    Question about Refrigerant



    I have always thought that when a system is short of gas that is running on R407c or like , that if more than 10% has been lost then rather than "top it up" it should be recovered and recharged because you don't know which of the blends has been lost....but if that is the case then when you ( for example) charge a system with say 3kg from a a full cylinder then how do you know what percentage of each blend is going to be charged into the system...(hope that makes sense)


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Question about Refrigerant

    Quote Originally Posted by marc5180 View Post
    but if that is the case then when you ( for example) charge a system with say 3kg from a a full cylinder then how do you know what percentage of each blend is going to be charged into the system...(hope that makes sense)

    You should always charge the refrigerant as a liquid.
    That will stop any seperation.


    taz.

  3. #3
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Question about Refrigerant

    http://www.refrigerants.dupont.com/S...pdf/h47125.pdf

    If your just interested in 407c and 410a Du-pont has the above info. I'm sure you could find other refrigerants as well. 1/2 the charge lost several times in a row and recharged with liquid 407/410 produce little to no ill effects depending on how many times it leaks out and is refilled.

    You must charge blends as a liquid.
    Last edited by BigJon3475; 30-11-2007 at 05:46 AM.

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Question about Refrigerant

    .

    Quote Originally Posted by marc5180 View Post
    I have always thought that when a system is short of gas that is running on R407c or like , that if more than 10% has been lost then rather than "top it up" it should be recovered and recharged because you don't know which of the blends has been lost....
    That’s what they tell you to do because the relatively high glide with R 407C, (about6.5 degrees) means that the vapour phase contains the 3 components in a differing ratio to the specified ratio for R 407C.

    But the first thing, obviously, is to find the leak and fix it.

    Quote Originally Posted by marc5180 View Post
    …...but if that is the case then when you ( for example) charge a system with say 3kg from a a full cylinder then how do you know what percentage of each blend is going to be charged into the system...(hope that makes sense)
    It does make sense, and the unequal separation in the vapour phase applies equally to service cylinders.
    The accepted wisdom is that the cylinder should be filled to its capacity each time you charge from it, rather than partially full, because this minimises the vapour content in the cylinder that is not in the correct mixture ratio.
    Then you charge in the liquid state to maintain the correct mixture which will have the correct mixture within acceptable tolerances.
    In reality, on a windy roof, this is easier said than done.

    Small imbalances in the mixture will go unnoticed in most systems. You will probably loose more capacity through dirty filters than a slight imbalance in refrigerant mix.


    .

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Question about Refrigerant

    Blend changes titration only when the system leaks refrigerant at a temperature inside the glide range, aka distillation

  6. #6
    Join Date
    Nov 2007
    Location
    Dubai
    Posts
    25
    Rep Power
    0

    Re: Question about Refrigerant

    Quote Originally Posted by BigJon3475 View Post
    If your just interested in 407c and 410a Du-pont has the above info. I'm sure you could find other refrigerants as well. 1/2 the charge lost several times in a row and recharged with liquid 407/410 produce little to no ill effects depending on how many times it leaks out and is refilled.

    You must charge blends as a liquid.
    i heard that in europe the are changing the 407 blends to 507 blends cause they seems to break up and cause frosting on the evaportors

Similar Threads

  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Replies: 14
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Basic question about refrigerant to use
    By cbfull in forum Fundamentals
    Replies: 25
    Last Post: 07-08-2007, 02:19 AM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •