    Fan Speed



    Hi from Greece,

    I want less humidity in a cold room (***** 22) with porks , the evaorator dont have ice but inside the room you can find a lot of water drops in the roof and the porks are very wet.
    The temperature inside is -0.5C whith Differential 0.5C The RH Humidity is 50% but the customer need less. The fans are ON when the Solenoid valve is ON and ofcourse off during defrost.
    If i install an inverter and when the solenoid valve is OFF i start the fans at low speed continiusly can i have less humidity ?

    Regards,

    Giannis



  2. #2
    Join Date
    Dec 2007
    Location
    Denmark
    Posts
    10
    Rep Power
    0

    Re: Fan Speed

    Are there any delay on fans after a defrost?
    Sounds like they start immediately after the defrost cycle is done.
    Try to delay 'em 2-3 min or till coil temerature is below zoro, that would prevent the water to "spray" out of the evaporator and stick to the cieling after a defrost cycle.

    In order to lower your humidity in the cold room you need to lower the temperature in your evaporator.
    If you have higher temperature difference between coil temperature and air intake temperature you will "catch" more water on the coil, thus lowering the humidity in the room.
    Maybe you can achieve it by lowering the fanspeed as you say, would like to hear the result if you decide to do this )

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Fan Speed

    Whats the evap temp air on/off?
    What's the coil size, heat load, coil surface area?
    If you want low humidty, you want a large TD on the air on/air off.
    But without any details we don't know if there's a low TD or high humidity from coolroom leaks or product sweating.
    But just guessing, if there's no ice on the coil and the coil temp is -0.5C, then you have a lot of defrosts or the coil isn't removing much humidity due to low TD

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Fan Speed

    Hi Giannis Are the water drops all over the roof or just in front of the evaps? Increasing the TD across the coil will decrease the humidity but be careful you don't get too big a TD as this will dry the meat out and the weight loss will be considerable. The best way to chill carcasses is to put the evaps behind a wall and reverse the air flow, blow the air from the bottom of the room and have the return air at the top. This stops condensation on the roof of the room. With a conventional room the air coming off the evap is very cold and this causes the roof to get very cold and when the hot carcasses are put in the room the hot humid air from the meat hits the cold roof and condenses. By running a colder evap you can compound the problem as the roof will be colder then it is at present. You can install some deflectors to direct the air away from the roof (this may help) and increase the air speed to max during the initial chill period then drop it back as the high air speed will also dry the meat out. Let us know how you get on . Paul

  5. #5
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Fan Speed

    First i will tommorow set the delay after defost as Spiffinator told me and i will send the data of 1 week temperature (room,evaporator,CP) recordings in this forum .Thank you i will have news tommorow

  6. #6
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Fan Speed

    Quote Originally Posted by Giannis View Post
    First i will tommorow set the delay after defost as Spiffinator told me and i will send the data of 1 week temperature (room,evaporator,CP) recordings in this forum .Thank you i will have news tommorow
    please also observe the cold room daily operations esp. on how long they leave door open and etc.

    this also helps to determine the suitability of the design apart from changing refrigeration paraemters.

  7. #7
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Exclamation More Data For The Problem

    This Attachment is one week recordings from the room. And photo from the drops, (some times ice drops)

    ROOM SIZE 90m3
    ***** R22
    COOLING CAPACITY 17KW
    AIR FLOW 15200m3/hour
    AIR THROW 20m
    FANS 2 X 500mm

    waiting your replay
    Attached Images Attached Images

  8. #8
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Fan Speed

    What height is the ceiling?
    What height is the thermostat?

    Sounds like you have warm air rising up and condensing on the ceiling. I would run the fans (or at least one of them) all the time except during a defrost.

    Also if you could get the evaporator colder it would help.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    Quote Originally Posted by Giannis View Post
    If i install an inverter and when the solenoid valve is OFF i start the fans at low speed continuously can i have less humidity ?
    You can lower the humidity by running a lower fan speed when the solenoid valve is ON.

    Keep in mind that this will lower the weight of the pork and therefore lower its value.
    Last edited by Gary; 21-12-2007 at 04:10 PM.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    Quote Originally Posted by chillin out View Post
    I would run the fans (or at least one of them) all the time except during a defrost.
    I agree. Cycling the fans with the solenoid valve is not a good idea. The fans should only be off during defrost.

  11. #11
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Fan Speed

    Thank you Gary

    I will try to Have the fans always ON but OFF during defrost.

    Must i change the speed ?
    Low speed when solenoid is ON and high when is OFF or the negative ?

    My Customer dont care about the weight losses but about the quality (not dark meat)

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    Lowering the fan speed (when the solenoid is ON) lowers the evaporator temp, thus increasing the TD. As several people have stated, increasing the TD lowers the humidity.

    Since it will be dehumidifying more it will be cooling less, so the run time is increased and you can expect more frost on the coil also.

    If you lower the fan speed too much, there won't be enough cooling to bring down the temperature and you may need more defrost cycles.

    Everything is a trade-off. You need to find the right balance between cooling and dehumidification. Slower fan speed, but not too slow.

    High fan speed when the solenoid is OFF will help to defrost the coil and will help to circulate the air throughout the room.
    Last edited by Gary; 22-12-2007 at 03:56 PM.

  13. #13
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Fan Speed

    Quote Originally Posted by Gary View Post
    Lowering the fan speed lowers the evaporator temp, thus increasing the TD. As several people have stated, increasing the TD lowers the humidity.

    Since it will be dehumidifying more it will be cooling less, so the run time is increased and you can expect more frost on the coil also.

    If you lower the fan speed too much, there won't be enough cooling to bring down the temperature and you may need more defrost cycles.

    Everything is a trade-off. You need to find the right balance. Slower, but not too slow.

    High speed when the solenoid is OFF will help to defrost the coil and will help to circulate the air throughout the room.
    Thank you Gary, And what about the Expance valve ? i must close a little or open ?

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    You won't need to adjust the expansion valve.

  15. #15
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Fan Speed

    Thank you Gary,

    I Will have the results soon !

  16. #16
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: More Data For The Problem

    Quote Originally Posted by Giannis View Post
    This Attachment is one week recordings from the room. And photo from the drops, (some times ice drops)

    ROOM SIZE 90m3
    ***** R22
    COOLING CAPACITY 17KW
    AIR FLOW 15200m3/hour
    AIR THROW 20m
    FANS 2 X 500mm

    waiting your replay

    a glance of the data ... i interprete as insuficient pulldown of temperature before the next defrost interval.

    kindly consider this. you definitely need the pulldown to works to your advantages.

  17. #17
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: More Data For The Problem

    Quote Originally Posted by hendry View Post
    a glance of the data ... i interprete as insuficient pulldown of temperature before the next defrost interval.

    kindly consider this. you definitely need the pulldown to works to your advantages.

    Hi hendry

    it would seem the room has not enough refrigeration in it

    About 30kW would suffice

    Evaporation is also important, but only if there is enough duty and air circulation in the room, I suspect neither is right in this situation.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    According to the temperature chart provided, the cooling seems to be off much longer than it is on... or am I reading it wrong?

  19. #19
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Fan Speed

    Quote Originally Posted by Gary View Post
    According to the temperature chart provided, the cooling seems to be off much longer than it is on... or am I reading it wrong?
    Hi Gary

    yes the coolers are off on stat quite a bit, too much for a room this size with this amount of cooling duty.
    Possibly the dual discharge coolers are short cycling their air or more likely by the humidity levels only refrigerating part of the room.
    Dual discharge coolers would not be my first choice to cure a meat product.

    Something is very wrong with this installation

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fan Speed

    Quote Originally Posted by Andy View Post
    Hi Gary

    yes the coolers are off on stat quite a bit, too much for a room this size with this amount of cooling duty.
    Possibly the dual discharge coolers are short cycling their air or more likely by the humidity levels only refrigerating part of the room.
    Dual discharge coolers would not be my first choice to cure a meat product.

    Something is very wrong with this installation

    Kind Regards Andy
    Hi Andy,

    I suspect we may see an entirely different picture once the fans are running during the off cycle. Cycling the fans with the solenoid would be the first thing that is very wrong here.
    Last edited by Gary; 24-12-2007 at 02:16 PM.

  21. #21
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Fan Speed

    Yes, we isntall a big evaporator becouse of customer,

    If you need more information Gary i can tell you anything about this system.

    I always trust your answers


    Regards

    Giannis

  22. #22
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Fan Speed

    Quote Originally Posted by Gary View Post
    Hi Andy,

    I suspect we may see an entirely different picture once the fans are running during the off cycle. Cycling the fans with the solenoid would be the first thing that is very wrong here.

    Yes very wrong

    Air should move constantly in the room, with a minimum of 0.5m/sec around the inside of the hams.


    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  23. #23
    Join Date
    Dec 2007
    Location
    australia
    Posts
    13
    Rep Power
    0

    Re: Fan Speed

    run fans continuously , only shut down on defrost.adjust temp set pouint from -0.5 to -1.0 with a 1.0 degree differential. slow fan speed down,adjust defrost frequency to suit coil frosting up.then log progress

  24. #24
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Fan Speed

    Quote Originally Posted by Andy View Post
    Hi Gary

    yes the coolers are off on stat quite a bit, too much for a room this size with this amount of cooling duty.
    Possibly the dual discharge coolers are short cycling their air or more likely by the humidity levels only refrigerating part of the room.
    Dual discharge coolers would not be my first choice to cure a meat product.

    Something is very wrong with this installation

    Kind Regards Andy
    as i was saying ... temperature pulldown is insufficient.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Speed control of the compressor
    By Peter_1 in forum Air Conditioning
    Replies: 10
    Last Post: 19-12-2007, 07:51 AM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  4. Pressure loss versus speed in suction line
    By Peter_1 in forum Fundamentals
    Replies: 14
    Last Post: 29-05-2007, 05:00 PM
  5. Kuba fan speed question
    By Peter_1 in forum Electrical
    Replies: 1
    Last Post: 07-12-2004, 07:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •