulb temp. of entering air = 80 F.
2-wet bulb temp of entering air = 67 F.
3-Leaving dry bulb temp of air = 60.8 F.
4-Leaving wet bulb temp of air = 57.2 F.
5-Air entering indoor unit cfm = 700 cubic ft/min.
I checked the outdoor dry bulb temp of air = 95 F.
Here I dont know if I have to take a ventilation effect in the calculations or not ,( but if it is exsists, where does it come from ?) so I didnt take it in regard.
When I put these informations on the psychrometric chart the result was far away from the nominal rated mentioned on the nameplate ,where is the mistake please help?
22-12-2007, 10:43 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Calculating Performance
That is about 14000 Btu of sensible heat.
You need to give us more details in order to give you any meaningful answer.
Pressures and temperatures of refrigerant in various part of air-con. are needed to tell you what is wrong with your unit.
23-12-2007, 03:14 PM #3
23-12-2007, 08:31 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
24-12-2007, 04:17 AM #5
Here's what I got from your readongs:
Total Cooling Btu/hr 20,430
Sensible Cooling Btu/hr 14,856
Latent Cooling Btu/hr 5,574
Tons of Cooling 1.7
CFM per Ton Leaving Coil 411.2
Sensible Heat Ratio 0.73
Dry Bulb TD 19.2°
Enthalpy Difference 6.52 Btu/lb
Mass Air Flow Rate 3152.87 lb/hr
CFM Entering Coil 727.7 ft³/min
Apparatus Dew Point 54.2°
Bypass Factor 0.26Last edited by wambat; 24-12-2007 at 04:56 AM.
25-12-2007, 08:15 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
I made some mistakes during conversion from imperial to SI units.
Wambat, what software is this?Last edited by nike123; 27-12-2007 at 09:03 PM.
27-12-2007, 06:08 PM #7
Entering Air 80/67, v=13.845 ft^3/lb da, h=31.51 Btu/lb da, Dewpoint about 60.3F, grains of mositure 78.6/lb da, 700 CFM
Leaving air, 60.8/57.2, h=24.58 Btu/ lb da, grains of moisture 64.3/lb da, dewpoint about 54.9F
total cooling is about 700/13.845x60x(31.51-24.58)= 21,023 Btu/hr
s
Calculating heat load
By Abe in forum Technical DiscussionsReplies: 13Last Post: 13-08-2010, 05:40 PM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Screw compressor performance
By faryuki in forum Industrial CompressorsReplies: 12Last Post: 17-12-2007, 03:50 AM -
Low System Performance (Hunting ?)
By rhlg in forum Technical DiscussionsReplies: 31Last Post: 25-10-2006, 01:05 AM