16-12-2007, 04:46 PM #1
Fan Speed
Hi from Greece,
I want less humidity in a cold room (***** 22) with porks , the evaorator dont have ice but inside the room you can find a lot of water drops in the roof and the porks are very wet.
The temperature inside is -0.5C whith Differential 0.5C The RH Humidity is 50% but the customer need less. The fans are ON when the Solenoid valve is ON and ofcourse off during defrost.
If i install an inverter and when the solenoid valve is OFF i start the fans at low speed continiusly can i have less humidity ?
Regards,
Giannis
-
17-12-2007, 10:40 AM #2
Re: Fan Speed
Are there any delay on fans after a defrost?
Sounds like they start immediately after the defrost cycle is done.
Try to delay 'em 2-3 min or till coil temerature is below zoro, that would prevent the water to "spray" out of the evaporator and stick to the cieling after a defrost cycle.
In order to lower your humidity in the cold room you need to lower the temperature in your evaporator.
If you have higher temperature difference between coil temperature and air intake temperature you will "catch" more water on the coil, thus lowering the humidity in the room.
Maybe you can achieve it by lowering the fanspeed as you say, would like to hear the result if you decide to do this )
-
17-12-2007, 11:35 AM #3
Re: Fan Speed
Whats the evap temp air on/off?
What's the coil size, heat load, coil surface area?
If you want low humidty, you want a large TD on the air on/air off.
But without any details we don't know if there's a low TD or high humidity from coolroom leaks or product sweating.
But just guessing, if there's no ice on the coil and the coil temp is -0.5C, then you have a lot of defrosts or the coil isn't removing much humidity due to low TD
-
17-12-2007, 01:25 PM #4
Re: Fan Speed
Hi Giannis Are the water drops all over the roof or just in front of the evaps? Increasing the TD across the coil will decrease the humidity but be careful you don't get too big a TD as this will dry the meat out and the weight loss will be considerable. The best way to chill carcasses is to put the evaps behind a wall and reverse the air flow, blow the air from the bottom of the room and have the return air at the top. This stops condensation on the roof of the room. With a conventional room the air coming off the evap is very cold and this causes the roof to get very cold and when the hot carcasses are put in the room the hot humid air from the meat hits the cold roof and condenses. By running a colder evap you can compound the problem as the roof will be colder then it is at present. You can install some deflectors to direct the air away from the roof (this may help) and increase the air speed to max during the initial chill period then drop it back as the high air speed will also dry the meat out. Let us know how you get on . Paul
-
17-12-2007, 05:37 PM #5
Re: Fan Speed
First i will tommorow set the delay after defost as Spiffinator told me and i will send the data of 1 week temperature (room,evaporator,CP) recordings in this forum .Thank you i will have news tommorow
-
18-12-2007, 02:25 AM #6
-
20-12-2007, 01:06 PM #7
More Data For The Problem
This Attachment is one week recordings from the room. And photo from the drops, (some times ice drops)
ROOM SIZE 90m3
***** R22
COOLING CAPACITY 17KW
AIR FLOW 15200m3/hour
AIR THROW 20m
FANS 2 X 500mm
waiting your replay
-
20-12-2007, 09:32 PM #8
Re: Fan Speed
What height is the ceiling?
What height is the thermostat?
Sounds like you have warm air rising up and condensing on the ceiling. I would run the fans (or at least one of them) all the time except during a defrost.
Also if you could get the evaporator colder it would help.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
21-12-2007, 04:08 PM #9
Re: Fan Speed
Last edited by Gary; 21-12-2007 at 04:10 PM.
-
21-12-2007, 04:13 PM #10
Re: Fan Speed
-
21-12-2007, 10:18 PM #11
Re: Fan Speed
Thank you Gary
I will try to Have the fans always ON but OFF during defrost.
Must i change the speed ?
Low speed when solenoid is ON and high when is OFF or the negative ?
My Customer dont care about the weight losses but about the quality (not dark meat)
-
22-12-2007, 03:40 PM #12
Re: Fan Speed
Lowering the fan speed (when the solenoid is ON) lowers the evaporator temp, thus increasing the TD. As several people have stated, increasing the TD lowers the humidity.
Since it will be dehumidifying more it will be cooling less, so the run time is increased and you can expect more frost on the coil also.
If you lower the fan speed too much, there won't be enough cooling to bring down the temperature and you may need more defrost cycles.
Everything is a trade-off. You need to find the right balance between cooling and dehumidification. Slower fan speed, but not too slow.
High fan speed when the solenoid is OFF will help to defrost the coil and will help to circulate the air throughout the room.Last edited by Gary; 22-12-2007 at 03:56 PM.
-
22-12-2007, 03:49 PM #13
-
22-12-2007, 04:02 PM #14
Re: Fan Speed
You won't need to adjust the expansion valve.
-
22-12-2007, 04:06 PM #15
Re: Fan Speed
Thank you Gary,
I Will have the results soon !
-
24-12-2007, 02:30 AM #16
-
24-12-2007, 01:29 PM #17
Re: More Data For The Problem
If you can't fix it leave it that no one else will:rolleyes:
-
24-12-2007, 01:39 PM #18
Re: Fan Speed
According to the temperature chart provided, the cooling seems to be off much longer than it is on... or am I reading it wrong?
-
24-12-2007, 01:49 PM #19
Re: Fan Speed
Hi Gary
yes the coolers are off on stat quite a bit, too much for a room this size with this amount of cooling duty.
Possibly the dual discharge coolers are short cycling their air or more likely by the humidity levels only refrigerating part of the room.
Dual discharge coolers would not be my first choice to cure a meat product.
Something is very wrong with this installation
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes:
-
24-12-2007, 02:10 PM #20
Re: Fan Speed
Last edited by Gary; 24-12-2007 at 02:16 PM.
-
24-12-2007, 08:46 PM #21
Re: Fan Speed
Yes, we isntall a big evaporator becouse of customer,
If you need more information Gary i can tell you anything about this system.
I always trust your answers
Regards
Giannis
-
25-12-2007, 03:43 PM #22
-
26-12-2007, 03:25 AM #23
Re: Fan Speed
run fans continuously , only shut down on defrost.adjust temp set pouint from -0.5 to -1.0 with a 1.0 degree differential. slow fan speed down,adjust defrost frequency to suit coil frosting up.then log progress
-
26-12-2007, 10:06 AM #24
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Speed control of the compressor
By Peter_1 in forum Air ConditioningReplies: 10Last Post: 19-12-2007, 07:51 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
Pressure loss versus speed in suction line
By Peter_1 in forum FundamentalsReplies: 14Last Post: 29-05-2007, 05:00 PM -
Kuba fan speed question
By Peter_1 in forum ElectricalReplies: 1Last Post: 07-12-2004, 07:17 PM