  1. #1
    talon771's Avatar
    talon771 Guest

    process chiller help



    I need some advice and maybe help with the basics:
    I have a Budzar (AC-08) 8 ton air cooled water chiller hooked up to my process. 35gpm/40 psi centrifugal pump. Feed/return lines are 2 inch, 32 foot climb up to my cooling line loop. 1" feeds from that to my process.
    The chiller maintains a 7 to 10 degree F differential, but the water temp climbs up. The compressor runs, no cycle. Pressure on the exit of the pump jumps between 25 and 35 psi. Even when I shut down my process it take awhile for the water temp to come down. I have used similiar sized chillers in the past that have had no problems.

    I have tried opening a cross over valve in my main cooling loop lines to make sure I have good flow through the chiller. Before I did this the compressor would shut off with a low pressure fault.(refrigerant).
    The chiller charge has been checked, pump, strainer and other lines checked.

    The chiller is not new to the company. Could the heat exchanger be scaled up?

    Or is my pump just not big enough?
    Past chiller I have used had the same flow but higher pressure capacity. Other plant had only 20 foot high lines.

    I was told if there is not enough flow through the chiller it won't cool right.

    Any help or pointing to some info to help would be appreciated.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: process chiller help

    By the sound of things there is a capacity problem somewhere and for some reason.

    Unfortunately so is there numerous reasons for this to happen and you really need to get a professional refrigeration engineer to have a hands on look at your system to determine where the fault/issue lies.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Thumbs up Re: process chiller help

    Sometimes as an engineer the real trick is knowing when to admit you are not sure and ask for assitance.
    " I was told if there is not enough flow through the chiller it won't cool right."
    Also with insufficent flow and incorrect safety setups you can crush the evaporator tubes rendering it useless.
    As Viking says Get Help.
    Cheers Grizzly

  4. #4
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    18

    Re: process chiller help

    'Pressure on the exit of the pump jumps between 25 and 35 psi'. if the pressure is going up and down and the pumps sound is changeing simultaneously, to me this sounds like the inlet to the pump is being starved of water. Not enough water flow through the evaperator can cause LP trips.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: process chiller help

    I assume the water loop has an automatic fill from city water supply through a pressure regulating valve (PRV) at the bottom of the loop. These valves come adjusted from the factory at 12psi. Your system needs the PRV adjusted to 16psi due to the height of the loop.

    Increase the water fill pressure and let us know how it worked out.
    Last edited by Gary; 11-12-2007 at 03:40 PM.

  6. #6
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: process chiller help

    Post a schematic with all valves and if you have something else specific...I've had once a problem only with unbalanced pipe network. The chiller worked excellent after but before it couldn't cool down more than DT of 2K. Lets take a look at schematic and than we can discuss...
    BR
    Be careful about reading health books. You may die of a misprint.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: process chiller help

    This thread is from 2007. I assume it has been fixed by now... although the OP did not let us know the outcome.

  8. #8
    1buck's Avatar
    1buck Guest

    Re: process chiller help

    Does the chiller have capacity contol..ie hot-gas by pass?

  9. #9
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: process chiller help

    Don't you just love it when they never come back and tell you the out come. I would like to know what the problem was or did he get fired before it was fixed.

    Ken

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 02:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. Process chiller calc
    By Rowan in forum Tools and Calculators
    Replies: 5
    Last Post: 13-07-2007, 03:28 AM
  4. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •