28-11-2007, 07:48 PM #1
daikin problem
i know l9 is compressor lock on a vrv2 system. But dont know were to go from here.On the same system uh and f3 came up on test could it be a pcb problem
-
28-11-2007, 11:48 PM #2
Re: daikin problem
OK,
L9 = Stall prevention
UH = Improper connection of transmission wiring between outdoor unit and outdoor unit outside control adaptor
F3 = Abnormal discharge pipe temp.
You might be right, the PCB might be on the blink..
But I would investigate a bit further before I order a new one.
Disconnect the inverted compressor, reset the unit and carry out a inverter check procedure just to see what happens.....
No doubt one of the Daikin guys will be able to give better information shortly.
-
29-11-2007, 10:29 AM #3
Re: daikin problem
UH - Malfunction of system, refrigerant system address undefined
* if you didn't worked with automatic addressing you must set address for each indoor unit, maybe you forgot some
* check the wiring connection between indoor and outdoor unit.
F3 - Abnormal discharge pipe temperature outdoor unit
* check the discharge temperature sensor, they are on the right side of the outdoor unit PCB
L9 - Inverter startup error
* check if stop valve is opened
* is a difference between high and low pressure prior to startup 0.2MPa? If not check the refrigerant system.
* check compressor wires, and measure windings
If you need more help do not hesitate to ask
Similar Threads
-
daikin L0 inverter problem
By robin r33 gtr in forum Air ConditioningReplies: 17Last Post: 11-03-2010, 11:25 PM -
Problem with an inverter compressor in V.R.V system DAIKIN R 407
By Harris Greece in forum Air ConditioningReplies: 10Last Post: 24-11-2007, 12:53 AM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM -
Daikin problem
By Jambo in forum Trouble ShootingReplies: 4Last Post: 28-07-2006, 07:42 PM