    Acceptable Moisture Content



    Hi Folks
    I have been asked a question that I am struggling to answer so I thought somebody out there may be able to help.

    The question is as follows:-
    What is the acceptable level of moisture contained in the refrigerant or oil in an operating refrigeration system?

    My answer was less than 10ppm as with new refrigerant but obviously that is not always possible in the field.

    There must be an industry standard somewhere that gives a figure but I can't find it.

    Thanks
    Ian



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Acceptable Moisture Content

    Can't help with a definitive answer Pooh but have a read of this pdf from Emerson...

    http://www.emersonflowcontrols.com/w...te%20Paper.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Acceptable Moisture Content

    I was told once by a Japan factory design engineer that it takes 2000 compressor run hrs for the moisture to become saturated in the oil.
    I think from memory that refrigerant spcification is about 10 or 20 ppm & manufacturers will try to acheive same.
    But any higher moisture content & the expected life time of the compressor bearings starts to become reduced.
    More moisture = shorter compressor life.
    The issue is that the installation engineer can only achieve best vacume available with his vac pump. Moisture in refrigerant cannot be changed & moisture left in equipment from manufacture cannot be changed.

    So how can the instalation / commissioning enginner measure or calculate how many ppm of moisture is in the system ?

    Ideally you would replace the complete oil charge after 2000 hrs because after 2000 hrs all moisture has become saturated in the oil & so if this is removed & replaced with new oil then all moisture has been removed from system ,,,,may be?

    Does any engineer carry out this procedure ??? what type of equipment ?

    Most a/c split systems & VRF systems do not have oil drain connection on compressor.

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Acceptable Moisture Content

    Good point Jollycold
    Some VRF systems do have a filter drier which can be replaced. Sub cooler circuit is a good place because refrigerant flow is always in the one direction.
    But as noted before on this forum it is difficult to put filter drier in liquid line for split systems due to pre expansion at outdoor unit.
    Perhaps if more contractors complained to manufacturers about lack of filter driers then they would include them.

  5. #5
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Acceptable Moisture Content

    Quote Originally Posted by Pooh View Post
    Hi Folks
    I have been asked a question that I am struggling to answer so I thought somebody out there may be able to help.

    The question is as follows:-
    What is the acceptable level of moisture contained in the refrigerant or oil in an operating refrigeration system?

    My answer was less than 10ppm as with new refrigerant but obviously that is not always possible in the field.

    There must be an industry standard somewhere that gives a figure but I can't find it.

    Thanks
    Ian


    Moisture is not the only impurity likely to be present, but it’s the core of this question.

    If we stay with the original question for a moment before branching off into the subject of driers, the answer to the question of how much moisture is permissible in a system is one that we know all along – nil, if you can achieve it.

    Recognising that ‘nil’ in absolute terms is impossible to achieve, the manufacturing standard on refrigerant purity (originally an ISO standard, I believe), provides a de minimis value of less than 10 ppm moisture in terms of chemical purity that is put on the market as virgin refrigerant. De minimis values are considered impossible to measure or insignificant in their effect.

    So, I think the answer to the question is zero moisture, or as close to it as you can practically achieve and most importantly, to maintain in use.

    Is it written down somewhere?

    Yes, I think so, but not as an absolute numerical value. Nil is the goal that every manual on best practice reinforces. Teaching standards on system evacuation should cover it. Whilst it’s not specifically covered by a value in EN 378, it is implied.


    .

  6. #6
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Acceptable Moisture Content

    Hi All, I have a problem, it being any moisture in a system is a major and when any system has a problem the onus is on the technician to make sure the system is tight but with all the pressures ie time and money corners will be cut.

    Regards norm
    My wife used to say you never listen to a word I say at least I think that what she said

  7. #7
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Acceptable Moisture Content

    Thanks all, there still does not appear to be an answer on this one.

    Ian

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Acceptable Moisture Content

    Quote Originally Posted by Thermatech View Post
    The issue is that the installation engineer can only achieve best vacume available with his vac pump.
    Triple evacuation will remove more contaminants than single evacuation, regardless of how long the pump is left in the system. When the pump (and the system) reaches its deepest vacuum, further pumping is pointless. But repeating the process can remove more of the contaminants.

    For example, if the first evacuation removes say 90% of the charge (and therefore 90% of the contaminants), then the second evacuation removes 90% of the remaining contaminants bringing the total removal to 99%. Then the third evacuation removes 90% of the remainder, bringing the total removal to 99.9% of the contaminants.

    If you break the vacuum each time from the high side, this sweeps the remaining contaminants through the system to the low side. Then begin the next evacuation from the low side, pulling out the contaminants before evacuating from both sides.
    Last edited by Gary; 09-12-2007 at 01:41 PM.

  9. #9
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Acceptable Moisture Content

    Gary
    read the original question I am not asking about evacuation methods I asked about what the maximum acceptable moisture content is for an operating system, in other words how much moisture is OK.

    Ian

  10. #10
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Acceptable Moisture Content

    Quote Originally Posted by Gary View Post
    Triple evacuation will remove more contaminants than single evacuation, regardless of how long the pump is left in the system. When the pump (and the system) reaches its deepest vacuum, further pumping is pointless. But repeating the process can remove more of the contaminants.

    For example, if the first evacuation removes say 90% of the charge (and therefore 90% of the contaminants), then the second evacuation removes 90% of the remaining contaminants bringing the total removal to 99%. Then the third evacuation removes 90% of the remainder, bringing the total removal to 99.9% of the contaminants.

    If you break the vacuum each time from the high side, this sweeps the remaining contaminants through the system to the low side. Then begin the next evacuation from the low side, pulling out the contaminants before evacuating from both sides.
    I would assume that if we pumped down to 1000 Microns, a lot more of the charge would be gone than 90%.
    There are 25,400 Microns in a inch of vacuum. By my math this works out to about .02 pounds of pressure absolute. Without doing a lot of calculating this early, I believe this would remove about 99.8 or so % of the contaminants, without a triple evacuation.
    I have used triple evacs in the past, but with a good pump and hose setup I do not see the need.

  11. #11
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Acceptable Moisture Content

    Pooh
    This question is theoretical for most engineers because it is not possible to connect a meter to any systems which indicates exacly what the moisture content is in ppm.
    Service & commissioning engineers cannot accurately calculate or even estimate what the actual ppm might be.
    They can only triple evecuate as best practice using a good quality Torr gauge & hope that the moisture level is close to the 10 ppm standard specification for the refrigerant.

    If any one can find any details of any instrument that you can connect to any refrigerant system & it gives a digital reading of the ppm moisure content please share the details with us.

    This is of interest to many contractors beause some manufacturers strip down compressors which are returned under warrantee. If any copper deposits are found on hot moving parts in the compressor the warrantee claim is rejected.
    The reasoning goes like this,
    1/ Copper deposits are caused by acid which leaches the copper from copper tube in the system.
    2/ Acid is formed in system due to excessive moisture.
    3/ Moisture can only be pressent due to poor evacuation at commissioning or during service work.

    Currently contractors have no really good way to prove what the actual moisture connent is so they have to swallow the cost.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Acceptable Moisture Content

    Quote Originally Posted by Pooh View Post
    Gary
    read the original question I am not asking about evacuation methods I asked about what the maximum acceptable moisture content is for an operating system, in other words how much moisture is OK.

    Ian
    The answer is, of course... as little as possible.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Acceptable Moisture Content

    Quote Originally Posted by NH3LVR View Post
    I would assume that if we pumped down to 1000 Microns, a lot more of the charge would be gone than 90%.
    There are 25,400 Microns in a inch of vacuum. By my math this works out to about .02 pounds of pressure absolute. Without doing a lot of calculating this early, I believe this would remove about 99.8 or so % of the contaminants, without a triple evacuation.
    I have used triple evacs in the past, but with a good pump and hose setup I do not see the need.
    I used 90% because the math is easy, making the explanation clearer.

    Use 99.8% and adjust the math for each evacuation accordingly. It may not be needed, but it certainly doesn't hurt.

