Results 1 to 8 of 8
Thread: mitsubishi mr slim
-
06-12-2007, 01:23 AM #1
mitsubishi mr slim
Hi all,
This Mr Slim just brought up a phase rotation fault when the sparks pulled fuses out one by one. The sparks put the fuses back one be one and two out of the three units showed a phase rotation fault.
ANY IDEA WHY?
Thanks
-
06-12-2007, 01:35 AM #2
Re: mitsubishi mr slim
what works did the sparks do while the fuses were out?
Paul
"KEEP IT COOL"
-
06-12-2007, 01:40 AM #3
Re: mitsubishi mr slim
Have you switched the unit off and on again after the sparky played with the fuses ?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-12-2007, 01:43 AM #4
Re: mitsubishi mr slim
On the old fixed speed units if you run for any time on 2 phase then the compressor motor windings will burn out. Unit would only stop if control board supply phase disconnected.
On newer inverter units pulling fuses one by one like this could potentially cause damage to the inverter.
I think most 3 ph Mr Slims have always had phase rotation protection because the scroll compressor needs to spin only one direction.
Did the unit run ok after power reset ?
If not then there may be some damage which will need further investigation.
-
06-12-2007, 10:08 AM #5
Re: mitsubishi mr slim
The unit did not still has a fault, two units have a phase rotation fault. one unit was fine. the sparks pulled fuses to do his five year electric test. after his test he put the fuses back and two out of three units have this fault. the units are 7 years old.
-
06-12-2007, 10:39 AM #6
Re: mitsubishi mr slim
To eliminate any mains supply problem you need to use a phase rotation tester at the isolator.
We had the same fault occur after a sparky replaced the outdoor isolator due to vandalism, but we traced it back to a faulty mcb - just coincidence with the work the sparky did.
If the Mr Slim can't see 3 phases you get the same fault code.
-
24-08-2009, 06:57 PM #7
Re: mitsubishi mr slim
Any Info on why i cant get 12v reading going to controller par21
-
13-01-2010, 08:26 PM #8
Similar Threads
-
Mitsubishi Light Truck Refrigeration
By Mastercool in forum TransportReplies: 2Last Post: 23-11-2007, 07:15 AM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 11:23 PM -
mr slim
By Andy AC in forum Air ConditioningReplies: 2Last Post: 18-10-2007, 11:43 PM -
Mitsubishi compressor lock
By marc5180 in forum Air ConditioningReplies: 29Last Post: 08-10-2007, 05:48 PM -
mitsubishi mr slim master and slave
By r600a-bang in forum Air ConditioningReplies: 2Last Post: 24-07-2006, 10:24 AM