    Variable speed drives for single phase motors



    Gentlemen

    Here is another one which i have been wondering about for quite sometime. I have to upgrade a wing of an office building and install variable air volume diffusers to achieve my goal. This dictates that i should vary the air volume from the air handing unit as well. My problem is i should use the existing AHU and it has 3 single phase supply air fans. I have never seen a single phase inveter. Can someone tell me a brillliant idea to use.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Variable speed drives for single phase motors

    Do you have a three phase supply available in the building that you could use ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Variable speed drives for single phase motors

    You could connect these three fans in star as one three phase fan motor and regulate speed with one three phase inverter.
    Last edited by nike123; 10-12-2007 at 07:26 PM. Reason: wrong statement

  4. #4
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Variable speed drives for single phase motors

    Quote Originally Posted by Brian_UK View Post
    Do you have a three phase supply available in the building that you could use ?

    Brian uk

    yes the existing unit is supplied with 3 phase power which they distributed each phase among the 3 fans.

  5. #5
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Variable speed drives for single phase motors

    Quote Originally Posted by nike123 View Post
    You could connect these three fans in star as one three phase fan motor and regulate speed with one three phase inverter if you have three phase supply.
    I understand and agree with you in principle, but i have my fears. does this really work practically. i have never seen or tried it. have you done this before or seen such an installation.

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Variable speed drives for single phase motors

    Quote Originally Posted by nike123 View Post
    You could connect these three fans in star as one three phase fan motor and regulate speed with one three phase inverter if you have three phase supply.
    I understand and agree with you in principle but i have my fears. Have you done this before or seen such an installation. does it really work practically. please let me know.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Variable speed drives for single phase motors

    I didn't done that before but I don't see to many reasons why this should not be working satisfactory in practice if you carefully set min. and max. sped. It is similar to conventional PWM by thyristor or triac in conventional fan speed regulators

    This could be of some value to you:
    http://tinyurl.com/3yb7sr
    http://tinyurl.com/yswttm
    http://tinyurl.com/387tge
    http://tinyurl.com/2lybnj
    Last edited by nike123; 10-12-2007 at 10:23 AM. Reason: adding links

  8. #8
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Variable speed drives for single phase motors

    alternatively you could use a motorised damper in conjunction with a static pressure sensor to meter the air. Although this would involve some clever control.

    You could also use a single phase stepped speed control (transformer type) or a three phase version but you would have to introduce protection on the transformer output side on each.

    Phase chopper speed controllers are available for single phase applications but they are generaly only suitable for low load/ torque.

    all that aside I would rip out the three fans and put a 3 phase fan in

    good luck

  9. #9
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Variable speed drives for single phase motors

    Nikes idea will work but....
    an invertor will probabley pickle itself as you have a greater scope for phase balance faults as the 3 fans will inevitabley load up differently (especially when speed changes occur). My advice is dont do it unless you have time and money to spare

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Variable speed drives for single phase motors

    Quote Originally Posted by TRASH101 View Post

    Phase chopper speed controllers are available for single phase applications but they are generaly only suitable for low load/ torque.
    This is exactly what the fan motors is, low torque and load is rising proportionally with speed.
    If it is compressor, than I should be worried!
    But as you said "advice is dont do it unless you have time and money to spare"

  11. #11
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Variable speed drives for single phase motors

    Thank you guys for all the insights that you are giving me. This forum is such a good idea.

Similar Threads

  1. Replies: 15
    Last Post: 17-04-2009, 03:50 PM
  2. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  3. Variable speed screw compressors
    By Friobernal in forum Industrial Compressors
    Replies: 1
    Last Post: 14-11-2004, 09:28 AM
  4. Variable speed fridge compressors
    By Brian_UK in forum Air Conditioning
    Replies: 5
    Last Post: 18-05-2002, 11:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •