    commissioning of propylene refrigerant cycle



    Hello to everybody!
    I've just found this site and I hope that you can help me to solve the following problem.
    I'm studing how to perform a commisioning of a propylene refrigerant circuit. I have a lot of references where is written that after blowing with nitrogen I have to put the system under vacuum to evaporate residual water and dry all the lines. Don't you think that blowing with nitrogen is enough?Do you know if water can react with propilene and cause some problem to the system?
    A part from freezing, what is the problem of having water inside the line?

    I hope that you can help me

    KIKA



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: commissioning of propylene refrigerant cycle

    Vacuum and why to do it???

    Firstly, your nitrogen is a "non condensable" gas, this means that any nitrogen left in the system will reduce the performance (and most likely stop the system working all together).

    Depending on what oil your system uses, even small amounts of moisture will turn the oil in to accid (not desireable).

    Also, even small amounts of moisture will be able to block expansion devices and other small orifices in your system.


    There really aren't any excuses NOT to give the system a good, deep, standing vacc before you commission it.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: commissioning of propylene refrigerant cycle

    Water can affect the oil used.

    Residual nitrogen can increase the discharge pressure and operating costs if not evacuated from the system.

    Water can freeze into ice at the expansion devices causing operation problems.

    It is important to ensure the oil has sufficient viscosity to allow for dilution, which can and will occur.

    Pull a vacuum, like any other refrigeration system!
    If all else fails, ask for help.


  4. #4
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: commissioning of propylene refrigerant cycle

    Welcome to the forum Kika

    I saw this post this morning and was confused as to your question.
    Were you asking about water in the Propylene Side of the system?

  5. #5
    kika's Avatar
    kika Guest

    Re: commissioning of propylene refrigerant cycle

    Thank you for your suggestions. I wasn't thinking of the problem of the dilution of the oil. For what concerning nitrogen I think that it can be easily evacuated from the uncondensable line of the propilen condenser. Is this a desirable solution?
    Moreover I was thinking to install in the system a filter for the absorption of residual water and flow the gassous propilen from time to time.
    ....Our team is trying to reduce the time of commissioning because in the past we had a lot trouble and vacuuming lasted more than 2 weeks!!! I know that this time may seem short, but the system is very small.
    I have another question about the circuit. What about the connections? Once again I see that flanged connection aren't desirable on the line. Do you suggest to weld all the valves? What about the connections between main equipment and the pipes?
    Waiting for your precious answer
    KIKA

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: commissioning of propylene refrigerant cycle

    My recommendation is to minimize the use of flanges. Use welded valves and fittings as much as possible.
    When using threaded joints; seal weld the joint.

    Purge with nitrogen, and then vacuum. Manual purging of nitrogen off of the condenser does not remove all of the nitrogen.

    If it is taking too long to vacuum a system then the vacuum pump is too small, or you have too much water in a system.
    If all else fails, ask for help.


  7. #7
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: commissioning of propylene refrigerant cycle

    Italy is part of the EU & should comply with EN:378 which states a vacuum of 200 microns should be acheived on the refrigerant side of the system.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. propylene refrigerant criteria
    By zhouweidl in forum Hydrocarbons
    Replies: 3
    Last Post: 30-07-2009, 01:01 PM
  3. Explosion Ratings - Propylene Refrigeration Cycle
    By awhicker in forum Industrial Compressors
    Replies: 6
    Last Post: 03-11-2007, 12:25 AM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. propylene refrigerant
    By zhouweidl in forum Fundamentals
    Replies: 1
    Last Post: 12-05-2006, 02:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •