    more daikin questions



    Any idea why a daikin 60 would need 2.5 interconecting cable?(mains is going to out door unit)



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: more daikin crap

    Yes,
    But as I object to your heading of this thread.........

    (And besides, we would need the full model ref to be able to answer your question).


    P.S. let's keep this forum nice, informative and FRIENDLY, if you just want to throw excrement around I suggest you find a local play group.

    (And NO, I have no ties with Daikin what so ever.)

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: more daikin questions

    Quote Originally Posted by dai kin View Post
    Any idea why a daikin 60 would need 2.5 interconecting cable?(mains is going to out door unit)
    What makes you think it needs 2.5mm2 cable?

  4. #4
    Join Date
    Mar 2002
    Location
    Sydney Australia :D
    Age
    53
    Posts
    47
    Rep Power
    0

    Re: more daikin questions

    Indoor unit will take its power from the outdoor for its fan motor and pcb's. Interconnects can be 1.5mm as they are low voltage. You could run the power fro the indoor in 1.5 but not recommended.

    Cheers
    :cool: Do the job once & do it right. :cool:

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: more daikin questions

    Quote Originally Posted by Stuart View Post
    Indoor unit will take its power from the outdoor for its fan motor and pcb's. Interconnects can be 1.5mm as they are low voltage.
    The interconnect cable has to be rated for mains voltage - it is not ELV, i.e. 50v or less, and should be sized in accordance with BS7671.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: more daikin questions

    Quote Originally Posted by jollycold View Post
    He didn't say it was ELV he said it was LV and as such he was right...
    Yes I know, but a lot of folks think that LV = 50v or less

  7. #7
    Join Date
    Jun 2004
    Location
    wales
    Age
    53
    Posts
    25
    Rep Power
    0

    Re: more daikin questions

    Had a good look in side the indoor unit electrics box today and can see no good reason why this unit would need a 2.5 interconecting (install book tells you to use 2.5)it even has a 5amp inline fuse on no1 conection(live).I just can not see the point as it is only on the 60 and 71 range,back to 1.5 on a 100 and 125.

  8. #8
    Join Date
    Dec 2007
    Location
    Gloucestershire
    Posts
    8
    Rep Power
    0

    Re: more daikin questions

    The interconnecting cable on the 'split' units needs to be rated to what ever the main power supply to the outdoor unit is. ie 20amp MCB interconnecting needs to be rated at 20amp. This is because the 240v is looped straight from the main power supply so is still fused at the main MCB. Might have been easier to say that it is not sub-fused in the outdoor unit.

  9. #9
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: more daikin questions

    Inappropriate post- deleted by Mod
    Last edited by frank; 06-12-2007 at 09:45 AM.

  10. #10
    Join Date
    Jun 2004
    Location
    wales
    Age
    53
    Posts
    25
    Rep Power
    0

    Re: more daikin questions

    Good point did`nt think of that! the 100 and 125 single phase units(30amp) are fused down on the outdoor pcb and that is why they still use the 1.5 cable.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. DAIKIN - Weybridge: How to get a Quote.
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 25-04-2007, 08:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •