Results 1 to 8 of 8
Thread: Tex Sizing
04-12-2007, 05:43 PM #1
Tex Sizing
HOW CAN WE SIZE UP A THERMOSTATIC EXPANSION VALVE,COZ THE COMPANY'S CHILLER EXPANSION VALVE HAS NO SPECS ON ITS VALVE ITSELF DUE TO FADING.
I AM A NEW MAINTENANCE AT THESE COMPANY AND I NEED SOME HINTS ABOUT MY QUERY.
THERE'S NO PROBLEM ON THE OPERATION BUT FOR SPARE PURPOSES I WANT TO REQUEST FOR THESE EXPANSION VALVE.
LOOKIN' FORWARD FOR YOUR VIEWS.
THANK YOU VERY MUCH!
04-12-2007, 08:36 PM #2
Re: Tex Sizing
Try asking the chiller manufacturer for the details of the TXV.
04-12-2007, 09:43 PM #3
Re: Tex Sizing
Hello cristopher_uy, what make, model is the chiller. Also how many kilo's and which refrigerant is in it.
04-12-2007, 10:13 PM #4
Re: Tex Sizing
Isn't this classed as shouting?
THANK YOU VERY MUCH!Tony
04-12-2007, 11:44 PM #5
Re: Tex Sizing
Yes it is Tony, but some don't know it
05-12-2007, 12:00 AM #6
Re: Tex Sizing
Hi, Tony
yes it is, but he is in trouble and looking for help
Best regards, Josip
05-12-2007, 12:25 PM #7
Re: Tex Sizing
As Brian UK said, contact the Chiller manufacturer for the TEV model, otherwise you will only be guessing and not get the correct one.
05-12-2007, 12:57 PM #8
Re: Tex Sizing
Hi Christoper Uy,
Sizing the exp. valve you have to know the following.
a) max evaporator load
b) evaporating temp.
c) condensing temp.
d) Liquid subcooling
Then for easy selection find the catalog/book of any refrigeration components manufacturer like danfoss or alco then look on their selection table.
for your continue learning in refrigeration you can visit www.danfoss.com;)
A/C Chiller Sizing tables
By romaurie in forum Tools and CalculatorsReplies: 1Last Post: 12-12-2010, 01:04 PM -
Capillary tube sizing
By Sledge in forum RefrigerantsReplies: 7Last Post: 16-11-2010, 11:44 PM -
Piping and line sizing in lbs/min
By Kathleen in forum Tools and CalculatorsReplies: 18Last Post: 29-05-2009, 03:07 PM -
Compressor sizing using R404a
By PCL in forum RefrigerantsReplies: 4Last Post: 14-08-2006, 11:09 PM -
Sizing for Australia
By dogma in forum FundamentalsReplies: 5Last Post: 17-03-2006, 10:05 AM