    Help needed!



    Hello friends!
    Gr8 to be a part of this forum..
    A few queries as far as the R-22 refrigeratrn system is concerned( 81TR @ -32 deg C brine outlet )
    Our system is designed for a sunction superheat of -35deg C . THe system is also having an economiser .The refrigerant vapour pressure before sucntion is ~0.2 kg/cm2. Brine leaving is at ~-31.3 deg C , but the temp of the suction vapour is as low as -42 deg C.THe system is also having an economiser .
    Is this situation normal??( COnsidering a delta between refrigerant and brineas high as 9 deg C ???)
    Wld appreciate your valuable feedback . SOme reference material links in this regard would also help

    Cheers !!

    Govind



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Help needed!

    First things first, superheat can only be a possitve nunber, other wise you'll get liquid back to the compressor.

    Than a 9K approach (sat. evaporator temp - leaving brine temp) sounds about right to me.

    Brine has a lower specific heat than water and because it's more oil like will also thansfer the heat far worse then water.

    The specific heat for water is, rounded up, 4,2 kJ/kg*K, for 30% ethlyleenglycol, off the top off my head, it's 3,85 kJ/kg*K.

  3. #3
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Smile Re: Help needed!

    Quote Originally Posted by gk2108 View Post
    Hello friends!
    Gr8 to be a part of this forum..
    A few queries as far as the R-22 refrigeratrn system is concerned( 81TR @ -32 deg C brine outlet )
    Our system is designed for a sunction superheat of -35deg C . THe system is also having an economiser .The refrigerant vapour pressure before sucntion is ~0.2 kg/cm2. Brine leaving is at ~-31.3 deg C , but the temp of the suction vapour is as low as -42 deg C.THe system is also having an economiser .
    Is this situation normal??( COnsidering a delta between refrigerant and brineas high as 9 deg C ???)
    Wld appreciate your valuable feedback . SOme reference material links in this regard would also help

    Cheers !!

    Govind
    Govind,
    you means your saturated suction temp (SST) = -35degC?

    yes, below -25degC needs economizer.

    suction pressure is ok [within range].

    if dT is 9K, your SST = -32-9 = -41degC.
    but, you may still get lower Suction Temperature due to actual superheat and piping design.

    hope that helps.

  4. #4
    gk2108's Avatar
    gk2108 Guest

    Re: Help needed!

    Sanderh,
    What i meant was that our chiller system is designed for a brine outlet temp of -32 deg C , and the suction at the compressor at -35 deg C . That makes it +3 deg C suction superheat.apologies for penning down wrongly.
    Now ,in practice, what i am observing is that the refrigerant gas suction temp is around -41 deg C and the brine leaving the chiller is at -31 deg C.This is a DX type of a chiller.and i wanna know whether such a high dT( between the refrigerant gas and the brine ) is allowable , and is this efficient operation??????
    Regards

    Govind

  5. #5
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Help needed!

    I understood your question, hence the numbers to explain it, imo, better.


    Can you tell me what brand it is?

  6. #6
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Help needed!

    Quote Originally Posted by gk2108 View Post
    Sanderh,
    What i meant was that our chiller system is designed for a brine outlet temp of -32 deg C , and the suction at the compressor at -35 deg C . That makes it +3 deg C suction superheat.apologies for penning down wrongly.
    Now ,in practice, what i am observing is that the refrigerant gas suction temp is around -41 deg C and the brine leaving the chiller is at -31 deg C.This is a DX type of a chiller.and i wanna know whether such a high dT( between the refrigerant gas and the brine ) is allowable , and is this efficient operation??????
    Regards

    Govind
    Govind, efficient in our context is low input higher output.

    currently, your data explains that you need dT of 10K to produce -31degC brine.
    normally, in our design, we use merely 8K max. to do so.
    probably, there might be some other issue/s in your system which you should consider.

    sometimes, in our troubleshooting, we seek beyond the arising problem/s to eliminate the issue/s.

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Help needed!

    Ok, first the suction superheat is the difference between the saturated vapour temperature and the suction temperature. The other value to use is the difference between the evaporator outlet temperature and the saturated vapour temperature, or approach.

    Super heat should be, dependend on the type of expansion valve, between 3 and 10 K. The approach for a shell/tube heatexchanger normally 1 to 5 and up to 8 for brine. Brazed plate heatexchangers slightly higher.

    If superheat is too high either the charge isn't right, the valve isn't openeing enough or there could be oil in the evaporator.

    If approach is too high the same goes for the oil or the evaporator is fouled!

    For some reason you won't tell what brand it is, this however would help a lot!

  8. #8
    gk2108's Avatar
    gk2108 Guest

    Re: Help needed!

    The chiller package is basically an assembled one.Mfg by Systems and Components . the compressor is Hallscrew( twin lobe , HS2028 series). expansion valves are danfoss make( solenoid operated exp valve). And the evaporator is of copper metallurgy.
    Regards
    Govind

  9. #9
    gk2108's Avatar
    gk2108 Guest

    Re: Help needed!

    Sanderh,
    Can you suggest sum ebooks which could make me understand these fundamentals in a better way>??Basically my job profile is to take care of the utility operations, without much more stress on all these design aspects..but i guess this wld direclty affect our overall system performance..

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Help needed!

    I don't know of any ebooks. But perhaps someone in your country with experiance in chillers can help and have a look!

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Help needed!

    Quote Originally Posted by gk2108 View Post
    Sanderh,
    What i meant was that our chiller system is designed for a brine outlet temp of -32 deg C , and the suction at the compressor at -35 deg C . That makes it +3 deg C suction superheat.apologies for penning down wrongly.
    Now ,in practice, what i am observing is that the refrigerant gas suction temp is around -41 deg C and the brine leaving the chiller is at -31 deg C.This is a DX type of a chiller.and i wanna know whether such a high dT( between the refrigerant gas and the brine ) is allowable , and is this efficient operation??????
    Regards

    Govind
    Possibly some definitions would be helpful, in the interests of improving communications.

    A "delta-T or dT" is a change in temperature of a single substance or flow of substance. For example, if the entering brine is -37C and the brine outlet temperature is -32C, this is a change in temperature of 5K or "5K delta-T".

    A "temperature difference or TD" is a comparison of the temperatures of two different substances or flows of substances. For example, if the brine inlet temperature is -37C and the saturated suction temperature is -41C, then the difference in the temperatures of the two flows is 4K or "4K TD".

    The "approach temperature" is a particular type of TD, specifically the difference between the brine leaving temperature and the saturated suction temperature. As heat is transferred between these two substances, the temperatures come closer to each other, or "approach" each other. If the brine leaving temperature is -32C and the saturated suction temperature is -41C, then this gives us "9K approach".

    The "superheat" is a particular type of delta-T, specifically the difference between the saturated suction temperature of the refrigerant and the temperature of the refrigerant in the suction line. If the saturated suction temperature is -41C and the suction line temperature near the compressor is -35C, then we have "6K superheat" at the compressor inlet.
    Last edited by Gary; 22-12-2007 at 05:55 PM.

  12. #12
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Help needed!

    Thanks for explaining it Gary, I was busy the last few weeks and finely have 3 weeks of holiday now!!

    Anyway, as I said before an approach of 9K would be reasonbly common on a plate heat exchanger when using brine. However a shell/tube one would have a lower one. Reasons for the approach to become higher can be found in my previous post.

Similar Threads

  1. Autocascade refrigeration system: design verification needed
    By DaBit in forum Technical Speculations
    Replies: 3
    Last Post: 07-02-2010, 07:48 AM
  2. Smart/As needed evap defrost?
    By dkemper in forum Fundamentals
    Replies: 6
    Last Post: 27-10-2008, 07:25 PM
  3. Horsepower needed for 20 ton icemaker
    By claude11 in forum NH3
    Replies: 2
    Last Post: 25-10-2007, 12:00 AM
  4. Carrier 40GKX028 service manual needed
    By Ireland in forum Air Conditioning
    Replies: 6
    Last Post: 08-02-2007, 07:06 PM
  5. Replies: 17
    Last Post: 25-08-2003, 09:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •