30-11-2007, 08:31 AM #1
High Level alarm / low level alarm for Low Pr. receiver
Recently we have done a ref system with low pr receiver. It is also having Ammonia Pumps etc. Incidently durign commissioning stage we came across a situation wherein Liquid was coming back to compressors. It had do with High level cutout being faulty in the low pr. receiver. We were wondering on more safety for this particular issue. I came across very good suggestion in Industrial Refrigeration handbook by Wilbert Stoecker. I though I must share this point with the forum. Ofourse many may be using this extra safety though.
30-11-2007, 06:06 PM #2
Re: High Level alarm / low level alarm for Low Pr. receiver
Getting liquid back into compressors is serious. How did it happen?
Since you did not mention what the suggestion was from the book, I am assuming you mean the use a mechanical float switch to shut down the compressors.
Capacitance probes are nice, but I always prefer to have a mechanical float switch for protecting the compressors. The floats rarely fail so I think this is a good protective measure.If all else fails, ask for help.
30-11-2007, 11:51 PM #3
Hi, smpsmp45
Originally Posted by US Iceman
...but you can have a problem with suction headers (wrong slope, wrong connections...etc..and you can collect a lot of liquid within and suddenly return to compressor causing a big headache...
...sorry, but I have to ask, is this plant one of Allana cold stores in Mumbai...
....before 25 years I had this situation (2times before we discover what and why/but that is another long story), with emergency stop of the chemical process plant with cost of about 120000DEM (60000 Euro today) each emergency stop....the good luck was because we (ex Yugoslavia) in that time were socialist country with "collective responsibility" I do not want to imagine court processes and compensation today...
coming back to your problem....within new compressors control cabinet there is always suction temp probe where you monitor suction superheat (SSH) and stop compressor/s automatically if become to low and before liquid return....
Best regards, JosipLast edited by Josip; 01-12-2007 at 12:15 AM. Reason: add some text
01-12-2007, 12:14 AM #4
The good old days Josip
18-12-2007, 06:42 AM #5
i look at this problem in a very much different perspective.
my opinion:
1] liquid floodback or floodstart happens may be the cause of insufficient evaporation velocity for the refrigerant in the low receiver.
2] possibly, the normal liquid level is arealdy high (referring earlier point) & when fluctuations in liquid return volume, new level is beyond tolerable level and carry back via suction pressure.
3] construction of lo receiver is also very important. there are few important features which are intentionally fabricated inside the receiver to handle such issues.
High Deferential Oil Pressure Alarm
By NNNNNN in forum Trouble ShootingReplies: 27Last Post: 24-12-2007, 01:06 PM -
high volume flow rate
By cakabo28 in forum Technical DiscussionsReplies: 5Last Post: 04-10-2007, 03:41 AM -
liquid receiver low level alarm
By racknovice in forum Supermarket RefrigerationReplies: 8Last Post: 18-08-2007, 06:53 PM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM