    Question Refrigeration plant Hydro test



    Dear all,

    I have a silly question. Does any Refrigeration plant, which runs in satisfactory condition requires pressure test periodically. If it is required and it can be done with Nitrogen then it is ok. But entire refrigeration system or presuure vessel like liquid receivers in large capacity plants can be done with Hydraulic test (Water). Is it advisable? Is there any EHS regulatory requirement any where to do Hydro test of Refrigeration plant periodically, which normally done in other vessels like Boiler.

    With regards,
    P S Rao.



  2. #2
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Refrigeration plant Hydro test

    Hi PS, Most systems only require a pressure test (a ) if you have a leak or if they are shut down for annual maintenance, though this only usual on large plant

    Regards Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  3. #3
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Refrigeration plant Hydro test

    psrao
    1] periodic test in any plant subject to authority requirement.
    2] once your plant in up running, no external water/moisture should enter incidentally.
    3] dry nitrogen is good choice!
    4] test pressure depends on the aging of equipment; possibly to 1.5 times ops pressure.
    5] vacuum test also deem necessary.

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Refrigeration plant Hydro test

    Hi, P S Rao

    Quote Originally Posted by psrao View Post
    Dear all,

    I have a silly question. Does any Refrigeration plant, which runs in satisfactory condition requires pressure test periodically. If it is required and it can be done with Nitrogen then it is ok. But entire refrigeration system or presuure vessel like liquid receivers in large capacity plants can be done with Hydraulic test (Water). Is it advisable? Is there any EHS regulatory requirement any where to do Hydro test of Refrigeration plant periodically, which normally done in other vessels like Boiler.

    With regards,
    P S Rao.

    It is not a silly question, at all...,but all depending on the rules and laws in certain area/country.

    ....it is obligatory to do the pressure test of vessels after every 3-5 years with nitrogen (maybe some x-ray too), but authorities can request a hydraulic test (with water or oil) and then you need to isolate complete vessel and perform it....those rules you must know before making a design the plant (to make flange connections on pipes where you need, drains, additional valves to isolate vessels without to stop the plant during pressure test (maybe for short time), etc) it is expensive but maybe less then to buy a new vessel and especially when change of vessel is almost impossible....)

    ...when we come to this point then we can see how good/bad is design of our refrigeration plant

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Aug 2007
    Location
    Perth, West Australia
    Age
    55
    Posts
    11
    Rep Power
    0

    Re: Refrigeration plant Hydro test

    To answer your question fully, the worst thing that can happen to your system is to get moisture in it. Moisture reacts with most refrigerants to create acid (which destroy the laquer on electrical windings and create sludge) and cause annoying blockages at the LRCD.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigeration plant Hydro test

    Never hydro test a refrigeration that has been in operation. (especially with water, which is what a hydro test usually consists of unless otherwise specified)

    We expend considerable time and energy to ensure the refrigeration system is completely dry before charging refrigerant into the system.

    If you need to do a pressure test, this can easily be done with dry nitrogen before the system is started. I can't imagine why anyone would want (or be forced to) pressure test an existing system.

    If there are leaks then fix the leaks.
    If all else fails, ask for help.


  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Refrigeration plant Hydro test

    Hi, Mike

    Quote Originally Posted by US Iceman View Post
    Never hydro test a refrigeration that has been in operation. (especially with water, which is what a hydro test usually consists of unless otherwise specified)
    Yes, but 23 years before I had to repeat hydro test on each vessel we installed, brand new plant... (in spite what we had for each vessel factory hydro test attest) ....explanation given by inspector was: vessels have been transported to the site and who knows what was during transportation, simple....he was my Freddy Kruger, because we have to install couple of ammonia plants in his area of inspections...

    Quote Originally Posted by US Iceman
    We expend considerable time and energy to ensure the refrigeration system is completely dry before charging refrigerant into the system.
    Right, I was trying many times to explain him about problems if some water remains in system....his answer was....that is not his problem

    Quote Originally Posted by US Iceman
    If you need to do a pressure test, this can easily be done with dry nitrogen before the system is started. I can't imagine why anyone would want (or be forced to) pressure test an existing system.
    ....hard to imagine...how you will call execution of those works....we were forced to hydro tests, drying, etc....we did them all...plant is still running

    What I want to point out....for some old plants, inspector can request hydro test, complete x-ray or to reduce head pressure or to replace all vessels with new i.e. revamping plant...all that for safety what is correct.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigeration plant Hydro test

    HI Josip,

    No, I understand what you are saying. However, it does not mean the inspector is correct.

    I am aware of several projects where this happened to several large screw compressor packages. The pipe fitters (who normally did steam & boiler systems) thought they woud hydro the compressor packages.

    Very big mess!!!!!

    Is it possible to do this?.... yes.

    But it is sure a difficult way to operate a start-up!
    If all else fails, ask for help.


  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Thumbs up Re: Refrigeration plant Hydro test

    Quote Originally Posted by Toosh View Post
    Hi PS, Most systems only require a pressure test (a ) if you have a leak or if they are shut down for annual maintenance, though this only usual on large plant

    Regards Norm
    May I just point out that a existing system requiring a Hydrolic Pressure test is extremely rare although not unkown.
    A Pressure test using Nitrogen is more common but only normally where a physical problem has occured, To make the Pressure Vessels Inspector concerned about strength and integraty? IE. where a weld has failed or pipe has split entering the pressure vessel.
    A Pressure Test is not to be confused with a leak test, both use nitrogen but the pressures required are hugely differant.
    Also extreme caution should be observed when adding any Nitrogen to Part of a system because if your isolation valve / valves pass.
    You are then adding non condensables to your refrigerant side of your system. Personnaly I tend to avoid were possible part pressurising any system.
    I appologise to most of the guys here as I am probably teaching to suck eggs.
    But the number of time I here people say pressure test rather than leak test. I felt it would not harm to point out there is a huge differance.
    Thanks Grizzly

  10. #10
    Join Date
    Jan 2008
    Location
    qatar
    Age
    51
    Posts
    61
    Rep Power
    17

    Re: Refrigeration plant Hydro test

    hai guys can you give me full details about container chiller the brand of carrier.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Refrigeration plant Hydro test

    Hi, rkmoorthy

    Welcome to RE forums....

    Quote Originally Posted by rkmoorthy View Post
    hai guys can you give me full details about container chiller the brand of carrier.
    Can you be more specific with your request (size, capacity, colour), please

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Refrigeration plant Hydro test

    Water is the worst thing you can put in a refrigeration system. Most codes allow for a pneumatic test on the vessels and piping systems as well as hydro test.

    One manufacturer I worked for NEVER tested a refrigeration vessel with water. They used a light oil which was compatible with most oils and refrigerants on all vessels and heat exchangers which they built. They also required the same of vessels they purchased from outside sources. If they could not test with oil, they had to perform a pneumatic test or provide a through drying procedure on the vessel.

    I had a chemical customer "Hydro" test a remote evaporator system and piping after will told them in writing of the potential problems. When we got on site to commission the system, water could be blown from the low point drains. They had to blow hot dry nitrogen through the system for two weeks to get it dry enough to use a vacuum pump. Even with the vacuum pump we still ran a "cold trap" for about 5 days. Then it took another week on the vacuum pump to get it dry enough to charge with R-22 (about 9000# of R-22).

    Now they raised old Billy heck about taking too long to start the system. The flooded evaporators had lo-fin tubes and we figure the fins were holding water.

    So when any one wants a refrigeration system hydro tested on water, I have them sign a disclaimer about the problems of water.

    Ken

  13. #13
    Join Date
    Apr 2008
    Location
    Philippines
    Posts
    12
    Rep Power
    0

    Re: Refrigeration plant Hydro test

    Hi PSRAO,

    Just note and very simple. It's a big NO to introduced H2O to pressure test a refrigeration side for plant installation including the vessels in the circuit is prohibited. Yet for load side you may like water/glycol evaporators etc. As the guys advise, Dry Nitrogen is the best element to be used in testing.

    BR,
    mctavara

  14. #14
    massfd's Avatar
    massfd Guest

    Re: Refrigeration plant Hydro test

    I like the oil idea better, using nitrogen or any other compressed gas for high pressure testing can be like a bomb going off if the vessel ruptures.

    Useing water or oil just results in a big leak as there is no stored energy as there would be when using any compressed gas.

    We have to test our 4500psi air cylinders at 7500psi, they are first filled with water to the top. A rupture during testing just releaves the pressure, I would hate to see what would happen if it contained 7500psi of compressed air

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigeration plant Hydro test

    Quote Originally Posted by massfd View Post
    I like the oil idea better, using nitrogen or any other compressed gas for high pressure testing can be like a bomb going off if the vessel ruptures.

    Useing water or oil just results in a big leak as there is no stored energy as there would be when using any compressed gas.

    We have to test our 4500psi air cylinders at 7500psi, they are first filled with water to the top. A rupture during testing just releaves the pressure, I would hate to see what would happen if it contained 7500psi of compressed air
    Did you read any post above or you just want to impress us with your pressures 10 times greater then what we dealing with?

  16. #16
    massfd's Avatar
    massfd Guest

    Re: Refrigeration plant Hydro test

    Quote Originally Posted by nike123 View Post
    Did you read any post above or you just want to impress us with your pressures 10 times greater then what we dealing with?
    Yes I did read the post and it bothers me that the title is Hydro Test but some are talking about using nitrogen.

    My point was Hydro Testing and pressure testing are not the same thing. Hydro testing results in very little stored energy being released in a failure where a compressed gas failure will release large amounts of energy.

    I have made my point, nike123 whats yours???

  17. #17
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Refrigeration plant Hydro test

    in my 20 plus experience in refrigeration this is my first time i heard of hydro test on refrigeration system.system operating satisfactorily doesnt require leak test,much less a water test.fyi.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigeration plant Hydro test

    Quote Originally Posted by massfd View Post
    Yes I did read the post and it bothers me that the title is Hydro Test but some are talking about using nitrogen.

    My point was Hydro Testing and pressure testing are not the same thing. Hydro testing results in very little stored energy being released in a failure where a compressed gas failure will release large amounts of energy.

    I have made my point, nike123 whats yours???
    Both hydro or gas test are pressure tests and pressure resistant testing is purpose of these tests. My point is all arguments against hydro (water) test elaborated in most of previous posts!
    When you got lot reasons to not use hydro test and only one for use of such test in refrigeration system, then it is wise to consider and judge that arguments on balance against each other.

Similar Threads

  1. advanced refrigeration technology
    By Lc_shi in forum Fundamentals
    Replies: 10
    Last Post: 16-02-2011, 05:22 PM
  2. large refrigeration plant cooling tower issue
    By Lc_shi in forum New Technologies
    Replies: 4
    Last Post: 25-03-2007, 01:35 PM
  3. refrigeration system air-tightness test
    By Lc_shi in forum Fundamentals
    Replies: 20
    Last Post: 08-03-2007, 10:22 AM
  4. Refrigeration Test
    By dannygo in forum Domestic
    Replies: 9
    Last Post: 06-07-2006, 10:18 PM
  5. project of refrigeration plant
    By gesi in forum Fundamentals
    Replies: 5
    Last Post: 12-06-2006, 07:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •