    new comp,low suction !



    Hi, help plz. If installed a new comp for a 12000 btu split, it was working well for days, then it stop cooling, the liquid line is cold, and only a little suction on the low side. Can the 4 way valve be the problem ? Thanks in advance



  2. #2
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    253
    Rep Power
    17

    Re: new comp,low suction !

    Sorry to be so obvious, but it does have all the hallmarks of 'short of gas'.

    Trevor

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: new comp,low suction !

    I'd agree, it seems short of refrigerant if the liquid line is cold.
    To test the reversing valve, take the pipe temperatures of the discharge in, discharge out, shouldn't be more than 2C difference. Likewise the suction in and suction out should be more than 2C difference.

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: new comp,low suction !

    Could be over condensing. Does it have a fan speed controller?

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: new comp,low suction !

    Quote Originally Posted by TRASH101 View Post
    Could be over condensing. Does it have a fan speed controller?
    Split systems have the TX inside the outdoor unit, so the liquid line he's refering to as cold is after the flow control device. Normally that's not cold (as in under 10C cold), unless it's expanding too early, ie. low in refrigerant.
    A split system short on refrigerant will normally have a cold "liquid" line. The easiest way to spot a split short of refrigerant is a frosted up "liquid" line.
    On a normally charged split system system, the "liquid" line will be warmer than the suction line.

    edit: like in a regular commercial system, anything low on refrigerant will ice up the entry of the evap and not cool effectively. In a split they will have a low temp or frost on the "liquid" line.
    Last edited by paul_h; 07-12-2007 at 12:07 PM.

  6. #6
    Join Date
    Oct 2007
    Location
    PHILIPPINES
    Age
    47
    Posts
    10
    Rep Power
    0

    Re: new comp,low suction !

    newly installed compressor means,the former compressor electrically burned or mechanically damaged where some foreign materials blocked a certain points of the system in general.

    if the system was been flushed out,leak free and well vacuumed,we may say the aboved mentioned refrigerant shortage is the cause and additional charging is recommended.add some and observe.

    if problem ,no cooling ,which is the specific problem of all the system exists,try to flushed out the system again and install new drier if it was not been changed lately and follow the basics steps of a leak free and cleaned system,b4 energizing the system.

    thanx

  7. #7
    Join Date
    Dec 2007
    Location
    South Africa
    Age
    41
    Posts
    17
    Rep Power
    0

    Re: new comp,low suction !

    Thanks to all your replys, hope to solve the prob!

Similar Threads

  1. suction line freezeing
    By karimihassan in forum Air Conditioning
    Replies: 4
    Last Post: 05-08-2007, 05:17 AM
  2. liquid injection triggered on low suction method
    By liptow in forum Fundamentals
    Replies: 10
    Last Post: 22-03-2007, 03:37 PM
  3. Replies: 10
    Last Post: 18-03-2006, 08:35 PM
  4. Suction temp
    By Temprite in forum Commercial
    Replies: 18
    Last Post: 30-05-2005, 10:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •