    I would appreciated any help I can receive regards with a Mitshubishi Inverter Split Wall Mount heat pump. Model Number FDKA 201

    Unit has a hard wired remote controller

    On starting the remote controller displayerd the following:

    04
    9F
    Then 2 hand ( palm) symbols with the word, " WAIT " in between

    Unit did not switch on, remained locked out. I rechecked all the connections, Power was ok at outdoor unit, and 240 v on interconnecting number 1

    I checked all the XYZ connections on the remote to the indoor unit, All were fine.

    Pressing the SW9 switch on the outdoor to initiate a test run produced nothing, although pressing the small white button on the indoor ( with japanese script) unit ran in cooling mode

    Please help if anyone knows of this fault code

    Regards
    Abe



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Need Help with a Mitsubishu

    OK,
    So it's a Mitsubishi HEAVY you are looking at.

    I can't find the codes you are mentioning, normally their fault codes starts with an E.

    But, This is a link to the full service manual.

    The "wait" bit does indicate that there is a problem with the communications, has the unit run or is it a new install?
    Last edited by The Viking; 16-12-2007 at 05:41 PM.

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Need Help with a Mitsubishu

    Viking

    I apologise , I posted this under Legal, should have been under Air Conditioning.

    Its a brand new install

  4. #4
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Need Help with a Mitsubishu

    Abe, do you get the flashing palms/wait signal as soon as it is powered up or after you ask for heating/cooling?
    These units will not let the compressor start unless the crankcase heater has been on long enough for the sensor on the top of the compressor to get warm enough. Until its warm, it will just sit there.
    Have you checked your wiring through your internal isolator?

    Andy

  5. #5
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Need Help with a Mitsubishu

    Abe
    I had a similar problem and it turned out to be the hand held IR sensor was factory connected, soon as i unpluged it the unit fired into life on the hard wired controller

    Regards
    Pavilion

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Need Help with a Mitsubishu

    Quote Originally Posted by Andy AC View Post
    Abe, do you get the flashing palms/wait signal as soon as it is powered up or after you ask for heating/cooling?
    These units will not let the compressor start unless the crankcase heater has been on long enough for the sensor on the top of the compressor to get warm enough. Until its warm, it will just sit there.
    Have you checked your wiring through your internal isolator?

    Andy
    I did not see any flashing lights if I recall, but the unit was switched on at isolator , and compressor was not warm, And was freezing cold yesterday. I know Mitsu recommend swiching the isolator on 24 hours before.

    Maybe it was locked out, I dont know, I still think something wrong with hard wired controller

  7. #7
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Need Help with a Mitsubishu

    Quote Originally Posted by pavilion View Post
    Abe
    I had a similar problem and it turned out to be the hand held IR sensor was factory connected, soon as i unpluged it the unit fired into life on the hard wired controller

    Regards
    Pavilion
    pavillion

    this unit only comes with a hard wired remote, no hand held ir......os is it somewhere in the indoor unit

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Need Help with a Mitsubishu

    He was talking about the indoor unit sensor so maybe there is one to look out for
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Need Help with a Mitsubishu

    Abe

    The unit i installed came with a hard wired controller but the indoor unit was wired for a remote ir sensor which caused a conflict with the hard wired remote. Try speaking to 3D air sales tech guys (part of HRP) on 01359272211 they talked me through the problems while i was on site.

    Regards
    Pavilion.

  10. #10
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Need Help with a Mitsubishu

    Quote Originally Posted by pavilion View Post
    Abe

    The unit i installed came with a hard wired controller but the indoor unit was wired for a remote ir sensor which caused a conflict with the hard wired remote. Try speaking to 3D air sales tech guys (part of HRP) on 01359272211 they talked me through the problems while i was on site.

    Regards
    Pavilion.
    I spoke with Technical today, they said, take the front cover off, indo screws etc, and lift the entire casing off, located on the right hand side near the evap fan is a pcb board, lift it half way up, and look for a jumper link J31.

    Cut the link in half. ie: sever it completely
    Then the hard wired will work.........as you say, its wired to work with a hand held remote.

    next question:

    WHY THE BLEEDING HELL DONT THEY TELL US THIS WHEN THEY DELIVER THE UNIT, AND WHY IS A UNIT SUPPLIED WITH A HARD WIRED CONTROLLER BUT CONFIGURED TO A HAND HELD???

    Lolllllll

    Now it means another trip 30 miles down the road and more fidgeting, at least the frown on my forehead has dissapeared.

    Come on Mitsu, I rate you highly, but on this occasion you have stressed me.

    I hope other members will be better served if installing similar, the units are the FDK versions.........not SRK

    Thats my christmas holidays fouled up.....Ahh well

  11. #11
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Need Help with a Mitsubishu

    Know what you mean, spent a day trying to sort the thing out, not good on a tight quote Like you say better instructions please mitsi.

  12. #12
    Join Date
    Dec 2007
    Location
    england
    Age
    39
    Posts
    13
    Rep Power
    0

    Re: Need Help with a Mitsubishu

    hey i installed some heavy twins and they did not tell me that i needed to set dip switches wasted alot of time ,they need to tell you things like that when you buy kit off them

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Need Help with a Mitsubishu

    Quote Originally Posted by airconboy View Post
    hey i installed some heavy twins and they did not tell me that i needed to set dip switches wasted alot of time ,they need to tell you things like that when you buy kit off them
    Are you sure that this is not described in instalation manual?

  14. #14
    Join Date
    May 2006
    Location
    Norwich
    Age
    53
    Posts
    134
    Rep Power
    18

    Re: Need Help with a Mitsubishu

    Quote Originally Posted by nike123 View Post
    Are you sure that this is not described in instalation manual?
    its on a seperate sheet

  15. #15
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: Need Help with a Mitsubishu

    Hey Abe,never really experienced that code before.Could help if you phone Mitsubishi directly and speak to one of the consultants...