    Refrigeration System for Agricultural Produce



    I have been working in the field of Precooling and High Humidity Cold Stores for various Fruits and Vegetables. Studying various books and seeing the installed plants, I find that the system where the air in the Cold Rooms are being sucked in and blown over bare tube coils, and water in being sprayed or spilled over the coils and the air containing the water droplets are being supplied to the room are being considered as more efficient. This system is being termed as Forced Air Cooling.

    The reason for the efficiency is being claimed is that as the air is being sucked through the boxes, the cooling of the produce is better.

    The air being sucked are usually propellor fans. Now what would be the static pressure so as to have a high efficiency for such aplication. Further the water moisture which is being supplied to the room are larger in size due to which they tend to settle on the card board boxes and also on the fruits and floor of the room. This tends to damage the fruit. What could be the highest humidity achieved.

    I have installed plants with DX ceiling hanging . They have pull through fans and as such the velocity is higher. The surface area is much higher with more air supply. The td of the coil has been reduced and the controls have been selected properly. I have not used any additional humidifiers. The coil itself is generating the required humidity due to which the moisture articles are not only very small, but they do not tend to settle on the boxes, fruits and the floor.

    The results have been good as there has been no rejection of the fruits exported so far.

    Under the circumstances as stated above, which system would it be considered better.

    I am asking this, as there are a large number of people in the forum who are executing similar projects . What is their experience and opinion.



  2. #2
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    Samarjit Sen,
    i find u has been a regular in this forum. good!

    about your Q ...
    i install mainly the later type. we do not practice formal b'coz the setback on big droplets.
    the later, yes, produces better RH ctrl.
    but, one must sequence the defrost procedures right otherwise condensate water will still fly everywhere upon fan operations.

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Refrigeration System for Agricultural Produce

    Hello Hendry,

    We put electric defrost and do not have any problem. The condensate water does not carryover through the fan.

    What is the Rm. Temp. and the RH being maintained in your plant.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigeration System for Agricultural Produce

    Quote Originally Posted by hendry View Post
    one must sequence the defrost procedures right otherwise condensate water will still fly everywhere upon fan operations.
    I'm sure that most are aware of that.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    Brian, how much do you know about the individual steps within defrost mechanism? How should be the sequence for each step to take place? How long should that step to be?
    >> mismatched! costly plant to operate & bad pull down.

    Samarjit, we have had experiences with different type.
    1] 65%, +18degC;
    2] 95%, -20degC

    Ammonia & HFC too!

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Refrigeration System for Agricultural Produce

    The refrigeration systems that are being installed by us are generally for Fruit & Vegetable Storage with a temperature of -1 oC and a RH of 95 to 97% and Ice Cream Hardening and Storage with a Temperature range of - 25 oC to - 40 oC. These plants are being operated with R 22.

    The defrost is important and so is the sequence and I am sure that the people involved in such projects are very well aware of the same.

  7. #7
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    samarjit,

    agreed.
    when i write 'sequence', it means the tiny little details of the mechanism. It is far more than just defrost in every 4 hours only.
    i hope you are clear & so do Brian.

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Refrigeration System for Agricultural Produce

    hendry,

    I am sorry, but to be honest I am yet to understand what yiou said . I shall appreciate if you could please do clarify your comments.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigeration System for Agricultural Produce

    Samarjit,

    He is talking about the sequence of operation during a defrost cycle.

    1. De-energize liquid line solenoid
    2. Pump down evaporator
    3. Stop fans
    4. Close suction valve
    5. Energize hot gas solenoid
    6. After defrost is complete...
    7. De-energize hot gas solenoid
    8. Equalize evaporator pressure with suction pressure
    9. Open suction valve
    10. Energize liquid line solenoid and let coil re-freeze water droplets
    11. Turn on fans
    Those are the major items and you could possibly have a few more depending on circumstances.
    If all else fails, ask for help.


  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Refrigeration System for Agricultural Produce

    Hi Mike,

    Thank you for stating the explanations. I am sure that any one involved in defrosting of the coil would be aware of the sequences. Hiowever, we are doing the the defrosting with electrical heaters which we find much more efficient and effective. Earlier we were defrosting the coil with hot gas, but found that at a temperature of -35 oC or below, the process does not work as the defrost is not proper.

    My initial question is still unanswered. What is your opinion on the same.

  11. #11
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    Quote Originally Posted by Samarjit Sen View Post
    hendry,

    I am sorry, but to be honest I am yet to understand what yiou said . I shall appreciate if you could please do clarify your comments.
    samarjit,
    i think i could not provide much of my expertise to others from now onwards ...

    Because i've been informed to tune down my pace.

    may be ... some other time.

  12. #12
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    Quote Originally Posted by US Iceman View Post
    Samarjit,

    He is talking about the sequence of operation during a defrost cycle.
    1. De-energize liquid line solenoid
    2. Pump down evaporator
    3. Stop fans
    4. Close suction valve
    5. Energize hot gas solenoid
    6. After defrost is complete...
    7. De-energize hot gas solenoid
    8. Equalize evaporator pressure with suction pressure
    9. Open suction valve
    10. Energize liquid line solenoid and let coil re-freeze water droplets
    11. Turn on fans
    Those are the major items and you could possibly have a few more depending on circumstances.

    thank you, Iceman. at least i know i join the right group of people to further enhance my knowledge.

  13. #13
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Refrigeration System for Agricultural Produce

    I was browsing through the website when I came accross the undermentioned link. Maybe this would be of interest to some.

    http://postharvest.tfrec.wsu.edu/pgD...?article=PC97U

  14. #14
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration System for Agricultural Produce

    Hi, M/S samarjit.

    i've just been released from "quarantine".

    here i'm again sharing my view/s with you on an public channel/s.

    yes, i ran thru you recommended webpage/s.

    i also use some of those modern tech. to enhance our design & pursue better efficiency in total response/s.

    i hope your quest on unit cooler's design has ended with fruitful info after so many parties have answered with much enthusiasm.

    i also take this opportunity to apologize to you in case i might have offend your feeling/s in one way or the other.

    see you in my thread/s [i've started 1 but no response as of to-date] ....

Similar Threads

  1. Single stage refrigeration system optimizing diagram
    By autt in forum System Optimization
    Replies: 34
    Last Post: 03-12-2008, 03:13 PM
  2. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •