    110v 60hz in a country w/ 220v 50hz



    Can I use a fridge 110v 60hz in a country w/ 220v 50hz with a power inverter that lowers the 220v to 110v bt can not change the 60hz to 50hz obviously?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    It is the frequency that determines the speed of a motor not the voltage. If you had a 4 pole motor rated at 50hz then the speed would be determined by the following formula:

    (seconds in minute x frequency/pole pairs) - friction losses.

    friction losses can vary but are normally around 4%. So for this motor the speed can be determined as:

    60 x 50/2 - 4% =1440rpm

    If you had the same motor running at 60 hz then the speed would be 60 x 60/2 - 4% = 1728rpm - this is an increase of 20% so the amp draw would be increased, the heat generated by the motor would be increased but the life of the motor would be shortened.

    The answer to your question is yes - but not for long!


    Frank

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34
    Although it isn't clear, I'm thinking the question involves running a 60hz unit on 50hz power, in which case the opposite would apply.

    The unit's capacity would be reduced by about 20%, and less heat would be generated. In other words, it wouldn't hurt the system (assuming the voltage is correct), but it may not have enough cooling capacity to do the job.
    Last edited by Gary; 18-03-2003 at 10:49 PM.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    Gary

    I agree, but when the motor is wound for 60hz then exactly what I've said happens.

    Frank

  5. #5
    dkupinsky's Avatar
    dkupinsky Guest
    Thanks for your help.
    I have found a fridge with specifications of 50hz/60hz - is it possible to have a motor that switches or does it make more sense that it is a 60hz motor that will work on 50hz power?

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    We've had quite a few problems with 60hz cam timers on York condensing units. These units are manufactured in the US, shipped to France or thereabouts, the wiring is changed to comply with CE markings and then finally shipped to the UK for installation.

    Because the cam timers are wound for 60hz, when they are operated on 50hz the get really hot and eventually burn out. Even York admit they are a constant problem.

    I've seen many a 60hz fan motor "melted" after being run at 50 hz.

    Frank

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    dk

    Does the compressor name plate give 2 running currents for the different frequencies?

  8. #8
    Join Date
    May 2006
    Location
    Australia
    Age
    48
    Posts
    12
    Rep Power
    0

    Re: 110v 60hz in a country w/ 220v 50hz

    Hi
    the problem is very simple to understand.

    Operating at 50hz will slow the rotor.The speed of an induction motor is given by 120*frequency/no pole of motor less 4% for full load speed.

    The BIG problem comes when you transform the voltage to 110v ac 50 hz. This violates the rated airgap flux of the motor and results in magnetic saturation giving rise to EXcessive heating!!!!

    To overcome this the voltage/frequency ratio must be maintained as the frequency is changed. A typical VSD does this in ausie slang we calll them VVVf drives ie variable voltage variable frequency drives.

    to fix your problem your motor's native volatge frequency is 110v/60 must equal ?/50

    ?=92V if you fed your compressor 92V@50hz via a cutom made transformer it will work perfectly.The speed will be lower but the motor will be more energy efficient as its iron losses are lower when operated at the corect voltage at reduced frequencies.

    I know this as i commision and design variable drive systems for motors rated 10kw to 10 megawatts. Its always boils back to the same basics.

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: 110v 60hz in a country w/ 220v 50hz

    I have two peices of machinery that are designed to run at 240 @ 50Hz, How would they opperate at 208V @ 60Hz?

    I don't think any thing would be need doing as the voltage drops with the gain in frequancy but you'd know better!

    Thanks.

  10. #10
    Join Date
    May 2006
    Location
    Australia
    Age
    48
    Posts
    12
    Rep Power
    0

    Re: 110v 60hz in a country w/ 220v 50hz

    Hi
    If you operate a 240v 50hz compressor on 208v 60 hz it is likely to stall if you chrge it up fully. The reason now is you have reduced the volatge per hertz ratio which will cut the torque availble to the compressor by a square of the volatge reduction percentage.
    \
    This means if this 50hz compressor is to operate in a 60hz supply you will have to feed that baby 288V!!!
    but you are only giving it 208 V.

    (208/288)squared = 0.52 which means its likely to halve its available torque which means it will opeate slower than when it was on 50Hz and worse is it will operate hotter and stall easier due to excess slip of the induction motor.

    Looks like the only way you can get good results with this one is to operate it at a bit less than 50% capacity at 208V60hz or less or risk stalling and overheating on aconstant basis.

    My thoughts are it will be an abortion.

  11. #11
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: 110v 60hz in a country w/ 220v 50hz

    Quote Originally Posted by dkupinsky View Post
    Can I use a fridge 110v 60hz in a country w/ 220v 50hz with a power inverter that lowers the 220v to 110v bt can not change the 60hz to 50hz obviously?
    If it's just a fridge, then yes, I've seen a fair few in australia run for years. Most of the posts here are comparing more complicated things than a basic fridge.
    You will lose some performance and defrost cycles will be out, but it will work.
    But then again, a transformer to run them aren't cheap, and moving something as heavy as a fridge internationally isn't cheap. You're better off to buy one to suit local mains supply in the country with a different voltage/frequency.

  12. #12
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: 110v 60hz in a country w/ 220v 50hz

    Quote Originally Posted by The MG Pony View Post
    I have two peices of machinery that are designed to run at 240 @ 50Hz, How would they opperate at 208V @ 60Hz?

    I don't think any thing would be need doing as the voltage drops with the gain in frequancy but you'd know better!

    Thanks.
    Most things that are desgined to run in countries with 240v mains are actually rated at 220v. For example here in australia most houses have 230-250v mains, the most common being 240v, But all the gear we get here is rated for 220V and the national standard to 230v.
    That being said, I've seen stuff fall over and die at 217V. so I don't see much hope on running them at 208V.
    What you're asking them to do here is run faster at less voltage, even less of a chance of them running at 50hz and 208v which is a big ask in itself

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: 110v 60hz in a country w/ 220v 50hz

    Slightly confusing the situation. I have bought 115V 60HZ POWER TOOLS from USA working on the premise that running through a 110v 50hz transformer. They would just run slightly slower and draw less amps.
    So far it has proved to be a very very cheap source of Industrial grade (110v) power tools.
    Which appear to run fine!
    Is that correct?
    Grizzly
    ps Has anyone noticed how old this thread is?

  14. #14
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: 110v 60hz in a country w/ 220v 50hz

    Quote Originally Posted by Grizzly View Post
    Grizzly
    ps Has anyone noticed how old this thread is?
    More often than not what happens is that someone will be looking through threads and reply to a post without realising that it is out of date.
    Then people answer their posts and hey presto the thread is alive again.

    you won't catch me replying to old posts.

    taz

  15. #15
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: 110v 60hz in a country w/ 220v 50hz

    Good info from Frank and Gary but it looks like Tsangep is " THE man of the moment " when it comes to motors and frequencies - so ,,,, it's good to meet you online Tsangep, no doubt we will call on your motor knowledge further.

    Attached is something useful for readers, perhaps - it deals more specifically with 3 phase power : a little old but this solid info never goes out of fashion.
    It's along the same line as Tsangep said about any frequency variation should be in same ratio as the voltage variation ( or conversely). I.E. running a 460/3/60 rated motor on 380/3/50 supply.

    best regards
    T-P
    Attached Files Attached Files
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  16. #16
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: 110v 60hz in a country w/ 220v 50hz

    Well if any one is curious the equipment was a nice washer & drier from Switzerland, it is now running on a 230V circuit as messured at the plug and seems to be doing fine.Need to replace the timer motor though with a 60Hz wound one lol.

  17. #17
    e_alfares's Avatar
    e_alfares Guest

    Re: 110v 60hz in a country w/ 220v 50hz

    Dear Gentleman;
    I have 250 Pcs of Trane Air-condition 50Hz ,in saudia Arabialace we have 60 Hz ;If their is any converters in the market or solution to convert it please advise me.
    >>
    Best Regards

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: 110v 60hz in a country w/ 220v 50hz

    Quote Originally Posted by e_alfares View Post
    Dear Gentleman;
    I have 250 Pcs of Trane Air-condition 50Hz ,in saudia Arabialace we have 60 Hz ;If their is any converters in the market or solution to convert it please advise me.
    >>
    Best Regards
    There is nothing which cost less than air conditioner itself.

  19. #19
    flavius005's Avatar
    flavius005 Guest

    Re: 110v 60hz in a country w/ 220v 50hz

    Hello,

    I would like to as what happens if I use a Black& decker jigsaw that I bought from US,in Europe.

    I want to use a voltage converter from 220V to 110V but I'm warried about the frequency...for US is 60 and 50 in Europe.

    Is there any risck if I use it at 110V - 50 hz?

    is there a way to obtain 110V - 60 Hz from 220 V -50 Hz


    Thank you

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: 110v 60hz in a country w/ 220v 50hz

    Quote Originally Posted by flavius005 View Post
    Hello,

    I would like to as what happens if I use a Black& decker jigsaw that I bought from US,in Europe.

    I want to use a voltage converter from 220V to 110V but I'm warried about the frequency...for US is 60 and 50 in Europe.

    Is there any risck if I use it at 110V - 50 hz?

    is there a way to obtain 110V - 60 Hz from 220 V -50 Hz


    Thank you
    Did you read anything what was written in this thread before you posted this question?

  21. #21
    robertlight's Avatar
    robertlight Guest

    Re: 110v 60hz in a country w/ 220v 50hz

    It seems by your calculation below that the motor would run at a slower speed at 50hz than at 60hz... so why would it burn out?

    I suppose in a refrigeration application it would have to run longer to get the same work done.... and since it is running slower, whatever cooling facility it had would be less efficient.

    What a shame... I would love to buy appliances that would work both in the U.S. and in Europe. Where in the world did they get the idea of 50hz in the first place? 220V I can understand... copper is more efficiently utilized...but alas homeowners are more likely to be killed at 220V.

    Many thanks for the physics lesson.

    - Bob

    Quote Originally Posted by frank View Post
    It is the frequency that determines the speed of a motor not the voltage. If you had a 4 pole motor rated at 50hz then the speed would be determined by the following formula:

    (seconds in minute x frequency/pole pairs) - friction losses.

    friction losses can vary but are normally around 4%. So for this motor the speed can be determined as:

    60 x 50/2 - 4% =1440rpm

    If you had the same motor running at 60 hz then the speed would be 60 x 60/2 - 4% = 1728rpm - this is an increase of 20% so the amp draw would be increased, the heat generated by the motor would be increased but the life of the motor would be shortened.

    The answer to your question is yes - but not for long!


    Frank

  22. #22
    Join Date
    Jun 2007
    Location
    Norway
    Age
    74
    Posts
    56
    Rep Power
    17

    Re: 110v 60hz in a country w/ 220v 50hz

    I am used to a lot of USA equipment rated 60hz here in Europe. We sold many blood bank fridges and on them they simply made a step down trafo 100v to make the correct voltage. The units with a small Copeland works well and many units out there is more than 20 Years old. The even more strange is that they used a currrent type start relay who had to kick in about every 3 minutes(X20Years). What a quality on those parts.An important issue is that a slower rotating compressor (50hz)sucks a lot more of amperage than on 60hz. Copeland 115volt 60hz and 100volt only on 50hz to prevent the current and heat to destroy them. Copeland is more aggresive to rate the voltage these days. The ultra low temperature freezers with Copelands we trade are rated 208-230 at 60hz and only 200volt at 50hz. The lower speed make fewer changes of the impedance who gives less resistance and make them to suck quite higher amperage for sure. A little on the side, but a product as a contactor rated at 60hz draws same way because the impedance to a higher amperage. I have equipment burning those coils and the US marked never saw it due to their less amp/heat over them by 60hz.
    Another maker who produce all kind of waterchillers/circulators had only one extra in the specification and that was a 17% capacity reduction if used on 50hz and it was approx. the truth too. Never saw a reduced lifetime on them, but the ULT units we trade get a shorter lifetime to at a beginning to hard working low stage compressors.

  23. #23
    Join Date
    May 2009
    Location
    aust
    Age
    53
    Posts
    14
    Rep Power
    0

    Re: 110v 60hz in a country w/ 220v 50hz

    So technical.im with grizzly.an old recip on r22@50hz eg carrier120 rated at 60hzwas charged with r500 and the refrigerant seemed to solve the issue .or is that the issue?

Similar Threads

  1. 50HZ compressor on a 60HZ circuit
    By dan wong in forum Technical Speculations
    Replies: 28
    Last Post: 13-06-2009, 05:52 PM
  2. 50Hz vs. 60Hz, okay to run at slower frequency?
    By pezagent in forum Commercial
    Replies: 10
    Last Post: 26-05-2003, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •