    Talking Where Do I Locate a Buffer Tank?



    Hi, I am a first time user but I think I will become a regular user!
    We look after a new hospital that has just had the mechanical services come out of warranty. Thank god we didn't do the installation because it is shocking. The main Rhoss heatpump chiller has now lost 2 compressors due to liquid slugging. There is no buffer tank in the circuit and the supplier is blaming this as the reason for liquid slugging. If we are to install a buffer tank would it be positioned before the pumps or after them but before the chiller?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Where Do I Locate a Buffer Tank?

    Hi Jethro and welcome to the forum.

    According to this...
    http://www.cemline.com/CWB_piping_diagram.pdf
    the circuit would be - chiller - load - buffer tank - pump - chiller etc etc
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Where Do I Locate a Buffer Tank?

    This heat pump should have a liquid accumulator in the suction line right before the compressor to protect it from slugging but if you mean the chill water line and an air seperator then in a closed system where are you taking on air?
    Last edited by wambat; 27-08-2007 at 01:27 AM.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Where Do I Locate a Buffer Tank?

    Accumulators are cheap and sure shot at helping to stop slugging, better then that is do an audit of the whole operating system and tune it properly and get the best capacity sequencing of the compressors.

    Any thing short is patching, and thats a nasty never ending game, Only way to win it is not to play in the first place.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Where Do I Locate a Buffer Tank?

    I think what he is looking for is a "water" buffer tank. From his description of the problem the water volume for the system is too small and allowing the system to short cycle on low load conditions.

    I remember seeing some statement about this in Trane chiller brochures as something very important to pay attention to.

    An accumulator is secondary protection for the compressor in light of not having the water tank to add system volume.
    If all else fails, ask for help.


  6. #6
    Join Date
    Aug 2007
    Location
    New Zealand
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: Where Do I Locate a Buffer Tank?

    The heatpump chiller is a RHOSS aircooled twin circuit machine. During normal operation it runs fine but as soon as a defrost cycle is completed one compressor starts to slug and the crankcase oil foams enough to drop the compressor out on oil failure. The second compressor on the machine doesn't experience the same problem. Any suggestions?

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Where Do I Locate a Buffer Tank?

    Quote Originally Posted by Jethro Bush View Post
    The heatpump chiller is a RHOSS aircooled twin circuit machine. During normal operation it runs fine but as soon as a defrost cycle is completed one compressor starts to slug and the crankcase oil foams enough to drop the compressor out on oil failure. The second compressor on the machine doesn't experience the same problem. Any suggestions?
    Increase superheat on TXV!

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Where Do I Locate a Buffer Tank?

    Quote Originally Posted by Jethro Bush View Post
    The heatpump chiller is a RHOSS aircooled twin circuit machine. During normal operation it runs fine but as soon as a defrost cycle is completed one compressor starts to slug and the crankcase oil foams enough to drop the compressor out on oil failure. The second compressor on the machine doesn't experience the same problem. Any suggestions?

    Hi Jethro

    it has been known for Rhoss to position the TXV bulbs in the wrong position, we normally move the bulb on the heat pump chiller models to the main compressor suction on the compressor side of the 4 way valve.

    Also check the operation of the outdoor fan if you are in heating and the refrigerant charge.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. Buffer Tank Sizing
    By deepakrbhat in forum Fundamentals
    Replies: 12
    Last Post: 12-02-2010, 09:31 AM
  2. Ice Bank Tank for Chilled Water
    By Samarjit Sen in forum Commercial
    Replies: 26
    Last Post: 31-10-2009, 09:18 AM
  3. surge tank on racks
    By frozen ocean in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 25-08-2009, 03:22 PM
  4. Need Help with cold water tank design
    By ac_sheldon in forum Industrial
    Replies: 9
    Last Post: 21-11-2008, 11:24 PM
  5. natural Stratification tank
    By Camille in forum Industrial
    Replies: 0
    Last Post: 03-05-2007, 01:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •