    charging a system



    hi guys
    talking to old school fridge engineer the other day and he was talking about how he used to charge systems till one of the lines frosted up then release refrigerant till it chased back ???
    can anyone expand on this old teqnique
    cheers



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: charging a system

    Hmm,

    Dosn't sound like good engineering practise.

    But I have seen it done.

    It will only work on capillary (or fixed orifice) units and has never been considered good engineering practice.

  3. #3
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: charging a system

    did this used to be a common practice???(thaks for the quick reply)

  4. #4
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: charging a system

    Yes, it was common practice. Years ago electronic scales did not exist and charging columns (stills) were very expensive so the easiest method was to overcharge & let a bit out.
    Today of course that would be illegal.

  5. #5
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: charging a system

    very much so

  6. #6
    panas's Avatar
    panas Guest

    Re: charging a system

    Hello!
    It's my first post for this forum. I am new in this field. I am from Israel. I can the only add that this method of charging is one of the populare in Israel nowdays too. Why? It's simple and enough effective. Don't need to study much. If one need to start he would beging by this way. But I am going to learn and practice the modern charging methods now by help of this forum.

  7. #7
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: charging a system

    thanks jollycold a very detailed and informative reply into past techniques ( or maybe not so past in some cases????)

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    13
    Rep Power
    0

    Re: charging a system

    this was used on capillary systems if you were unsure of refrigerant charge,over chargeing system on capillary would cause the suction to frost back to compressor ,then letting enough refrigerant out would cause the frost line to drop of suction.this was when you new you had the charge right, of course this practice is highly illegal today especially in australia.due to refrigerant licensing laws.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: charging a system

    Good method, when charging, is that you put some good (precise) thermometer on suction line and CAREFULLY monitor temp. As you adding refrigerant, temperature of suction line, in some point, will start to rapidly fall (in comparison to temperature change before). This is point where you are in 5% of correct charge. Now carefully add refrigerant by monitoring superheat and sub cooling to required values.
    I draw some chart to illustrate this.

    http://www.mediafire.com/imageview.php?quickkey=alibmjlbykg&thumb=4

    Last edited by nike123; 26-12-2007 at 10:46 PM.

  10. #10
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: charging a system

    thanks for all tour replies

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Charging the system
    By CJG21 in forum Fundamentals
    Replies: 5
    Last Post: 13-05-2007, 02:47 PM
  5. System charging
    By Dylan in forum Fundamentals
    Replies: 10
    Last Post: 17-12-2004, 10:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •