    I just began working for a refrigeration company and I come accross Walk-In cooler systems where the suction line is frosted all the way to the compressor.
    Fellow workers tell me that it is nothing to worry about. What I remember from school tells me that this should not happen at any time. Is this not a sign that the system is over charged?
    11,025
    Re: Suction Line Freezing
    Not neccessarily.
    What is the ambient temperature and what is the pipe temperature?
    Nov 2005
    New Zealand
    550
    Hi John Did you check the superheat
    regards norm
    My wife used to say you never listen to a word I say at least I think that what she said
    disturbed's Avatar
    disturbed Guest
    Hey johan
    let me tell. Is U have Section Reciver used Return Section pipe?
    Jul 2001
    Sydney, Australia
    753
    It all depends what the temps of the system are. If that pipe temp at compressor is below zero - chances are it'll form snow/ice. The system may still be running with a good amount of superheat - for example when setting up our supermarket racks we aim for around 20K superheat max, this means on a freezer system that runs at -30sst (refrigerant temp in coil) you will likely see -10C back at the compressor (pipe temp) this is 20K of superheat but at -10C will freeze any moisture to the pipe and form ice - its still superheated though with no chance of smashing comps with floodback.
    A medium temp system will generally not ice at the comp as it runs at between -10 and 0C sst (depending on design), add some superheat and the pipe at the comp is usually above freezing point and will sweat only depending on the ambient air conditions (dewpoint)
    ...and she said "give it to me you big fridgie"
    Oct 2003
    5,630
    34
    This is such a big common misunderstanding. Even teachers still teach that you may never see frost on the suction line.
    Pennsylvania
    113
    I imagine those teachers would faint in the engine room of my -40f ammonia system. It has balls of ice 3" thick coming off the small uninsulated areas of pipe right before the compressor.
    Ice on the pumped liquid pumps is at least 6" thick.
    As was said previously - frost on the suction line is not a problem with lower temp systems.
    Then again, what's the old saying? "All generalities are false - including this one"
    Feb 2006
    derbyshire
    610
    if its a cooler then somethings wrong assuming the rooms not below 0 deg C, are the evaps iced up,dirty,no air flow ? if thats o/k its start looking at TEV,s ,overcharging etc.
    Jul 2001
    Sydney, Australia
    753
    Same in Australia - like brian_chapin says... show them a pumped liquid system and they'd fall over
    I think they must all be domestic or air conditioning mechanics originally
    Nov 2006
    63
    392
    Quote Originally Posted by 750 Valve View Post
    Not this teacher, been round the block several times and seen and worked on most things out there.
    I have experienced engineers come into our workshop and flip due to the ice on the suction lines of our -20 deg C coldrooms when the students run them up, as the installations are only used for a couple of days we do not insulate due to the cost. These engineers utter those immortal words "there's liquid going back to the compressor" most of them do not understand the basics which freightens me.
    Ian
    Somerset
    69
    4,711
    Hi Pooh.
    Didn't Glen Moore of Danfoss Tech. Support do a piece in the Service Engineer Mag recently on this very subject.
    Incidently the scariest thing about an iced up liquid pump. Is when you have to remove the build up to service the pump. Sometimes only a hammer will do -scary!
    cheers Grizzly.
    Take heart your obvious proof that there are knowledgeable trainers out there!
    Nov 2006
    63
    392
    an ex colleague of mine turned up on site to do a liquid pump change to find the site fitter removing the ice ready for him with an air chisel at which point my mate left the building for breakfast at a cafe about two mile away. There are some very scary people out there.
    Ian
    Aug 2003
    Netherlands
    49
    620
    21
    To futher the discussion and perhaps a learning experiance, tell me if the amount of ice on this compressor is ok or if there's a problem.
    Some info, it's a chiller delivering brine at -10 dgr C.
    Nov 2006
    63
    392
    Sanderh
    is there any measurable superheat at the compressor, if so it is OK, if not then you have a problem. If you are supplying Glycol at -10deg C then you will be evaporating at nearer -20deg C so even with 8def K superheat the vapour coming down the suction line will be at -12deg C so you will get frost.
    Without measuring the superheat we are all guessing if there is a problem.
    Ian
    Aug 2005
    5,302
    I continue to be amazed at this topic.
    Ice forms below the freezing temperature of water (32°F or 0°C).
    If the evaporating temperature + the evaporator superheat is still below below the freezing temperature of water (32°F or 0°C) ice or frost will form.
    Lack of superheat tells you if you have liquid, not frost or ice.
    Oct 2003
    5,630
    34
    I think Sanderh knows the answer for his question, it's only to see if others can judge this right like Pooh.
    Somerset
    69
    4,711
    [quote=Grizzly;86469]Hi Pooh.
    Iceman.
    Your point is very valid,
    If I can I will get a copy of the article I refer to and post a copy.
    It basically say's the same as you. In that "fully" trained Engineers can't seem to get their heads around the fact that Ice dosn't allways mean liquid floodback.
    And it can just be sub-zero (0c) superheated vapour!
    Don't give up on us yet!
    Grizzly.
    Aug 2003
    Netherlands
    49
    620
    21
    Your right Peter! Problem was solved months ago, a no brainer! Just wanted to help "educate" my fellow ref engineers! (Don't get upset, I don't mean anything by it).
    Due to sensor faults all oil was lost to the evaporator and thereby limiting refrigirant flow through the evap and thus causing the compressor to frost over!
    Fault was easy to find, but then getting all the oil back! That took 4 hours, after replacing the sensors!
  19. #19
    Aug 2005
    5,302
    Now that we have this cleared up, let's look at a similar condition where liquid can exist.
    If you have a suction line operating below freezing temperatures you can easily tell if liquid is present or not. If the suction line is frosted over a bit, scrape off the frost with your fingernail. If the frost does not reform on the suction line this simply means the line is cold.
    If the frost reforms quickly, then there is a slight amount of liquid present in the line.
    Cold gas forms frost very, very slowly while liquid will boil off and allow frost to form much more quickly.
    I bet some of you older guys have noticed this too.
  20. #20
    Feb 2001
    Doncaster, England
    199
    Hi 750 Valve,
    This sounds an excessive amount of superheat - it makes the system less efficient.
    5 - 7K is more than sufficient.
    Tony
  21. #21
    Somerset
    69
    4,711
    Thumbs up Re: Suction Line Freezing
    I have another, Clear the frost from an area, lick the end of your finger. Place it against the pipe and if it sticks or there is resistance as you pull your finger away.
    Generally there is liquid there!!
    And remember to remove your finger slowly! It Works, try it.
  22. #22
    Aug 2005
    5,302
    Yep, that works also Grizzly.
    But, you learn quickly not to let your finger stick. Once is all it takes.
  23. #23
    malaysia
    159
    Quote Originally Posted by Sanderh View Post
    i feel your photo display an abnormal state for a semihermetic comp.
    my photo for sharing of normal operations.
  24. #24
    Oct 2006
    1,843
    21
    Or as I once saw a student do.
    Just lick the pipe!!
    You can't buy inteligence
    taz.
  25. #25
    Jul 2001
    Sydney, Australia
    753
    Quote Originally Posted by Tony View Post
    Hi 750 Valve,
    Mate thats MAX total system superheat (measured at compressor inlet), if I had 5k back at my racks I'd be a bit worried, a change in conditions in the cases/rooms (evap fan failure) on the rack will likely end up in floodback (not just ice, but the type your valves don't appreciate ).
    The 5-7k you speak of is EVAPORATOR superheat, I am talking about TOTAL SYSTEM superheat.
    pooh its good to know somebody's teaching them correctly
  26. #26
    Apr 2001
    79
    5,071
    35
    In a suction line, liquid droplets can and will travel with the superheated vapor. This is called "carryover". All of those droplets will disappear at about 5.5K/10F superheat.
    But as 750 Valve points out, this is cutting it too close. Small fluctuations can allow liquid to reach the compressor valves.
    Compressor manufacturers recommend a minimum of 11K/20F superheat at the compressor inlet.
    This may or may not involve frost. There are many systems out there with frost on the compressor, yet they are not necessarily flooding.
    You can only tell by measuring the superheat.
  27. #27
    Nov 2006
    63
    392
    Iceman, Grizzly
    I too have used the sticking finger method but I beleive that without knowing the actual superheat you are as good as guessing, yes it is a guide but there is no substitute for actual accurate measurements. These then give you the information to do analysis accurately and fix the problem first time.
    Ian
  28. #28
    Aug 2005
    5,302
    I'm in agreement with Ian. There is no substitute for good hard data.
    The finger method or scrapping off frost is one of those "quick" ideas for trying to find the culprit quickly.
    It goes back to some comments Peter made in an earlier post about using your five senses to find problems a little faster. These are invaluable if the person knows how to interpret the information so that they can begin to collect data from the problematic area.
  29. #29
    Somerset
    69
    4,711
    Ian.
    You guys at Star get all the toys don't you!
    But I have to buy the batteries for my thermometer and I have 10 fingers.
    Some of them are slightly de-sensatised. Due to picking up to many hot pieces of metal before I should of.
    Although as Iceman points out I may not have for long.
    And as Taz points out there is allways my tounge!
    Are you telling me I have got to buy a new battery?
    And has anyone tried these new Lithium ones yet?
  30. #30
    Nov 2006
    63
    392
    do'nt tie me to Star, other than teaching their apprentices and having some good freinds who work for them I never have (do not know why). We all use all of our senses to find faults but how many of us have been caught out by them, I have on more than one occassion and ended up doing more work than I had to.
    Ian
  31. #31
    Apr 2001
    79
    5,071
    35
    Short cuts should only be used by the experienced and should never be presented as the right way to do things. They have no place in the schools.
    First learn the best way. Short cuts come later and should be understood to be inferior to accurate measurements albeit sometimes faster.
    That said, there is merit to using the senses. For example, imagine that you enter a very cold environment. You grasp a block of wood in one hand and a steel pipe in the other hand. They are the same temperature, but the steel transfers the heat from your hand much faster and thus feels "colder".
    While the skin is a poor judge of temperature, it is a fair judge of rate of heat transfer.
    It is possible to grasp a suction line and feel the ebb and flow of liquid as the TXV modulates, due to the difference in rate of heat transfer between the vapor and the liquid.
  32. #32
    Somerset
    69
    4,711
    [quote=Pooh;87018]Grizzly
    Pooh.
    Sorry I must have misread some of your posts.
    Gary, Pooh and anyone else I have misled. It was only ment as a light hearted comment not to be taken to seriously.
    Surely sometimes, a little humour is as such a good teaching tool as being deadly ernest?
    Cheers Grizzly.
    Last edited by Grizzly; 21-12-2007 at 01:07 AM. Reason: Iceman had allready stated his view
  33. #33
    raju's Avatar
    raju Guest
    The line froast would be assessed based on the sction teperature!!!!!!
    Quote Originally Posted by John Kuchinic View Post
  34. #34
    Mar 2005
    638
    Sounds like you need to do a bit more studying. An A/C application should not have frost or ice on the suction line. If you are operating a refrigeration unit on a freezer, the suction line will have frost of ice on it if it is not insulated.
    Look at you evaporator temp and suction temp and see where you are.
    Ken
  35. #35
    Apr 2006
    41
    1,620
    Worked on a sandwich cooler while back, R-12 all glass. Suction line had a wonderfull frost coat, well more like ice coat.
    Why in a hot resteruant did it have the ice? Well humidity and a frozen up evap! Solution was simple, give her a defrost and then insulate the suction line to stop sweating and fix the defrost timer!
    The freezer was the same old kit, Rest of it was fine but gave it a therough defrost dried off the suction line and insulated it up nicely but to be safe checked SH and it was just dandy, reason for the several foot thick ice was just it was running in a humid environment at a chilly temp, nothing to sweat over, frankly I get worried when I see a freezer with out some sort of frost!
  36. #36
    82
    74
    Keep it simple WORK ON AIR CONDITIONING.
    Frosting back...
    1. Compressor runs continuously?
    2. Reduced air flow?
    3. Oversized equipment/refrigerant?
    4. Contactor stuck on replace?
    5. Clean filters.
    6. Check drive belts.
    7. Fit hot gas bi pass.
    8. Charge to full s/g(near enough its only air conditioning)
    R22 do whatever it takes to maintain 200psig high 60psig low.
    Don't injure yourself, I had to run a job at 400psig to stop frosting.
    Do not get fixated on the txv!!!
    Grump
    Last edited by chillin out; 05-02-2008 at 05:36 PM. Reason: Very confusing post...lol
  37. #37
    Feb 2008
    Las Vegas, NV
    67
    330
    This compressor has 15 degrees of superheat.
    Frost tells you it's below dewpoint but......always check the superheat to verify there's no flooding.
  38. #38
    Aug 2001
    Gold Coast, Australia
    600
    28
    What the old guys always told me was that if the suction line is frozen - don't worry. If the compressor body is frozen - you've got a problem.
  39. #39
    Dec 2006
    69
    35
    You guys need to watch out for the electrical terminals with those semi's, make sure there's a good earth cable attached, found too many with the insulators burnt right through yet still running!
  40. #40
    Auckland
    74
    3,357
    37
    the enthalpy of saturated suction vapour will not form ice on suction at compressor if superheat of TX vav is correct and system is designed with correct balance. Basic design criteria. Back to to basics people.
    Spot compressor so iced-up, fortunately it is a screw-semi, got injection oil cooling covered, but oil carry over is got be a problem.
    magoo
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. Suction line?
    By SkyWalker in forum Fundamentals
    Last Post: 18-05-2009, 10:34 PM
  3. suction line freezeing
    By karimihassan in forum Air Conditioning
    Last Post: 05-08-2007, 05:17 AM
  4. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Last Post: 08-05-2002, 05:19 AM