  14. #14
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Acceptable Moisture Content

    Gary, Thermatech
    you have both still missed the point of the question, I am not talking about new systems I am talking about systems that have been running for some conciderable time and have gained moisture due to poor service activities like not purging lines or putting oil in that was wet.
    A freind of mine who works in Dubai has asked the question as he has some wet systems that the clients won't do anything about as there is not a standard he can find that gives a higher limit on moisture. He has had some refrigerant tested in a lab and has found in excess of 200ppm but the client still won't allow him to remedy the fault by fitting a large number of drier cores etc to remove the moisture and due to the plant being used for process he cannot shut it down to evacuate it and replace the oil and refrigerant.

    Ian

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Acceptable Moisture Content

    Have a look here

    http://www.sporlan.com/70-10.pdf

    Has a chart for various refrigerants and the moisture/temperature levels that change the colour of the sightglass, which is what i tend to go by if they are fitted.

    jon

  16. #16
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Acceptable Moisture Content

    Sorry, I can't find the slide show I'm after (I know I have one from an oil manufacturer on a disk somewhere but I looked since this thread started and I now given up).

    From memory, I seem to remember that for mineral oils the answer is 100ppm but for new synthetic oils it's only ~75ppm. This is LESS than what the oil in the compressors has when the compressor leaves the manufacturer and the whole system relies on us, the service engineers to change driers until the system is dry.

    I have attached a slide from Copeland illustrating a "normal" work/moisture flow of a new system.
    Last edited by The Viking; 13-04-2008 at 09:52 PM.

  17. #17
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Acceptable Moisture Content

    Thanks for the extra explanation for the reason why you would like the ppm moisture information.
    As Viking has indicated I would normally expect the manufacturer of the compressor to be able to give an indication of max moisure level above which the compressor life will be compramized.
    Fair to say that at 200 ppm the compressor will have short life & the enduser will then have to pay for new compressor & burn out filter drier clean up procedure. The contractor can install shell driers with valves & bypass in the compressor suction which will allow the cores to be replaced without shutting down the plant which is what the enduser will require as the application is process.

  18. #18
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Acceptable Moisture Content

    Hey, I found it !!!

    So, looking at that slide from an old compressor manufacturer, the answer must be below 50 ppm.
    Last edited by The Viking; 13-04-2008 at 09:52 PM.

  19. #19
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Acceptable Moisture Content

    Thanks LRAC and Viking pretty much what I am looking for

    Ian

  20. #20
    Join Date
    Mar 2009
    Location
    La Piedad, Mexico
    Age
    38
    Posts
    93
    Rep Power
    16

    Re: Acceptable Moisture Content

    >Acctually there is a meter for this prupouse, its made by yellow yacket and measure the purity of the gas, the amount of air present in the system and if there is non condensables on it, a dream tool, i paste a link latter today if anybody is interested :-)

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

  22. #22
    Join Date
    Mar 2009
    Location
    La Piedad, Mexico
    Age
    38
    Posts
    93
    Rep Power
    16

    Wink Re: Acceptable Moisture Content


    Yeap, the same one.
    I like to know if somebody has use it, and if its really helped to correct some error.

    Im wondering if there is a notable diference between an a equipment that uses a gas with a 1% of non condensables and another wich uses a 10% of non condensables. More heat in the compresor? poor cold?.... danger of explosion?

Similar Threads

  1. Filter Drier Moisture content
    By caster in forum Trouble Shooting
    Replies: 4
    Last Post: 02-11-2007, 08:59 AM
  2. Moisture
    By Abe in forum Trouble Shooting
    Replies: 29
    Last Post: 07-08-2007, 05:50 PM
  3. Moisture in Propane Liquid
    By Nizar in forum Refrigerants
    Replies: 4
    Last Post: 24-07-2006, 04:12 PM
  4. Moisture loss calculation
    By gregorm in forum Technical Discussions
    Replies: 15
    Last Post: 15-05-2006, 04:23 PM
  5. Moisture bound insulation
    By Temprite in forum Commercial
    Replies: 2
    Last Post: 18-05-2005, 02:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •