    Daikin Comp and inverter



    I have a Daikin underslung outdoor unit (single phase 10kw) which has failed under warranty after 3 months.
    Fault code L5 and after many telephone conversations with Daikin they/ i have decided that it is a faulty comp and inverter board.
    Does anybody have any tips with regarding the replacement.?It looks a bit of a sod of a job from what ii saw today.
    I take it there is no point in me asking if Daikin will swap the outdoor unit complete which would make my life much easier?
    Also do Daikin still offer a labour allowance for carrying out these jobs?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin Comp and inverter

    i had a 14kw cassette alarm on l5 after 5mth.used an inverter checker -45 quid and proved 3 outputs . replaced just the compressor and no probs that was 18 mth ago.

  3. #3
    ritzz's Avatar
    ritzz Guest

    Re: Daikin Comp and inverter

    dear sir,i faced a problem with a daikin inverter system.i checked a daikin 12,000btu air con and found some dry joints on the board and i soldered and also repaired the leaking condenser.when i ran the unit its cooling bit the compressor is heating.i asked the fofum what could the fault but no answer. can anyone tell why the compressor is heating. the running amps is ok.

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin Comp and inverter

    Quote Originally Posted by ritzz View Post
    dear sir,i faced a problem with a daikin inverter system.i checked a daikin 12,000btu air con and found some dry joints on the board and i soldered and also repaired the leaking condenser.when i ran the unit its cooling bit the compressor is heating.i asked the fofum what could the fault but no answer. can anyone tell why the compressor is heating. the running amps is ok.
    You are better off starting a new thread for questions like this, otherwise people might answer the first (very old) post rather than read further and see you have bumped the thread and have an entirely new question.

    From what I gather, you are running a repaired daikin in cool mode, but the system is runing in heat mode?
    First, see if you are getting 240v to the reversing valve coil. If so, you have a control problem (controller, wiring, pcb etc)

    If you dont have mains power to the reversing valve solenoid, but the sytem is still in heat mode, you have a stuck valve. You could try beating the hell out of it with a rubber mallet. Or you may just need to replace the reversing valve.
    Last edited by paul_h; 05-11-2008 at 10:49 AM. Reason: of /= off

  5. #5
    Join Date
    Nov 2008
    Location
    tr
    Age
    54
    Posts
    5
    Rep Power
    0

    Re: Daikin Comp and inverter

    hi,
    ı have a 12 year daikin system experience.

    I m sure L5 is means inverter comp faliure %90
    or %10 inverter Card

    %50 both of faliure

    ı succest that check pipe line and sure its dry and clean

  6. #6
    Join Date
    Jul 2007
    Location
    Finland
    Age
    55
    Posts
    20
    Rep Power
    0

    Re: Daikin Comp and inverter

    Quote Originally Posted by water View Post
    hi,
    ı have a 12 year daikin system experience.

    I m sure L5 is means inverter comp faliure %90
    or %10 inverter Card

    %50 both of faliure

    ı succest that check pipe line and sure its dry and clean
    Closed ports in pipe line also cause L5 -alarms...

    Check with megger compressor's electric insulation resistance also.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Daikin VRV
    By nickthefridge in forum Air Conditioning
    Replies: 10
    Last Post: 14-10-2007, 01:42 PM
  3. Inverter systems
    By Latte in forum The Trail of Tears
    Replies: 23
    Last Post: 11-07-2007, 12:14 AM
  4. new daikin inverter kit
    By allyjg30 in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2007, 12:04 AM
  5. R22 Mitsi City Multi problem
    By markj in forum Air Conditioning
    Replies: 10
    Last Post: 05-03-2007, 08:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •