    404a or 134a for large + temp cold rooms?



    Hello all, I wanted to ask some advice on condensing group choice for a vegetable and fruit cold storage room on a farm.

    The customer wants a quote for two 8m*6m*2.6m cold rooms. As he wishes to recuperate a group he already has for one cold room I only need to quote for one condensing group.

    The suppliers I have contacted have both quoted groups with comps running on 404a.

    1 Unité Hermmétique TFH 4531 ZHR (5.99kw @ 0°c)

    2 Copeland H8-LF-30X (9.24kw @ 0°c)

    I thought 404a was better for low temp aplications and 134a would have been preferable.

    Has anyone got any comments on the use of 404a in positive refrigeration, and or any harm that may come to the compressor if it's not doing the job it was designed for?

    Thanks in advance
    Last edited by expat; 10-12-2007 at 09:50 PM.



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: 404a for positive temp cold rooms?

    Recently after lots of issues on HFC gases, etc, we have been using R 404A for all the applicaitons including low as well as medium temp. We do not face any problems whatsoever with this gas for such applications. Ofcourse it is expensive compared to R 22.

  3. #3
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: 404a for positive temp cold rooms?

    Thank you for that, I didn't think the suppliers would be making an error but better safe than sorry so I thought I would check with the experts

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: 404a for positive temp cold rooms?

    YEP. We also went through the same phase when we suddenly came across units with R 404A for Positive temp.

  5. #5
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: 404a for positive temp cold rooms?

    From transport aspect, today most of the bigger truck & all trailer equipment is all 404a. No adverse effects on recips, scroll or screws. Regardless its deep frozen load ( like ice, frozen meats & fish) , dairy or produce trailers : there's ONE refrigerant only -404a.
    In the CFC days, customers could specc units r12 for producr/dairy/chill temps and then r502 for the 'low temps' down to -29C (-20F).

    Some may argue that 404a is 'overkill' for positive ( above 0deg C) temps but that's just the way things are going - rationalization of product lines and options, inventory mgmt. However' there's no technical impediment to converting a unit 'back' to 134a in the field

    Small delivery vans can still be speccd with 134a or 404a however - application issues.
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  6. #6
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: 404a for positive temp cold rooms?

    I select using R404A whenever possible due its better performance. There is also some speculation the R134a has a doubtful future as a stand alone refrigerant.

  7. #7
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: 404a for positive temp cold rooms?

    Thanks again all. You might be interested in the software on this page

    http://www.bitzer.de/home/index.php?...&CMP=USA&NAV=1&

    You can try different comps on different refrigerants to the the capacity. Worht a look if you don't already know it.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM
  3. Porkka cold rooms
    By Andy AC in forum Commercial
    Replies: 6
    Last Post: 29-08-2007, 08:14 AM
  4. Frost Formation in Cold Rooms
    By Samarjit Sen in forum Technical Speculations
    Replies: 21
    Last Post: 04-08-2007, 05:19 PM
  5. High RH Cold rooms
    By tadipatrir in forum Fundamentals
    Replies: 37
    Last Post: 22-06-2007, 06:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •