18-12-2007, 12:30 AM #1
Daikin Comp and inverter
I have a Daikin underslung outdoor unit (single phase 10kw) which has failed under warranty after 3 months.
Fault code L5 and after many telephone conversations with Daikin they/ i have decided that it is a faulty comp and inverter board.
Does anybody have any tips with regarding the replacement.?It looks a bit of a sod of a job from what ii saw today.
I take it there is no point in me asking if Daikin will swap the outdoor unit complete which would make my life much easier?
Also do Daikin still offer a labour allowance for carrying out these jobs?
-
18-12-2007, 10:53 PM #2
Re: Daikin Comp and inverter
i had a 14kw cassette alarm on l5 after 5mth.used an inverter checker -45 quid and proved 3 outputs . replaced just the compressor and no probs that was 18 mth ago.
-
05-11-2008, 06:10 AM #3
Re: Daikin Comp and inverter
dear sir,i faced a problem with a daikin inverter system.i checked a daikin 12,000btu air con and found some dry joints on the board and i soldered and also repaired the leaking condenser.when i ran the unit its cooling bit the compressor is heating.i asked the fofum what could the fault but no answer. can anyone tell why the compressor is heating. the running amps is ok.
-
05-11-2008, 10:47 AM #4
Re: Daikin Comp and inverter
You are better off starting a new thread for questions like this, otherwise people might answer the first (very old) post rather than read further and see you have bumped the thread and have an entirely new question.
From what I gather, you are running a repaired daikin in cool mode, but the system is runing in heat mode?
First, see if you are getting 240v to the reversing valve coil. If so, you have a control problem (controller, wiring, pcb etc)
If you dont have mains power to the reversing valve solenoid, but the sytem is still in heat mode, you have a stuck valve. You could try beating the hell out of it with a rubber mallet. Or you may just need to replace the reversing valve.Last edited by paul_h; 05-11-2008 at 10:49 AM. Reason: of /= off
-
05-11-2008, 12:44 PM #5
Re: Daikin Comp and inverter
hi,
ı have a 12 year daikin system experience.
I m sure L5 is means inverter comp faliure %90
or %10 inverter Card
%50 both of faliure
ı succest that check pipe line and sure its dry and clean
-
08-11-2008, 08:44 PM #6
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Daikin VRV
By nickthefridge in forum Air ConditioningReplies: 10Last Post: 14-10-2007, 01:42 PM -
Inverter systems
By Latte in forum The Trail of TearsReplies: 23Last Post: 11-07-2007, 12:14 AM -
new daikin inverter kit
By allyjg30 in forum Air ConditioningReplies: 4Last Post: 09-06-2007, 12:04 AM -
R22 Mitsi City Multi problem
By markj in forum Air ConditioningReplies: 10Last Post: 05-03-2007, 08:44 AM