19-03-2003, 02:45 PM #1Why? There is not much pressure drop over suction line piping between the outlet of the evaporator and the compressor inlet. Mass flow is low, the 3/8" piping is wide enough to reduce gas speed in the suction line and therefore friction losses, and there is only 45cm / 1.5ft of piping between the evaporator outlet and compressor inlet.
The measurement of the gas temperature from the evaporator can be considered accurate since the small themocouple is mounted inside the receiver in a piece of 1/4" copper, where the suction gas passes over directly.
I am planning on mounting a pressure gauge on the compressor's service port. I have more space over there to mount such a gauge.
During pulldown everything worked fine, and the TEV showed it's best side by providing a much quicker pulldown than the capillary tube. However, as soon as the temperature and load reached their lowest points, the TEV became instable and started oscillating by injecting not enough refrigerant , an increasing amount of refrigerant up to the point where liquid was returned to the compressor, and then reducing the amount of refrigerant again until the evaporator starves.Last edited by Gary; 19-03-2003 at 02:57 PM.
Similar Threads
-
Pressure Transmitter R134a Setpoints
By cooltrain in forum Technical SpeculationsReplies: 0Last Post: 28-02-2005, 09:05 AM -
Is there anything about R134a that is better than R12?
By dude in forum RefrigerantsReplies: 5Last Post: 01-03-2004, 09:59 PM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM -
Minimal required R134a speed in suction line
By DaBit in forum CPU OverclockersReplies: 32Last Post: 08-05-2002, 05:19 AM -
Effect on design evaporator by using R507 instead of R22
By lappee in forum RefrigerantsReplies: 2Last Post: 18-09-2001, 05:15 PM