    Daikin VRV piping restriction



    Hi all,

    one of the piping restrictions on a VRV install is the maximum distance of 40m from the first refnet to the last indoor unit. I assume that has to do with the pressuredrop.
    The distance between the ou and the first refnet could vary greatly(within other restrictions), but there is still the same 40m max length.
    Does anybody know why?

    Cheers

    sumsor



  2. #2
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin VRV piping restriction

    I would say Pressure Drop and Oil Return.

    This could have a bearing on system operation and compressor life.
    No longer Active

  3. #3
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin VRV piping restriction

    Indoor units try to maintain target superheat through exp valve to control discharge superheat. If you have pressure drop then the pipe length judgement that is carried out during test operation could calculate wrong target settings and set wrong operating parameters. This can srew up a number of things.
    No longer Active

  4. #4
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin VRV piping restriction

    Sumsor

    Sent you a PM about the stages of test operation and what it looks for and how it calculates.
    No longer Active

  5. #5
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Daikin VRV piping restriction

    The reason for the 4om rule is to maintain equal and balanced pressure within the field piping and to ensure pressure drop is kept at a minimum. The greater the length of field piping, the more pressure drop, the technical data book will have a chart inside showing the drop dependant on length and height difference between indoor and outdoor units (The inverter compressor can compensate for this drop). There is a possible extension to this rule, up to 90m can be achieved, as long as the equivalent length between furthest unit to the first refnet and closest unit to the first refnet is no more than 40m (Equivalent Length). In this instance, an increase in size of main piping between refnets will be required to be done x 1 size up, and of course, only if Daikin give it the go ahead.

    The pressure drop is calculated during the test operation, where it also calculates length of run (Short/Medium/Long), and is calculated as follows:

    Evaporating target set to -15.

    During test operation the units will attempt to reach this target, if say you have 4 x indoor units and they all achieve -10. The system adds all these figures together = -40. It then divides this total by the number of indoor units -40 divided by 4 = -10. It subtracts this -10 from the target of -15 which equals +5.

    If this final figure is < 3, this would be considered a short piping run
    If this final figure is < 6, this would be considered a medium piping run
    If this final figure is > 6, this would be considered a long pipe run

    (On an old G series VRV system, there was a switch on the PCB which should have been set)

    The example above would mean the system would be considered a medium pipe run. Pressure drop is calculated during this operation.

    I hope the above above helps
    Last edited by Mentallist; 19-07-2010 at 08:29 PM.

  6. #6
    Join Date
    Jan 2009
    Location
    NZ
    Age
    48
    Posts
    35
    Rep Power
    0

    Re: Daikin VRV piping restriction

    Hi Crash Pilot and Mentallist,

    thanks very much for the quick replies. Exactly what I was looking for, very much appreciated.

    Sumsor

  7. #7
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Daikin VRV piping restriction

    I hear that Daikin VRV piping limits will be longer come end of this year/early next year. No details as of yet, but 1 thing I did hear is the level difference between indoor units will be extended to 30m as opposed to the current 15m, may also be further extensions to current total piping length. We shall see

  8. #8
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin VRV piping restriction

    Been out of the VRV circle for a while but have heard from a friend that units are already available and being installed in Aust.
    No longer Active

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Customer question re Daikin piping
    By thegeby in forum Air Conditioning
    Replies: 2
    Last Post: 17-01-2008, 09:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •